  • rsilvers
    replied
    Originally posted by solarix
    "A 400 service can still be a backfeed problem as the busbars are only 200A limiting you to no more than 40A backfeed each - or 32A inverter max
    I have 150 amp main breakers in each. So that is 90 each that can be back fed.

    Leave a comment:


  • solarix
    replied
    "So... I have 400 amp service at my house that is split into three main panels. Two of the panels are 200 amp bus bars with 150 amp breakers. A third is a 100 amp panel that is not part of this question. From what I can tell by reading here, I can have 90 amp back-fed solar breakers in the two larger panels."

    A 400 service can still be a backfeed problem as the busbars are only 200A limiting you to no more than 40A backfeed each - or 32A inverter max - or 7.7kW. Most utilities want you to have a single disconnect for all your solar backfeed so you can't split it up between several panels. Solution is to have less than 200 of absolute max potential load on one of the 200 busbars - then you can backfeed up to 200A no problem. You just need to label it so that additional loads can't be added.

    Leave a comment:


  • solarix
    replied
    A 200 panel can be backfed with up to 7.7kW of inverters. You just need an AC combiner (for your three 15A breakers) to bring your three inverters together then run that into a 40A breaker in the main panel. Make it a dedicated panel with no other loads - needs to be labeled "Dedicated Combiner - Do Not Add Loads to the Panel". The imbalance from the one 120Vac inverter is not a problem.

    Leave a comment:


  • rsilvers
    replied
    So... I have 400 amp service at my house that is split into three main panels. Two of the panels are 200 amp bus bars with 150 amp breakers. A third is a 100 amp panel that is not part of this question. From what I can tell by reading here, I can have 90 amp back-fed solar breakers in each of the two larger panels.

    I have learned so much from this, and answered my own questions. A few days ago I asked my town inspector some of this and he said "I would rather be talking to a licensed electrician as he would know what you need."
    Last edited by rsilvers; 04-24-2016, 10:22 PM.

    Leave a comment:


  • inetdog
    replied
    Originally posted by Naptown
    Even so with a sub panel arrangement it is possible to limit the OCPD to lower than the 120% rule. The issue is his 1 kw system puts a little over 4A but has a 15A circuit breaker.
    In this case a 6 or 8 circuit solar combiner/sub panel to combine all the arrays will allow him to connect all of them to 1 2 pole 40A breaker and feed the 200A panel no problem.
    Which is exactly what I said......

    Leave a comment:


  • Naptown
    replied
    Originally posted by inetdog
    I thought so too until I read the exact wording of the code (2011):

    (2) Bus or Conductor Rating. The sum of the ampere ratings of overcurrent devices in circuits supplying power to a busbar or conductor shall not exceed 120 percent of the rating of the busbar or conductor.

    Exception: Where the photovoltaic system has an energy
    storage device to allow stand-alone operation of loads, the
    value used in the calculation of bus or conductor loading
    shall be 125 percent of the rated utility-interactive current
    from the inverter instead of the rating of the overcurrent
    device between the inverter and the bus or conductor.

    Nothing about using the rated maximum current for a non-battery GTI.

    Remember that the power input from the panels is limited, but depending what kind of output voltage range the GTI has, the current may be more than that corresponding to the input power at the nominal output voltage.
    Even so with a sub panel arrangement it is possible to limit the OCPD to lower than the 120% rule. The issue is his 1 kw system puts a little over 4A but has a 15A circuit breaker.
    In this case a 6 or 8 circuit solar combiner/sub panel to combine all the arrays will allow him to connect all of them to 1 2 pole 40A breaker and feed the 200A panel no problem.

    Leave a comment:


  • inetdog
    replied
    Originally posted by Naptown
    Correct the total of all. But the governing ampacity is the maximum output from the inverters not necessarily the total of the breaker ampacity.
    Remember that inverters and solar are current limited so they will never produce more than the Isc amperage as opposed to a POCO line that could go up into the thousands of amps.
    I thought so too until I read the exact wording of the code (2011):

    (2) Bus or Conductor Rating. The sum of the ampere ratings of overcurrent devices in circuits supplying power to a busbar or conductor shall not exceed 120 percent of the rating of the busbar or conductor.

