I didn't check the numbers/calcs - but IMO going with 3/4 just makes life easier for 4x10AWG or 8x12AWG.
And isn't much more $.
BTW - that include a ground wire in the fill calc's? Or planning on running that outside the conduit? If it's inside the conduit it has to be counted for conduit fill (but wouldn't count for current de-rating purposes)
I think 9x12AWG still fit's in theory in 1/2" EMT - but it'll be a PITA I think.