Problem in Trannergy Inverter

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • nalinpc3
    Junior Member
    • Nov 2013
    • 11

    #1

    Problem in Trannergy Inverter

    I installed the trannergy 3kW inverter in one of my project. But it's giving poor performance. chart.jpeg
    This is a single day power chart. I checked all connection, wires, and all possible things. But still same result. What would be the problem. I have installed several system but only this is giving this result. Pls help me to sort out this
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    i suspect it's overheating and cutting back till it cools off later in the day. is it exposed to the sun ? does it have good cooling airflow around it ?
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • nalinpc3
      Junior Member
      • Nov 2013
      • 11

      #3
      no

      Originally posted by Mike90250
      i suspect it's overheating and cutting back till it cools off later in the day. is it exposed to the sun ? does it have good cooling airflow around it ?
      It's having good air flow and it's not exposed to the sun and the temperature also maintaining good. It's totally normal. What if the MPPT is not functioning properly

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        First thing I see is jagged peaks and valleys. So it's a cloudy/sunny day. 10% to full power and back, every 5 minutes.

        2nd is the dip in the middle, which has got to be thermal. If the inverter is ok, then there are a bunch of panels or connections that are going bad in the heat. Are these NEW panels, seconds, used ? One dud would barely be noticeable, but I'm seeing half dozen bad ones cutting out in the heat, and recovering as it cools off.

        That's the only way i can explain the power dip. Or - check the connections in the boxes with an IR thermometer. Maybe a loose wire is heating up and going bad at high power.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • nalinpc3
          Junior Member
          • Nov 2013
          • 11

          #5
          Originally posted by Mike90250
          First thing I see is jagged peaks and valleys. So it's a cloudy/sunny day. 10% to full power and back, every 5 minutes.

          2nd is the dip in the middle, which has got to be thermal. If the inverter is ok, then there are a bunch of panels or connections that are going bad in the heat. Are these NEW panels, seconds, used ? One dud would barely be noticeable, but I'm seeing half dozen bad ones cutting out in the heat, and recovering as it cools off.

          That's the only way i can explain the power dip. Or - check the connections in the boxes with an IR thermometer. Maybe a loose wire is heating up and going bad at high power.
          OK I will check. They are brand new and even I change the wire also. But still the same But as I observe the voltage is steady. Anyway I will check the connections. thank you for your help

          Comment

          • nalinpc3
            Junior Member
            • Nov 2013
            • 11

            #6
            Originally posted by nalinpc3
            OK I will check. They are brand new and even I change the wire also. But still the same But as I observe the voltage is steady. Anyway I will check the connections. thank you for your help
            You can check online through this portal. give me some relief

            Comment

            • nalinpc3
              Junior Member
              • Nov 2013
              • 11

              #7
              Originally posted by nalinpc3
              You can check online through this portal. give me some relief
              http://log.trannergy.com/Terminal/Te...52&key=7HE6G89
              and this is mostly happening all the time but in sunny days it will shows more fluctuations.
              If I don't. Have a thermal scan what can I do for finding bad connections.