I have a project where I am combing 6 inverters for a grid-tie system:
(4) SMA SB8000TL's
(2) SMA SB6000TL-22's
The Grid is 208Y 3-phase, 225A
I am planning on using an Eaton load center (3-phase), using 2-pole breakers for the inverters. 50A breakers for the 8's and 40A for the 6's. Output for the 8's is 38.5A and 25A for the 6's, which gives me a total of 204A, upped to 255A (125%). The panel I am looking at is a 225A rated CH series, which would allow me 270A (120%).
Does this seem feasible?
Oh, regarding existing loads on the utility, there is only an old 225A panel that has a pump attached (was all to be removed / demolished before the client decided they wanted to have solar). So we are going to simply tap at the meter (or splice box) and leave the existing alone.
(4) SMA SB8000TL's
(2) SMA SB6000TL-22's
The Grid is 208Y 3-phase, 225A
I am planning on using an Eaton load center (3-phase), using 2-pole breakers for the inverters. 50A breakers for the 8's and 40A for the 6's. Output for the 8's is 38.5A and 25A for the 6's, which gives me a total of 204A, upped to 255A (125%). The panel I am looking at is a 225A rated CH series, which would allow me 270A (120%).