How large Gen Set required for Hybrid PV System?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • kashif5
    Junior Member
    • Dec 2014
    • 6

    #1

    How large Gen Set required for Hybrid PV System?

    Hi All,

    I've a query about Hybrid PV System.

    I want to install a PV system that can be synced with grid and gen-set. i want to know if there is any ratio limitation for pv and genset ? I read that with SMA fuel controller, 600 KW PV can be installed with 1MW Gen-set. so i suppose that without SMA fuel controller, it should be more less for 1MW Gen-set. am i right or not? is there any proper information for that? like if I've a gen set of 1MW, then how big PV can be installed? or i can install any size pv with any size gen-set?

    Regards
    Kashif
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    1 Mw genny? Are you supplying the city?
    MSEE, PE

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #3
      Hybrid PV Systems cannot sell generator power to the grid, only the 48V battery power. batteries charged by the sun, not a diesel genset.
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        Not to mention very foolish to sell battery power to the grid.
        MSEE, PE

        Comment

        • kashif5
          Junior Member
          • Dec 2014
          • 6

          #5
          Originally posted by Sunking
          1 Mw genny? Are you supplying the city?

          its an industrial solution. 1 MW get-set is normal in industry.

          Comment

          • kashif5
            Junior Member
            • Dec 2014
            • 6

            #6
            Originally posted by Mike90250
            Hybrid PV Systems cannot sell generator power to the grid, only the 48V battery power. batteries charged by the sun, not a diesel genset.
            its not selling energy to grid. PV systems sync with grid (when available) and get-set. so if grid is not available then it detects current from gen-set. but in that case i dont know that for a pv of lets say 500KW, how large gen-set is required. hope it clear.

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #7
              Hybrid PV cannot sync your genset to the grid, you will have to chose using grid power, or genset power.

              Most inverters have small 60A transfer switches, so you can't use that large of a genset with them
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • kashif5
                Junior Member
                • Dec 2014
                • 6

                #8
                Originally posted by Mike90250
                Hybrid PV cannot sync your genset to the grid, you will have to chose using grid power, or genset power.

                Most inverters have small 60A transfer switches, so you can't use that large of a genset with them

                i think i m not clear in my question.

                I'm not trying to sync gen-set with grid. what I'm trying to do is "Sync PV with Grid" as per safety feature of PV, PV need a grid to run (unless its off-grid). PV sense current from grid and keep producing electricity. as soon as grid goes down, PV shutdowns. so in case grid is not available, gen-set is used to sync with PV so that PV may keep producing electricity.

                Now question is: for 500KW PV, how large gen-set should be there to sync with PV. if gen-set is small then PV can destroy get-set by reverse flow of current. thats all i know (may be I'm wrong). but i dont know any exact ratio of Pv and Gen-set output.

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #9
                  i think i m not clear in my question.
                  Yep. You are talking really big, industrial size install. 10Kw and under is small, homeowner size and most likely 98% of the installs globally..

                  500Kw is large enough for a small city, and you will need to have an industrial electrical engineer manage it for you. Schneider Electric http://www.schneider-electric.us/sit...comm-util.page has trailer sized solar inverters. your engineering staff will need to work with them to find the answers to your questions.

                  This forum is mostly consumer / homeowner oriented, not utility scale.
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • SunEagle
                    Super Moderator
                    • Oct 2012
                    • 15184

                    #10
                    I also don't think there is any gen set that can mimic the grid and fool a pv system to keep generating. Unless of course the gen set is the size of a Utility generating plant at maybe 60MW but I could be wrong.

                    Comment

                    • kashif5
                      Junior Member
                      • Dec 2014
                      • 6

                      #11
                      Originally posted by SunEagle
                      I also don't think there is any gen set that can mimic the grid and fool a pv system to keep generating. Unless of course the gen set is the size of a Utility generating plant at maybe 60MW but I could be wrong.

                      YES thats wht i was saying....trying to create replica of grid.... I give you an example.... for a complete set of 4MW gen-set (4 Gen of 1 MW each), we are installing 740 KW PV. but still not sure what is exact ratio. currently we are trying to keep it 1/3 of gen.... but I want to know if there is any actual data.

                      thanks for your rtime.

                      Comment

                      • SunEagle
                        Super Moderator
                        • Oct 2012
                        • 15184

                        #12
                        Originally posted by kashif5
                        YES thats wht i was saying....trying to create replica of grid.... I give you an example.... for a complete set of 4MW gen-set (4 Gen of 1 MW each), we are installing 740 KW PV. but still not sure what is exact ratio. currently we are trying to keep it 1/3 of gen.... but I want to know if there is any actual data.

                        thanks for your rtime.
                        I do not know what the correct and safe ratio would be. I would suggest you contact a local Engineering outfit for your answers.

                        Comment

                        • russ
                          Solar Fanatic
                          • Jul 2009
                          • 10360

                          #13
                          Originally posted by SunEagle
                          I do not know what the correct and safe ratio would be. I would suggest you contact a local Engineering outfit for your answers.
                          For a project that size they have an engineering firm they are working with - even in Pakistan. Probably this is a bean counter trying to make points with the boss.
                          [SIGPIC][/SIGPIC]

                          Comment

                          • paulcheung
                            Solar Fanatic
                            • Jul 2013
                            • 965

                            #14
                            I don't get this, If the site is going to run the generator as large as the demand, where is the PV coming? for what reason?

                            Comment

                            • inetdog
                              Super Moderator
                              • May 2012
                              • 9909

                              #15
                              Originally posted by paulcheung
                              I don't get this, If the site is going to run the generator as large as the demand, where is the PV coming? for what reason?
                              To reduce the load on the generator (and therefore the fuel consumption) during the hours where PV is producing.
                              As long as the PV does not bring the generator into a situation where the prime mover is operating inefficiently, it will be able to reduce overall costs.
                              It is critical to this kind of design that the load never go lower than the PV output, with maybe even a 50% safety factor. Otherwise, to prevent destructive backfeeding of the generator, the PV will have to be automatically throttled down.
                              SunnyBoy 3000 US, 18 BP Solar 175B panels.

                              Comment

                              Working...