    Exception: Where the photovoltaic system has an energy
    storage device to allow stand-alone operation of loads, the
    value used in the calculation of bus or conductor loading
    shall be 125 percent of the rated utility-interactive current
    from the inverter instead of the rating of the overcurrent
    device between the inverter and the bus or conductor.

    Nothing about using the rated maximum current for a non-battery GTI.

    Remember that the power input from the panels is limited, but depending what kind of output voltage range the GTI has, the current may be more than that corresponding to the input power at the nominal output voltage.

    Leave a comment:


  • Naptown
    replied
    Originally posted by bcroe
    I think you are saying, it doesn't apply to the sub panel. But if the sub panel connects to a breaker on
    the main panel, is that breaker still limited to 20% of the main? Bruce Roe
    Correct the total of all. But the governing ampacity is the maximum output from the inverters not necessarily the total of the breaker ampacity.
    Remember that inverters and solar are current limited so they will never produce more than the Isc amperage as opposed to a POCO line that could go up into the thousands of amps.

    Leave a comment:


  • peakbagger
    replied
    Its a 25 year old Westinghouse main panel so I dont hold up much hope on getting any specs on the bus bar rating on the web . Down rating the main breaker is intriguing. The biggest load in the house is an oven and on rare occasions a welder but I expect I could drop down to a 150 AMP main breaker and never notice it. Given the current real estate around the existing panel, fitting in an auxiliary panel would be difficult or might require moving the main panel. If I had to move the main panel, I would probably just buy a new one with 250 AMP bus and a 200 Amp main breaker. Of course since I have to work with an electrician for a sign off, it may all come down to what he is comfortable with, nevertheless armed with options I can challenge him if he goes of on an expensive tangent.

    Thanks for all the input!

    Leave a comment:


  • inetdog
    replied
    Originally posted by bcroe
    Looking at my own Sq D QO main panel, each bus is 1" wide by 1/4" thick, pretty substantial. I
    wonder how their current rating can be found?

    The whole 120% idea is of course idiot proof. But the only way to reach current of the main +
    backfeed breaker in the bus, is put the 2 at one end, then put loads equaling more than 120%
    along the other end. That isn't sustainable, because when the backfeed stops, the main will drop.
    My loads certainly don't come anywhere near the capacity. A cure is to put the backfeed at the
    opposite end of the bus from the main. Then there is no way the source currents can be additive,
    feeding loads in the middle. Bruce Roe
    You cannot tell by looking, but if there is a part number you can check with the manufacturer. Or you can just check the part number of the whole panel with the manufacturer to see what ampacity bus is used in it.

    And the code already requires you to put the backfeed breakers at the other end of the bus from the main. (That is why they give you the extra 20%!)
    It does not make complete sense, since the bus overload will, as you say, occur only at the exact point along the bus that the 120% load connects. But that is the way it is written.

    There is no guarantee that the back feed will stop when you apply a 120% load (not a short circuit), so you can overload that one spot on the bus for as long as you want as long as the load does not exceed the sum of the two feeds.
    In theory, if the bus rating is based in part on the ability of the bus to transfer heat to unloaded parts of the bus, the overloaded contact point (with contact resistance) between the load breaker and the bus could overheat. (I am just playing devil's advocate here, not saying I agree with the rule.)

    Leave a comment:


  • bcroe
    replied
    Bus size

    Originally posted by inetdog
    Also, be careful with your words. A single backfed breaker at the main, without a subpanel is not
    limited to 20% of the main breaker size.
    The sum of the backed breaker(s) and the main must not exceed 120% of the bus rating. Even if
    you buy a panel with a pre-installed main breaker, you cannot assume that the bus rating of that
    panel is equal to the main breaker size.
    Manufacturers often use a 150A bus in their 100, 125 and 150A panels. And in some cases the bus
    rating of a 200A panel will be 225A.

