So, What's anyone doing to comply with Rapid Shutdown?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Rocksteady2R
    Junior Member
    • Jul 2014
    • 34

    #1

    So, What's anyone doing to comply with Rapid Shutdown?

    Deadline's coming up, and most string inverters are still up a creek w/o a solution... I know some of our ops guys are trying to find the right equipment to do it as a kind of 3rd party... Is that really the only feasible solution?

    I understand, as far as I've read, that SolarEdge and Enphase (and other Micro's) are compliant, but they're not more than 10% of our business, if that.

    What're ya'll coming up with for solutions?
  • inetdog
    Super Moderator
    • May 2012
    • 9909

    #2
    You will find some DC combiners with rapid shutdown circuitry. I have no idea how well they work or what they cost.
    SunnyBoy 3000 US, 18 BP Solar 175B panels.

    Comment

    • ButchDeal
      Solar Fanatic
      • Apr 2014
      • 3802

      #3
      Originally posted by Rocksteady2R
      Deadline's coming up, and most string inverters are still up a creek w/o a solution... I know some of our ops guys are trying to find the right equipment to do it as a kind of 3rd party... Is that really the only feasible solution?

      I understand, as far as I've read, that SolarEdge and Enphase (and other Micro's) are compliant, but they're not more than 10% of our business, if that.

      What're ya'll coming up with for solutions?
      We have made our base system be SolarEdge.
      For Battery backup we would just have to add a disconnecting combiner usually the birdhouse.
      OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

      Comment

      • Amy@altE
        Solar Fanatic
        • Nov 2014
        • 1023

        #4
        We've been on NEC 2014 here in MA for a while. Midnite Solar's Disconnecting Combiner Box with Birdhouse has been accepted by the inspectors here.

        For larger systems, and systems that need Arc Fault Detection too, SolarBOS has got some sweet products.

        If you are using SolarEdge, make sure you get the Rapid Shutdown kit that has the required cables and firmware update, it is not installed by default.
        Solar Queen
        altE Store

        Comment

        • inetdog
          Super Moderator
          • May 2012
          • 9909

          #5
          Originally posted by Amy@altE
          If you are using SolarEdge, make sure you get the Rapid Shutdown kit that has the required cables and firmware update, it is not installed by default.
          Just cutting the grid power to the SE inverter is not enough to cause all of the optimizers to go to 1V output soon enough to meet the Rapid Shutdown requirement?
          There does not seem to be any code requirement for a specific Rapid Shutdown switch as long as killing the electrical service connection will do that job and it is marked accordingly.
          SunnyBoy 3000 US, 18 BP Solar 175B panels.

          Comment

          • Amy@altE
            Solar Fanatic
            • Nov 2014
            • 1023

            #6
            Originally posted by inetdog
            Just cutting the grid power to the SE inverter is not enough to cause all of the optimizers to go to 1V output soon enough to meet the Rapid Shutdown requirement?
            There does not seem to be any code requirement for a specific Rapid Shutdown switch as long as killing the electrical service connection will do that job and it is marked accordingly.
            The cables in the shut down kit discharge the capacitors in the system, allowing it to quickly drop the voltage below the required range when power is cut. Without it, when cutting the power, the caps hold onto the voltage for too long. It's a minor upgrade, but required.
            Solar Queen
            altE Store

            Comment

            • SunEagle
              Super Moderator
              • Oct 2012
              • 15179

              #7
              Originally posted by Amy@altE
              The cables in the shut down kit discharge the capacitors in the system, allowing it to quickly drop the voltage below the required range when power is cut. Without it, when cutting the power, the caps hold onto the voltage for too long. It's a minor upgrade, but required.
              There must be bleeder resistors in there somewhere to control the capacitor discharge.

              Comment

              • Amy@altE
                Solar Fanatic
                • Nov 2014
                • 1023

                #8
                Originally posted by SunEagle
                There must be bleeder resistors in there somewhere to control the capacitor discharge.
                Yes, they do. Here's the install guide. http://www.solaredge.us/files/pdfs/p...tion_guide.pdf
                Solar Queen
                altE Store

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15179

                  #9
                  Originally posted by Amy@altE
                  Yes, they do. Here's the install guide. http://www.solaredge.us/files/pdfs/p...tion_guide.pdf
                  Interesting. I would have expected the resistors to be have a high wattage rating and possibly fins to dissipate the heat.

                  Based on those figures it looks like the resistor is maybe couple of watts but with a shrink wrap tubing around them so they can't put out that much heat.

