I've read through NEC Article 110: Requirements for Electrical Installations and I can't find the answer.
Here is a pic of the subpanel being installed. Before I finish mounting, strapping conduit, and running cabling through, can anyone throw me any red flags if the location will be a possible problem to AHJ.
2015-11-21 20.00.38.jpg
It's within an attached garage, 125amp rated 8/16 fed with #6/3 with no main disco, 50amp breaker at main panel.
Obviously not a lot of room on the left side near the PV inverter AC conduit. I told the installer I didn't like the AC conduit sticking that far out from the side, but I didn't want to haggle over 2 inches as he said something about needing that much room for the bend. But was annoying considering I already moved the surface mount receptacle over 18" to the right to make room for the panel.
Here is a pic of the subpanel being installed. Before I finish mounting, strapping conduit, and running cabling through, can anyone throw me any red flags if the location will be a possible problem to AHJ.
2015-11-21 20.00.38.jpg
It's within an attached garage, 125amp rated 8/16 fed with #6/3 with no main disco, 50amp breaker at main panel.
Obviously not a lot of room on the left side near the PV inverter AC conduit. I told the installer I didn't like the AC conduit sticking that far out from the side, but I didn't want to haggle over 2 inches as he said something about needing that much room for the bend. But was annoying considering I already moved the surface mount receptacle over 18" to the right to make room for the panel.