I have a sunsaver MPPT connected to a 230 watt panel charging liquid acid deep cycle to run a couple 12 v dc pumps and have been getting a external wiring error display. All wires and connections look good, I am at a lost and need to get the water pumping any ideas please?
Try our solar cost and savings calculator
Morningstar external wiring error?
Collapse
X
-
-
Haven't run into that problem with the Sun Saver MPPT
But what I would suggest is you disconnect everything from the charge
controller and hook the battery up first make sure it cycles through the
leds then stops on whatever the battery state is at.
Then hook up the solar panel be sure its hooked up the correct polarity
if there is no error I'm guessing you maybe hooking the pumps to the
load terminals and they my be drawing enough to cause the error but
not enough to give overload error. The other possibility if they are hooked
to the load terminals is the are generating a lot of noise that it is messing up
the charge controller.
If either of these things is a possibility then you should hook the pumps directly
to the battery terminals and give that a try.
Outside of that there is not much else I can say as you never included any specs
on the solar panel or pumps or how the pumps were wired in. -
Bet you anything you connected the panel before the battery. Battery is the first thing to be connected, and the last to be disconnected.
In addition your panel is too large for the controller. Reconnect everything in the right order, and double check polarity with a volt meter before connecting. Only 4 wires.MSEE, PEComment
-
I have had this system working steady for the past 3 years. The controller is supposed to be large enough for the panel, that was the whole reason I ordered it and replaced my old controller so I doubt that is the issue, I ordered it from the out fit in Arizona. The pumps are 3 amp bilge pumps, very small loads. Charge is up on bat.Comment
-
The panel will work fine its just that when you have good sun light the panel will
produce more then the charge controller will use i.e if it produces 16amp the controller
will clip it to its max of 15amp is all so you are not getting the full benefit of the over
200 watts max the controller uses.
Now as for the problem does it go away if you do not have the pumps hooked up
and you reset the charge controller by unhooking and hooking back up as stated
You have to understand as the pumps get older if these are one that use brushes
the can generate a lot of r.f. noise that can feed back to microprocessor controlled
charge controller that can interfere with its operation if hooked to the load terminals
That is not to say that it is the problem but you have to use the process of elimination
to trace down the problem.Comment