    If you have a 200A main, with a 200A bus, you can still replace the 200A main with a 150A main
    and then be able to use up to 90A of back feed (240A - 150A).
    Looking at my own Sq D QO main panel, each bus is 1" wide by 1/4" thick, pretty substantial. I
    wonder how their current rating can be found?

    The whole 120% idea is of course idiot proof. But the only way to reach current of the main +
    backfeed breaker in the bus, is put the 2 at one end, then put loads equaling more than 120%
    along the other end. That isn't sustainable, because when the backfeed stops, the main will drop.
    My loads certainly don't come anywhere near the capacity. A cure is to put the backfeed at the
    opposite end of the bus from the main. Then there is no way the source currents can be additive,
    feeding loads in the middle. Bruce Roe

    Leave a comment:


  • inetdog
    replied
    Originally posted by bcroe
    I think you are saying, it doesn't apply to the sub panel. But if the sub panel connects to a breaker on
    the main panel, is that breaker still limited to 20% of the main? Bruce Roe
    There is a good argument as to the justifiability of applying the 120% rule to a subpanel which is only serving as a combiner, but particularly if there are other loads in the subpanel, it is technically governed by the same bus loading rule that applies to a main panel. It is just usually easier to meet that rule.
    The saving feature that this sort of subpanel combiner has is that the bus calculation at the main panel can be based not on the individual subpanel breakers or even the breaker at the main panel, but rather the main breaker at the subpanel.
    So you could take three 8A GTIs, run each of them through a 20A breaker into a subpanel with a 30A main breaker and connect that subpanel feeder to a 50A breaker in the main. The calculation at the main would then use the 30A figure and not 60A or 50A.

    Also, be careful with your words. A single backfed breaker at the main, without a subpanel is not limited to 20% of the main breaker size.
    The sum of the backed breaker(s) and the main must not exceed 120% of the bus rating. Even if you buy a panel with a pre-installed main breaker, you cannot assume that the bus rating of that panel is equal to the main breaker size.
    Manufacturers often use a 150A bus in their 100, 125 and 150A panels. And in some cases the bus rating of a 200A panel will be 225A.

    If you have a 200A main, with a 200A bus, you can still replace the 200A main with a 150A main and then be able to use up to 90A of back feed (240A - 150A).

    Leave a comment:


  • bcroe
    replied
    120%

    Originally posted by Naptown
    What you are describing on the sub panel works. the Sub panel would not be limited to the 120% rule. This panel should be clearly marked and is actually more of a combiner box than anything
    I think you are saying, it doesn't apply to the sub panel. But if the sub panel connects to a breaker on
    the main panel, is that breaker still limited to 20% of the main? Bruce Roe

    Leave a comment:


  • inetdog
    replied
    Originally posted by peakbagger
    I have always assumed that MPPT works the best when the panels are identical with the same exposure. I am not sure I want to risk impacting the inverter efficiency bty having two strings with widely different exposures. Plus one string is on a pole mount vs the new string is on a roof so the temps will be quite different.
    If the two strings are within 10% with respect to Vmp during the time that they are both producing significant power, the output of the inverter should be within about 5% of the sum of the two strings operated at their individual Vmp. But this general guideline affects primarily use of different types of panels.
    The only effect which can cause changes in the Vmp with identical panels will be temperature and partial shading. The temperature effect will not be enough to cause even a 5% difference in Vmp.

    The exposure of the panels will change Imp but will have a negligible effect on the Vmp at which that current is obtained. Xantrex did some experimental studies that confirmed that paralleling arrays that differer only in exposure will not cause any loss of power, and that any clipping loss caused by an overlap of the two arrays exceeding the capacity of the inverter for a short time at midday will be more than made up for by the extended hours of higher power operation.

    Leave a comment:


  • Naptown
    replied
    What you are describing on the sub panel works. the Sub panel would not be limited to the 120% rule. This panel should be clearly marked and is actually more of a combiner box than anything

    Leave a comment: