Burned DC fuse holder and cable (Grid tied)

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • squelch
    Junior Member
    • Aug 2015
    • 11

    #1

    Burned DC fuse holder and cable (Grid tied)

    Hi everyone,

    just happend recently

    hope you can help me found out the reason for this one. see attachment

    in this scenario, is it loose connection ?

    based on your experiences,

    TIA
    Attached Files
  • solarix
    Super Moderator
    • Apr 2015
    • 1415

    #2
    Definitely a loose connection in there somewhere. Probably can't figure out where now. Once the plastic melts, the contacts start to move around and get worse. In the old days of "hard" plastics like bakelite, they did not melt so easy, but these new pvc and pe plastics are not near as tough. Still, one of the terminations probably did not get tightened well. It is something that is hard for inspectors to catch and why you want a good, detail oriented electrician. This kind of burned connection is the cause of lots of fires. Europe has gone to spring type terminations in order to not depend on the skill of the installer so much. I'm not real confident about those either. This whole problem is why the code is moving toward arc fault detection as it would have caught this failure earlier....
    BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

    Comment

    • squelch
      Junior Member
      • Aug 2015
      • 11

      #3
      Thanks Solarix,

      is thermal scanning monitoring can detect this loose connection before it happens/future prediction. its been running for 3 months now.

      Comment

      • DanS26
        Solar Fanatic
        • Dec 2011
        • 994

        #4
        If one of your connections was loose enough to cause this...then there is a HIGH likelihood that there are other loose connections in other parts of the system. I would highly recommend that you have your installer prove to your satisfaction that all connections are torqued to the proper manufacturers specifications.

        He needs to use a properly calibrated torque screwdriver on every connection. Sadly most electricians do not use torque tools on smaller connections and just go by feel.

        Comment

        • Smitty
          Junior Member
          • Aug 2015
          • 20

          #5
          +1 on the loose connection

          Comment

          • squelch
            Junior Member
            • Aug 2015
            • 11

            #6
            Originally posted by DanS26
            If one of your connections was loose enough to cause this...then there is a HIGH likelihood that there are other loose connections in other parts of the system. I would highly recommend that you have your installer prove to your satisfaction that all connections are torqued to the proper manufacturers specifications.

            He needs to use a properly calibrated torque screwdriver on every connection. Sadly most electricians do not use torque tools on smaller connections and just go by feel.
            Yes, torque screwdriver would be great. is it out on the market ? im also not aware of that.

            Comment

            • DanS26
              Solar Fanatic
              • Dec 2011
              • 994

              #7
              Originally posted by squelch
              Yes, torque screwdriver would be great. is it out on the market ? im also not aware of that.
              Are you a DIY'er? If you made these connections, then go to Lowes or HD and get the proper tool. Cost about $100.....don't play with fire.

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                Amazon has a great gunsmiths torque screwdriver that takes hex bits, so slot, square, star, hex, phillips, posi-torque can all be handled.

                With fuses, you get an extra failure point, the grip fit between the springs and the fuse body, a little resistance, it gets warm and oxidizes, gets warmer and oxidizes more....... I see the upper fitting is a bit smoked too, which leads me to think gripper fit, not the wire clamp.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • squelch
                  Junior Member
                  • Aug 2015
                  • 11

                  #9
                  guys, what should be the normal temp of the termination ?
                  ambient temp 30 C and im getting 50 C on the terminations , is this normal ?

                  Comment

                  • Mike90250
                    Moderator
                    • May 2009
                    • 16020

                    #10
                    Originally posted by squelch
                    guys, what should be the normal temp of the termination ?
                    ambient temp 30 C and im getting 50 C on the terminations , is this normal ?
                    Nope, connections should only be a degree or two warmer. I have to get 30amps going to show a degree rise.
                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    • squelch
                      Junior Member
                      • Aug 2015
                      • 11

                      #11
                      my reading is 26A dc
                      so the possibility of heating this up is the loose connection issue ?

                      Comment

                      • SunEagle
                        Super Moderator
                        • Oct 2012
                        • 15179

                        #12
                        2 wires on damaged fuse holder

                        Is there any reason why there are 2 wires connected at the bottom of the first 2 fuse holders and only one wire on the other fuse holders?

                        Just thinking that besides a loose connection you might have exceeded the amp rating of that fuse holder.

                        Comment

                        • sensij
                          Solar Fanatic
                          • Sep 2014
                          • 5074

                          #13
                          Originally posted by SunEagle
                          Is there any reason why there are 2 wires connected at the bottom of the first 2 fuse holders and only one wire on the other fuse holders?

                          Just thinking that besides a loose connection you might have exceeded the amp rating of that fuse holder.
                          Not just amp rating, but fuse block terminations are usually rated to accept only a single wire. Putting two in almost guarantees a poor connection. If you really need two wires going into the fuse, using Twin wire ferrules is one good way to do it.
                          CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                          Comment

                          • SunEagle
                            Super Moderator
                            • Oct 2012
                            • 15179

                            #14
                            Originally posted by sensij
                            Not just amp rating, but fuse block terminations are usually rated to accept only a single wire. Putting two in almost guarantees a poor connection. If you really need two wires going into the fuse, using Twin wire ferrules is one good way to do it.
                            Good point.

                            Two wires on the same terminal connection can heat differently and expand at different rates causing motion and a loose connection.

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by SunEagle
                              Is there any reason why there are 2 wires connected at the bottom of the first 2 fuse holders and only one wire on the other fuse holders?Just thinking that besides a loose connection you might have exceeded the amp rating of that fuse holder.
                              Not to mention compliance and workmanship issues.
                              MSEE, PE

                              Comment