Hey all,
Just wanna double check something. I got a existing ground rack system. 6000 inverter(240.vac). Were gonna add a new system. Existing home run wire size is 8 AWG at 450 feet. The new system will be 3000. Add a subpanel too combine both systems together. 6 kw and a new 3kw. Total 60 continuous amps at 450 feet. Change home run to 6 guage and add a 100 amp sub. Existing main is 400 amps. 400 buss. Seem correct?
thanks
Just wanna double check something. I got a existing ground rack system. 6000 inverter(240.vac). Were gonna add a new system. Existing home run wire size is 8 AWG at 450 feet. The new system will be 3000. Add a subpanel too combine both systems together. 6 kw and a new 3kw. Total 60 continuous amps at 450 feet. Change home run to 6 guage and add a 100 amp sub. Existing main is 400 amps. 400 buss. Seem correct?