Read your panel specs
In there they will give you a temperature coefficient
Generally it is somewhere around .36% per degree C
So take your panel open circuit voltage Multiply that by the percent
In the example above you would multiply by .0036.
Multiply that by the difference in temperature in degrees C from 25.
In your case that number would be 26 as record low was -1C
That will give you the open circuit voltage increase at the low temp
Now add to that the open circuit voltage of the panel to get panel open circuit voltage. This will give you the value for one panel. Then multiply that by how many panels are in a string.
In there they will give you a temperature coefficient
Generally it is somewhere around .36% per degree C
So take your panel open circuit voltage Multiply that by the percent
In the example above you would multiply by .0036.
Multiply that by the difference in temperature in degrees C from 25.
In your case that number would be 26 as record low was -1C
That will give you the open circuit voltage increase at the low temp
Now add to that the open circuit voltage of the panel to get panel open circuit voltage. This will give you the value for one panel. Then multiply that by how many panels are in a string.