I want to give back to the forum that offered free advice. Thanks to all who contribute.
I'm done with the install (pretty much) and waiting for details to turn on the system.
And it is New Year's Day and a good to time to write down points that might help others.
System Specs:
Milpitas CA, PG&E
Roof - 4:12 or 18deg, 158deg azimuthal
Supplier/Distributor - Renvu.com
String inverter - 2 strings
15 total panels, Sunvia 325W, 72 cell panels 4.875kW system size, 7 and 8 panel strings
SMA Sunnyboy SB4000TL-US-22 with Speedwire Webconnect
Ironridge XR10 rails (no snow here!)
Soladeck passthru
External 3/4" EMT for all wiring from array to jBox, to inverter, to AC disconnect, to Main Panel
Cutler Hammer DG221URB AC Disconnect
pvlabels.com for compliant labels
CAT6 line from home router to inverter
New tools acquired: Long 1/4" drill bit, MC4 Crimp tool, Hex to square drive bits, replacement 16ft tape measure, RJ45 Crimp tool for network cable
Tools that would have made the job easier, but I was too cheap to purchase: Hole Drill for 1 1/4 roof penetration, Hole punch or step drill for 1 1/8 conduit connection to Soladeck, conduit bender
Total system cost (with permits and Home Depot runs) - $10776.39. Expected tax credit (30%) - $3232.92, for final cost of $7543.47
Expected payoff time - <5years
Status, as of today: Everything I have is now installed. See below. After finishing installation, will call for City inspection, and then for Utility permission to turn on.
Renvu.com experience. Very good. Their customer support is very good with personal attention to any and all questions asked. However, there were some things I learned.
All in all, it has been a fun experience to date. Things aren't turned on yet, but I hope the inspection/power up experience will go smoothly. Thanks for all your help in giving me the confidence to make this happen. If you have any follow up questions, feel free to post here or PM me. I will share more details on request (cost sheet, calculations, SLD, etc)
I'm done with the install (pretty much) and waiting for details to turn on the system.
And it is New Year's Day and a good to time to write down points that might help others.
System Specs:
Milpitas CA, PG&E
Roof - 4:12 or 18deg, 158deg azimuthal
Supplier/Distributor - Renvu.com
String inverter - 2 strings
15 total panels, Sunvia 325W, 72 cell panels 4.875kW system size, 7 and 8 panel strings
SMA Sunnyboy SB4000TL-US-22 with Speedwire Webconnect
Ironridge XR10 rails (no snow here!)
Soladeck passthru
External 3/4" EMT for all wiring from array to jBox, to inverter, to AC disconnect, to Main Panel
Cutler Hammer DG221URB AC Disconnect
pvlabels.com for compliant labels
CAT6 line from home router to inverter
New tools acquired: Long 1/4" drill bit, MC4 Crimp tool, Hex to square drive bits, replacement 16ft tape measure, RJ45 Crimp tool for network cable
Tools that would have made the job easier, but I was too cheap to purchase: Hole Drill for 1 1/4 roof penetration, Hole punch or step drill for 1 1/8 conduit connection to Soladeck, conduit bender
Total system cost (with permits and Home Depot runs) - $10776.39. Expected tax credit (30%) - $3232.92, for final cost of $7543.47
Expected payoff time - <5years
Status, as of today: Everything I have is now installed. See below. After finishing installation, will call for City inspection, and then for Utility permission to turn on.
Renvu.com experience. Very good. Their customer support is very good with personal attention to any and all questions asked. However, there were some things I learned.
- Count panels when you receive them. Shipment of panels shorted me one. They shipped 14 by mistake. They are sending me a replacement next week.
- Buy bare Cu from Big Box. I ordered the SLD (single line drawing) from Renvu for $250. After the design came back, it called for 6AWG equipment ground on the roof. But the default order was for 500ft of 8AWG cu. And I didn't need the 500ft min order from Renvu. Got 70ft from big box and saved money. Renvu sending me a full credit return for the misallocated order.
- Don't order labels from Renvu. I ordered the default labels from Renvu. But if I had been paying attention, I shouldn't have. My city requires the red NEMA labels and not the Orange/white ANSI labels defaulted from Renvu. Ended up ordering custom labels (as required by the city) from pvlabels.com once the final numbers came back from the SLD. Pvlables.com placards come with stickers, so don't bother with rivets or rivet holes.
- Aesthetics weren't an issue, so I went with the blemished Suniva panels. They look fine from 20ft away. No issues.
- Default wire clips (Wiley ACC-PV) were difficult to use, and could only be installed to the thin frames of the panels. Not to the rails before panels are installed. OK, but splurging for rail mounted Ironridge clips might have saved some time.
- Check quantities of Rail before final order. Ironridge length calculated is used by Renvu. Neither accounts for the ability to cut rails in half. I have 2 panels installed by themselves and the rail calculator didn't account for me being able to cut a long rail in 2.
- Hardest part is finding the rafters. My roof has horizontal roofing boards under the plywood and over the rafters (from original shake roof?). No way to find the rafters from above without a $2500 stud finder. No thanks. I ended up trudging through the freshly insulated attic. Drilled up at one location, offset from a rafter, and then mapped upper locations across the roof from that base point. Then transferred those numbers to the top side roof. We hit every rafter where we could see the tails under the eaves. Not so exact at the roof hips where we couldn't see the tail ends for a good chaulk line.
- Used lots of roofing gunk during install of flashing feet. Pushed in each drilled hole and rainbow shape on the bottoms of the flashings. Praying for a leak tight install.
- Decided on Sunnyboy inverter partially because it includes the SPS outlet if the utility goes down and the sun is up. It's gimmicky, but could make the difference of keeping my freezer full of food if we ever get that Big one.
- Lifting panels to the roof. Not a single person job! We built a simple trolley that runs on my aluminum ladder. I used a set of wheels from a skateboard and some scrap lumber. Pulled assembly up with a rope from above, and lifted from below. Tied it off at the top, and then my helper came up and helped lift it off the trolley at the top. Worked good enough to get them on the roof safely. Luckily I have 2 ladders for access to the roof while the panel is at the top!
- Solar array connection to main panel - standard 2pole 30A CB should be installed opposite (on the far end from) the utility supply CB (200Amp in my case).
All in all, it has been a fun experience to date. Things aren't turned on yet, but I hope the inspection/power up experience will go smoothly. Thanks for all your help in giving me the confidence to make this happen. If you have any follow up questions, feel free to post here or PM me. I will share more details on request (cost sheet, calculations, SLD, etc)