powering off grid 35 kwk per day. need advice!!!

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • luhrs69
    Junior Member
    • Aug 2015
    • 2

    #1

    powering off grid 35 kwk per day. need advice!!!

    Need to provide power in remote location. 100% off grid. Based on current home power bill We consume 35 kwk per day. I cant find any info to amount of solar panels it will take. I will install a bank of batteries just not sure how many (deep cell) will be required. I want to cool the house, use ice maker and all other creature comferts. This house is in a remote berzil beach island so HVAC is a must. Kicker is we are retired and limited income.

    thanks in advance
  • solar pete
    Administrator
    • May 2014
    • 1873

    #2
    Originally posted by luhrs69
    Need to provide power in remote location. 100% off grid. Based on current home power bill We consume 35 kwk per day. I cant find any info to amount of solar panels it will take. I will install a bank of batteries just not sure how many (deep cell) will be required. I want to cool the house, use ice maker and all other creature comferts. This house is in a remote berzil beach island so HVAC is a must. Kicker is we are retired and limited income.

    thanks in advance
    Howdy luhrs and welcome to Solar Panel Talk.

    What you want is totally doable but it will be expensive. The 35kWh (kilowatt hours) per day is helpful to get a bit of an idea, but a bit more info will be required. I think you need to do a lot of reading in the off grid section of the forum and then re think your plans to try to get that kWh number down. Remember when you have high drawing appliances you will generally need a very large system. Working out dfay time versus night time usage will be helpful too. You might find running a genny when you need to run the high drawing appliances will enable you to have a slightly smaller system. Any way you cut it though this system wont be cheap, as a total wild guess you will need somewhere between 30K and 60K.

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #3
      I can answer all your questions. The short answer is it will never happen and give it up before you waste any more time on this silliness. Let's start with the battery because it is very easy to calculate, and will end all hopes and dreams you have. You need a 48 volts 3600 AH battery. Now I know this may not mean much to you but this will you will clearly understand. A 48 volt 3600 AH battery weighs 10.500 pounds which require an EPA permit, yearly inspections by your local fire department for having a huge toxic waste dump in your home, and will cost you roughly $40,000 every 5 to 6 years with each replacement. Told you that was easy.............................................. .................................................. .................................................. ..........................................Panel Wattage required depends on your location at a minimum if you live in Tuscon AZ will be 10,000 watts. If you live in Average USA requires 15,000 watts............................................. ..............................Like I said will never happen. If you are foolish enough to do it, for the first 5 years instead of paying the mean ole greedy power company 10 to 15 -cents per Kwh, you now pay over $1.50 per Kwh or a 1000% rate increase you so generously volunteered to pay.
      MSEE, PE

      Comment

      • ckhorne
        Junior Member
        • Nov 2012
        • 29

        #4
        Originally posted by Sunking
        Like I said will never happen. If you are foolish enough to do it, for the first 5 years instead of paying the mean ole greedy power company 10 to 15 -cents per Kwh, you now pay over $1.50 per Kwh or a 1000% rate increase you so generously volunteered to pay.
        If he's on a remote beach island off of Brazil, I don't think the EPA will come knocking and their power is likely a lot more expensive than average US.luhrs69 - it sounds like you need to start with lowering your expectation and finding out how to cut down your usage by half or more. Conservation is the first step to going off grid.

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15210

          #5
          Originally posted by ckhorne
          If he's on a remote beach island off of Brazil, I don't think the EPA will come knocking and their power is likely a lot more expensive than average US.luhrs69 - it sounds like you need to start with lowering your expectation and finding out how to cut down your usage by half or more. Conservation is the first step to going off grid.
          I agree that even though electrical power from a POCO would be more there than in the US an off grid solar battery system for 35kWh daily will be more than $100,000 and require the batteries (about 40% of that) to be replaced in 4 years.

          The OP needs to determine how much power he can live with (below that 35kWh) and while expensive go with a generator set instead of batteries. Even with high fuel costs to run that generator it will be less then purchasing and maintaining a large battery system. Or get connected to the grid and use the gen set when the power goes out.

          A smaller electrical footprint could improve the cost comparison of gen set to solar/battery but not at 35kWh per day.

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            Originally posted by ckhorne
            . Conservation is the first step to going off grid.
            Yep and Air Conditioning is the first thing that has to go away. Brazil has some of the least expensive electric rates in the world with an endless supply of sugar cane to burn for fuel. Going off-gris is going to cost him some 10 to 15 times more than buying it. Never going to happen on a Limited Income. When you go off grid there is no such thing as a BUDGET, sky is the limit because you have more money than what you know to do with. So you do not mind throwing money away, plenty more where that came from.
            MSEE, PE

            Comment

            • luhrs69
              Junior Member
              • Aug 2015
              • 2

              #7
              Off grid in Brazil

              Wow, I thought this would be a little easer then it appears to be. THANK ALL FOR YOUR INPUT.... Not what I wanted to here but it has opened my eyes a little wider. As I had said I'm 100% off grid and this is not by choice. I only have one way to have power brought in by law and in the area it would mean cutting through mangrove. This is prohibited. If I down size to a few lights, fans and refer will this be affordable? Well I guess that is an open question.... Where should I begin. I have $8,000 to spend.

