Sunny Boy 4000TL-US-22
A POCO in the US would not save any money doing it that way.Comment
208Y/120 service is common to apartment buildings who then take the neutral and two of the three phase conductors to supply each apartment's panel. The result is two 120V feeds which have 208V between the two line conductors instead of 240V.
But you are not likely to be installing a GTI in an apartment.
Also common in areas where air conditioning was first introduced while it was inefficient and required more power than it does today is what is called a high-leg delta. One of the three (or two) 240V transformer secondaries is center tapped to provide 120-0-120 service for most of the loads, but the third phase conductor is routed only to the panel or disconnect that supplies the A/C. Still not 208V, although the voltage from the high leg to the neutral will be 208V. That connection option is deliberately never used.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
Sure, that's true if you need to install a new transformer in order to establish service. But you generally want to use an existing transformer with excess capacity wherever possible. If you need to deliver single phase service and the nearest existing transformer with excess capacity is tri-phase then 208V may well be your cheapest option.Comment
I have one going in next week or so that is 3 phase 208v
This is with solar edge which can be either 208 or 240.
In this case we are using 3 inverters to balance the systems across phases.
Easy peasy
This is why most will allow either 208 or 240.
They do make a 3 phase inverter but would have taken 4 inverters instead of three on this job.NABCEP certified Technical Sales Professional
Biggest issue with going the "short cut" way is that will put an imbalance on the transformer by increasing the load on one phase. Having load imbalance causes the transformer to heat up and lose efficiency. If you owned that transformer you would be paying for those loses and your electric bill would be higher without any benefits. IMO that is not less costly.Comment
Last 60kw single phase transformer cost 11,000.00 installed by pocoNABCEP certified Technical Sales Professional
I can't get them for much less than that.
But I only buy the TL-US-22NABCEP certified Technical Sales Professional
The TL-US series requires 240 volt service to sell power back to the utility. The "secure power" feature does in fact output 120 volts, which is usable during power outages only.Comment
And it does not require one of those voltages just to sell back, it requires it to produce its full rated power at all. It is a grid tie inverter at heart, even though it has the option to install the off-grid Secure Power Supply (SPS) module. That module operates in a very limited scope without needing the batteries of a typical off-grid or hybrid installation.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment