5.75kw solarsystem connected to a 100 amp Panel via combiner panel ?
Collapse
X
-
-
Alternative?
I tried to read through all the posts and hope that this was not already mentioned, but here in WV you do not have to go through your panel box. The only difference here is they wanted a breaker panel mounted outside to handle the 300AMPs coming into the inverter, but they do not require the inverter to be directly tied to the existing panel.
Here is the link to the wiring options: https://www.firstenergycorp.com/cont...connection.pdf
You will notice close to the bottom there is an option for wiring separate from the main panel.Attached FilesComment
-
I tried to read through all the posts and hope that this was not already mentioned, but here in WV you do not have to go through your panel box. The only difference here is they wanted a breaker panel mounted outside to handle the 300AMPs coming into the inverter, but they do not require the inverter to be directly tied to the existing panel.
Here is the link to the wiring options: https://www.firstenergycorp.com/cont...connection.pdf
You will notice close to the bottom there is an option for wiring separate from the main panel.
Too bad they did not include a one-line diagram of it the way they did for the other interconnections, since that would have made it clearer.Last edited by inetdog; 03-20-2014, 10:36 PM.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
There was a misconception when I first wired mine and they suggested this setup, but it would have resulted in needing another inspection. I have a 200 amp service and it was no problem just adding it to a duel 40 amp breaker in the main panel. If I had a problem with 100 amp service I would try to connect without entering the main service panel, but I only know my state and inspector. Here they really didn't know what they were looking at, so it was no problem getting everything passed. Plus I paid a master electrician to tie it all in. Though it added $800 to the install the sound mind is worth it. I would still be surprised if they would not allow this type of connection, especially if a 100 amp breaker was added.Comment
-
100 amp panel will only take a 20 amp breaker of additional generation.
As was mentioned, if you have a 125 amp panel there would be no problem with a 30 amp of additional generation because you have a 100 amp main breaker.
The twenty percent rule would give you 125/5=25 amps additional available making a total of 125+25=150 amp total maximum. Because it would be a 125 amp panel with only 100 amp coming through the 100 amp main, you could easily accommodate 30 amps.
If as i suspect from your statements, it is a 100 amp panel with a 100 amp breaker, it can only accommodate a 20 amp breaker for generation.
An upgrade to 200 amps if your incoming wire will allow would bring your house to modern standards and allow 40 amp breaker for generation.
$1200 to $1500 is a fair and good price for the change over.
By the way, if your panel is a Zinsco panel, it would be wise to change for safety reasons. Zinsco is no longer manufactured and they are known to not break causing fires.Comment