That doesn't work much better than out-sourced call centers ...
ANYWAY, we're way off topic again ...
solar system design
Collapse
X
-
Leave a comment:
-
Yes I know.
Mercantilism is the economic policy of the Chinese government.Leave a comment:
-
Well sort of. The Design can easily be done overseas, and contracted out to undocumented roofers paid $30 per day. All it take sis one licensed contractor sitting in an office in TX to pull it off, sign the paperwork at inspection time, and collect a check from the Government
I had to stop by the local Sprint Store the other day to straighten out my corporate phone account. They recently off-shored some of their call center work and that was my first negative experience with Sprint in 9 years of being a customer. Companies =are= learning that we don't want to speak to someone in another country who knows =nothing= about whatever our issues are. Sprint is late to the off-shoring thing and will learn that sooner or later.Leave a comment:
-
The OP is from India.
I've got my issues with the Chinese, but not because they are a bunch of Commies. The Commies aren't the problem in China, it's the Merchantilists.Leave a comment:
-
Well sort of. The Design can easily be done overseas, and contracted out to undocumented roofers paid $30 per day. All it take sis one licensed contractor sitting in an office in TX to pull it off, sign the paperwork at inspection time, and collect a check from the GovernmentLeave a comment:
-
Riffraf if not for Americans, you would be Japanese my friend. Now who is going to save you from the Chi-Coms?Leave a comment:
-
Originally posted by RifRafwow you really giving the americans a good name with those comments, thanks for not letting my opinions down of yall
I also suspect Sunking knows that there is no way R.E. system design and construction can be outsourced to commie workers. Pretty hard to be an underpaid worker in Bangalore or Pune when the physical work is in Dallas or Houston!Leave a comment:
-
I've worked with a fair number of people from India, so I know there are cultural differences that can sometimes cause miscommunication. Rather than simply disagreeing, you'd do better to ask "Why is that the case?" For example, the reason that 85% full-cycle efficiency is unrealistic has to do with the voltage elevation during charging, and the voltage depression during discharging. A battery, such as the one you referenced, that is 95% efficient on an amp-hour basis isn't going to be 85% efficient in a real-world installation on a watt-hour basis. And the reason is that the voltage is 0.5 to 1.0 volts higher (per 12 volt monoblock) during charging, and 0.5 to 1.0 volts lower during discharge.
For a real example, my batteries "Absorb" at 57.6 volts, but they "run" at 49 to 50 volts. That voltage difference -- 86% lower during discharge -- is multiplied by the 95% amp-hour efficiency to yield a net 81% watt-hour efficiency. In your case, the discharge rate is higher, so the voltage depression will be greater and the full-cycle efficiency lower still.
Had you asked "Why?" instead of questioning us about our expertice, you'd have gotten that answer, and then you could have asked still more questions and gained additional knowledge.
Something to consider in the future.Leave a comment:
-
Then things went wrong and they blamed me.
Then they told me "We were paying you to be the expert".
Except, they stiffed me over $600.
So, I'm going to be suing them. They can explain to a judge why it's my fault they neglected to follow any of the advice they were given.Leave a comment:
-
Sometimes we smell a rat. Advice is being given, and you keep saying,oh, no matter, I'll do it this way. BTW, is this XYZ a good idea to 35% ?? Please you must tell me yesterday, as our reliable grid power is off.Leave a comment:
-
i'm new to field and in learning stage so i have to clear my doubts.Leave a comment:
-
Solar panel Wattage = [2475 x 1.5] / 5.5 hours = 675 watts if using MPPT controller and you actually get 5.5 Sun Hours which I doubt in winter.
No way should even consider taking a battery to 70% DOD, that is suicide, your battery would be worthless in a few short months, and just 1 cloudy day and you go dark. Try 20% DOD or 5 day reserve which is equivalent to 2.5 days real reserve to 50% DOD. You did not say what voltage you wanted the battery, or was it 48 volts?
At 48 volts the battery AH capacity needed is [2475 wh x 5 days] / 48 volts = 257 AH @ 48 volts.
Charge controller size assuming MPPT is Panel wattage / nominal battery voltage = 675 watts / 48 volts = 14 amps minimum.
but you didn't consider the losses.
and in calculating battery capacity i think DOD and battery efficiency should be considered.
and as there is availability of grid and my inverter is bidirectional so i'm not worry about battery life coz it can also charged by inverter when Grid is available. so it will rarely go in deep discharge level.
as load is very small, is it not good to design system on 24V system?Leave a comment:
-
Don't worry about the average sunshine hours, coz there is Grid which is also available nd my inverter is able to take grid input as its a bidirectional inverter. and for battery DOD and efficiency check this
http://www.hbl.in/brochures%20pdf/TubularGel_VRLA.pdf
(And you need to believe us -- 85% full-cycle efficiency doesn't exist, regardless of what the ad hype says.)Leave a comment:
-
Got a few minutes, then coffee and annoy some solar installers.
You need to provide us with more accurate, as well as more realistic, information. Very few places average 5.5 hours per day. You'd have to be in the tropics, which much of India is, but then you have to allow for the rainy season, which much of India has.
Also, there is no such thing as an 85% efficiency, measured in full-cycle watt-hours battery. For a stand-alone system, efficiencies are a lot lower because they have to be designed more robustly. You gain some efficiency when recharging from a discharged state, but we don't even know what that is for your system, because 5.5 hours for winter (Northern India) or rainy season (the rest of India) doesn't happen.
You =can= decide that 70% DoD is your design point, and there are valid reasons to do that, but it's a lousy design point, especially since foul weather tends to last more than one or two days, and that gets back to "rainy season".
Anyway, time for coffee!!!