I'm trying to understand the readings I'm getting off my solar panels to try to determine if something isn't quite right. Hoping to find someone to answer this who has a deep understanding of solar panels and how series connections, shading, and bypass diodes work.
I have a SolarCity install that I'm monitoring and I feel like it's not producing what it should during partial shade. So I'm going to explain this in detail and hope someone can explain what's happening.
I have 14 panels arranged in 2 strings in series of 7 panels. The AAB inverter has inputs for 2 separate strings. In full sun both strings produce almost exactly the same voltage and current. Panels are made by Canadian solar, 255 W I think.
Neighbor has some big palm trees that start to shade the array mid afternoon. One string is in full sun. The other is partially shaded. The shadow covers one panel completely and 2 other panels 1/2 diagonally. So the shaded string has 4 panels in full sun and 3 panels which are probably fully dead.
The sunny string has these readings: 193 V - 5.2 A - 1003.6 W
The shaded string has these readings: 111 V - 3.2 A - 355.2 W
So - here's my question.
The voltage drop is about right on. 111 / 193 = 4 / 7 - just what you would expect with 4 panels working and 3 dead.
but ...
Why is the current down from 5.2 A to 3.2 A ?
Shouldn't I be getting 577.2 W? Why am I missing 222 W?
If I had just 4 panels in the string in full sun I should get 111 V - 5.2 A - 577.2 W
The bypass diodes in the system should bypass the shaded panels allowing the full current of the sunny panels.
So - what am I missing here? There's something I don't understand.
I have a SolarCity install that I'm monitoring and I feel like it's not producing what it should during partial shade. So I'm going to explain this in detail and hope someone can explain what's happening.
I have 14 panels arranged in 2 strings in series of 7 panels. The AAB inverter has inputs for 2 separate strings. In full sun both strings produce almost exactly the same voltage and current. Panels are made by Canadian solar, 255 W I think.
Neighbor has some big palm trees that start to shade the array mid afternoon. One string is in full sun. The other is partially shaded. The shadow covers one panel completely and 2 other panels 1/2 diagonally. So the shaded string has 4 panels in full sun and 3 panels which are probably fully dead.
The sunny string has these readings: 193 V - 5.2 A - 1003.6 W
The shaded string has these readings: 111 V - 3.2 A - 355.2 W
So - here's my question.
The voltage drop is about right on. 111 / 193 = 4 / 7 - just what you would expect with 4 panels working and 3 dead.
but ...
Why is the current down from 5.2 A to 3.2 A ?
Shouldn't I be getting 577.2 W? Why am I missing 222 W?
If I had just 4 panels in the string in full sun I should get 111 V - 5.2 A - 577.2 W
The bypass diodes in the system should bypass the shaded panels allowing the full current of the sunny panels.
So - what am I missing here? There's something I don't understand.