    Day vs Night Load Profiles : Calculation Help

    I am getting myself confused with calculating the required array and battery size when faced with different day and night time load profiles. Maybe I am totally not getting how the math works, however it seems in a typical calculation, the total loads to be driven and the number of hours ( along with a host of other inputs - Depth of discharge, days of autonomy, insolation ...etc) are used. Especially with the hours of use for each load, I don't see a distinction being made between daytime and night requirements. I have a situation where the load profile at night is very different from the load profile during the day and I am not sure how to calculate the required array size to handle the daytime loads whilst at the same time charging the batteries for night time loads. I am thinking the batteries should be sized only to support the reduced night time load profile with a certain autonomy period built in.

    Can anyone share a sample calculation of how this works, assuming you have a daytime load profile about 3 times as large as what the night time profile is? ( told you I was getting myself confused.). Someone clear the confusion for me! thxx
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    For about 4 or 5 hours in daylight, your loads are running directly off the PV panels and are not subject to the 100% overhead that battery powered loads need to use. However, your active daytime loads reduce the amount of power that is available to recharge the depleted batteries.

    * 100% overhead:
    20% loss from panels not producing nameplate power when warm
    20% loss battery recharge losses
    5% charge controller losses (MPPT)
    15% loss inverter overhead/efficiency
    (dang, I can't recall that last 20%)
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • SunEagle
      Super Moderator
      • Oct 2012
      • 15164

      #3
      Originally posted by Mike90250
      For about 4 or 5 hours in daylight, your loads are running directly off the PV panels and are not subject to the 100% overhead that battery powered loads need to use. However, your active daytime loads reduce the amount of power that is available to recharge the depleted batteries.

      * 100% overhead:
      20% loss from panels not producing nameplate power when warm
      20% loss battery recharge losses
      5% charge controller losses (MPPT)
      15% loss inverter overhead/efficiency
      (dang, I can't recall that last 20%)
      That's called memory loss.