    Aluminium cables

    Hello solar buddies,

    I want to ask you one question. Do you know any good reason why aluminium cables (DC cables) are not used in PV systems. Every MW project is with expensive copper cables. Thanks in advance.
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    Because AL can be very dangerous with dis-similar metal connections, and takes training to terminate properly. In addition it takes much larger AL conductors to match copper in current carrying capacity.
    MSEE, PE

    Comment

    • Solarex
      Junior Member
      • Feb 2010
      • 2

      #3
      I see but when we have 5 MWp PV project and DC cables are 200-300-400 m from combiner (junction) box to Central inverter then AL cables with UV resistant seem to be more profitable.

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        I'm going to be pulling #2 aluminum cable for about 900' for my house & pump power. I'd rather use copper, but the price of #4 copper cable was astronomical. So I have to use the proper splices and NoOx coatings at the joints. Internal runs will be copper, just the long lengths will be aluminum .
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • mountain
          Member
          • Nov 2009
          • 56

          #5
          Single conductor aluminum wire (AL-RW90) is generally installed in conduit & is available in AWG#6 & larger.

          ACWU (armoured aluminum cable) is widely used in Canada at a fraction of the price of similar ampacity copper cable. For direct-bury use, it definately provides the best overall price performance for long underground runs. It is available in sizes AWG#6 & larger. Anit-shorts & correct terminating connectors must be used. Electricians only. It is widely available in the USA and is UL cert.

          However, you must be a registered electrical contractor (or engineer) to even buy aluminum wire & cable. In which case you know the correct terminating lugs & joint compounds will be used. Careful attention to bend radius is more critical than with copper, and AL wire and cable can be easily injured during installation.

          Voltage-drop calculations are part of any electrical design over a long feeder (like 900'), and Al has higher resistivity than Cu. Even so, in a direct price comparison, Al almost always wins over Cu. Cu gets used where the voltage-drop rule (5% max feeder + branch) simply rules out Al.

          For the average home do-it-yourself solar guy, copper is what is available & what should be generally used.

          If your project is of such a scale that economics dictate AL wire or cable, then using an electrical contractor will likely save you lots of $$$ in the long run... (true!) Your house won't burn down and your insurance will still be valid if it does.