                  Do these resistors have a standard rating or are they sized based on the input DC voltage and amp load of the array?

                  Comment

                  • Amy@altE
                    Solar Fanatic
                    • Nov 2014
                    • 1023

                    #10
                    Originally posted by SunEagle
                    Interesting. I would have expected the resistors to be have a high wattage rating and possibly fins to dissipate the heat.

                    Based on those figures it looks like the resistor is maybe couple of watts but with a shrink wrap tubing around them so they can't put out that much heat.

                    Do these resistors have a standard rating or are they sized based on the input DC voltage and amp load of the array?
                    Sorry, don't know.
                    Solar Queen
                    altE Store

                    Comment

                    • J.P.M.
                      Solar Fanatic
                      • Aug 2013
                      • 15048

                      #11
                      Originally posted by SunEagle
                      Interesting. I would have expected the resistors to be have a high wattage rating and possibly fins to dissipate the heat.

                      Based on those figures it looks like the resistor is maybe couple of watts but with a shrink wrap tubing around them so they can't put out that much heat.

                      Do these resistors have a standard rating or are they sized based on the input DC voltage and amp load of the array?
                      Will the shrink wrap change the temp. of the resistors ? --->>> resistance ?

                      Comment

                      • SunEagle
                        Super Moderator
                        • Oct 2012
                        • 15179

                        #12
                        Originally posted by J.P.M.
                        Will the shrink wrap change the temp. of the resistors ? --->>> resistance ?
                        The shrink wrap will make it harder to dissipate the heat when the resistor becomes the "dump load". If the wrap is not rated properly it could degrade depending on how many times the load is dumped and what the ambient temp is in the box.

                        I may be worried about nothing because the "load" being dumped is small and does not produce much heat.

                        I just know what dump load resistors look like and they have a lot of air around them to get rid of the heat quickly before it breaks down wire insulation.

                        Comment

                        • inetdog
                          Super Moderator
                          • May 2012
                          • 9909

                          #13
                          Originally posted by SunEagle
                          Interesting. I would have expected the resistors to be have a high wattage rating and possibly fins to dissipate the heat.

                          Based on those figures it looks like the resistor is maybe couple of watts but with a shrink wrap tubing around them so they can't put out that much heat.

                          Do these resistors have a standard rating or are they sized based on the input DC voltage and amp load of the array?
                          It looks like they have a standard rating, as the power difference among the optimizer models is small.

                          Since the optimizer's DC to DC converter operates at a relatively high frequency, the transfer and output capacitors can be small relative to the normal current handled by the unit. That means that a bleeder resistor which discharges those capacitors from >50V to <50V in under ten seconds will draw a current that does not dissipate much power.
                          It looks like the current drain of the bleeder resistors is constantly present during operation, so any power dissipated in the resistor will reduce the optimizer output by the same amount. The design is such that the power in the resistor is small and heat sinking is not necessary. The wires connected to the resistor terminals are probably more effective in carrying away heat than the surface of the resistor, and that path is not impeded by the shrink wrap.
                          SunnyBoy 3000 US, 18 BP Solar 175B panels.

                          Comment

                          • sensij
                            Solar Fanatic
                            • Sep 2014
                            • 5074

                            #14
                            Originally posted by SunEagle
                            Interesting. I would have expected the resistors to be have a high wattage rating and possibly fins to dissipate the heat.

                            Based on those figures it looks like the resistor is maybe couple of watts but with a shrink wrap tubing around them so they can't put out that much heat.

                            Do these resistors have a standard rating or are they sized based on the input DC voltage and amp load of the array?
                            The rapid shutdown occurs over 10 sec. The additional heat transfer offered by fins over that time scale would be insignificant.

                            A possibly error-prone stab at this:
                            A 10 HP VFD could have 1000 microfarad of capacitors in the DC bank. 10 HP = ~7500 W, a large-ish PV inverter size. Energy = 0.5 * C * V^2, = 0.5 * (1000 * 10^-6) * 500 ^2 = 125 J.

                            125 J dissipated over the 10 sec allowed by rapid shutdown is 12.5 W... so if this analysis is in the ballpark, the power rating of the resistor isn't too hard to meet.
                            CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                            Comment

                            • SunEagle
                              Super Moderator
                              • Oct 2012
                              • 15179

                              #15
                              heat loss clarification

                              inetdog, sensij

                              Thanks for the info. As I expected I was worried about nothing. Too small amount of energy to cause a lot of heat.

                              Comment

                              Working...