              Thanks

              Comment

              • Naptown
                Solar Fanatic
                • Feb 2011
                • 6880

                #8
                Panels about a dollar a watt for grid tie
                Racking about 30 cents a watt
                Charge controller 500-1800
                Inverter 2000
                Wires Etc 500
                Batteries ?
                Run the battery design link below
                Sun hours are in the gaisma link below
                3-4 kWh per day may be doable for the budget. Batteries are the wild card.
                NABCEP certified Technical Sales Professional

                [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15210

                  #9
                  Originally posted by luhrs69
                  Wow, I thought this would be a little easer then it appears to be. THANK ALL FOR YOUR INPUT.... Not what I wanted to here but it has opened my eyes a little wider. As I had said I'm 100% off grid and this is not by choice. I only have one way to have power brought in by law and in the area it would mean cutting through mangrove. This is prohibited. If I down size to a few lights, fans and refer will this be affordable? Well I guess that is an open question.... Where should I begin. I have $8,000 to spend.

                  Thanks
                  Until you can drop your usage to only 3 to 4kWh per day you won't be able to build an off grid system to meet your electric needs for anywhere close to $8,000.

                  Unfortunately a better investment for that $8000 would be in a generator and fuel storage.

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #10
                    Originally posted by Naptown
                    Panels about a dollar a watt for grid tie
                    Racking about 30 cents a watt
                    Charge controller 500-1800
                    Inverter 2000
                    Wires Etc 500
                    Batteries ?
                    Rich I don't think that applies to this guy. Sounds like he is near or off the coast in the Caribbean Sea. Prices will be much higher and selection and quality limited. In the mainland USA say AZ Sun for each Kwh of usable power in a day cost roughly $1800 to $2200. I would bet twice or thrice that much where the OP is at. Realistically $8K would get him a 2 to 3 Kwh system if he is lucky. Not quite 1/10th of what he wants. To get 35 Kwh/day going to cost $100,000 and half that in batteries every 5 to 7 year replacement cycle. Not going to happen.
                    MSEE, PE

                    Comment

                    • paulcheung
                      Solar Fanatic
                      • Jul 2013
                      • 965

                      #11
                      If is in Jamaica. He can get 5 to 7 KWH system with a little change for $8000 US dollars.

                      8 250 watts panels 2000 watts total JA$192,000
                      1 Midnite Charge Controller Classic 150 $78,000
                      1 Magnum MS4448PAE inverter/charger $250,000
                      8 US golf cart batteries @11,500 each $92,000
                      Labour and wires $150,000
                      Roof materials $75,000
                      1 midnite breaker box with 250amp breaker $25,000
                      battery wires $39,000

                      Total $901,000
                      @116.50 Exchange rate US$7,734.00

                      Comment

                      • Naptown
                        Solar Fanatic
                        • Feb 2011
                        • 6880

                        #12
                        Originally posted by Sunking
                        Rich I don't think that applies to this guy. Sounds like he is near or off the coast in the Caribbean Sea. Prices will be much higher and selection and quality limited. In the mainland USA say AZ Sun for each Kwh of usable power in a day cost roughly $1800 to $2200. I would bet twice or thrice that much where the OP is at. Realistically $8K would get him a 2 to 3 Kwh system if he is lucky. Not quite 1/10th of what he wants. To get 35 Kwh/day going to cost $100,000 and half that in batteries every 5 to 7 year replacement cycle. Not going to happen.
                        He is down to 4 kWh a day
                        Pricing in Brazil who knows.
                        NABCEP certified Technical Sales Professional

                        [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                        [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                        [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                        Comment

                        • SunEagle
                          Super Moderator
                          • Oct 2012
                          • 15210

                          #13
                          Originally posted by paulcheung
                          If is in Jamaica. He can get 5 to 7 KWH system with a little change for $8000 US dollars.

                          8 250 watts panels 2000 watts total JA$192,000
                          1 Midnite Charge Controller Classic 150 $78,000
                          1 Magnum MS4448PAE inverter/charger $250,000
                          8 US golf cart batteries @11,500 each $92,000
                          Labour and wires $150,000
                          Roof materials $75,000
                          1 midnite breaker box with 250amp breaker $25,000
                          battery wires $39,000

                          Total $901,000
                          @116.50 Exchange rate US$7,734.00
                          Even 6kWh per day is a far cry from what the OP wanted.
                          Last edited by SunEagle; 08-25-2015, 08:58 PM.

                          Comment

                          • paulcheung
                            Solar Fanatic
                            • Jul 2013
                            • 965

                            #14
                            Originally posted by SunEagle
                            Even 6kWh per day is a far cry from what the OP wanted.
                            He did say he will only need for fans and lights. if is two fans at 50 watts each and some LED lights, say 150 watts total for 16 hours on battery that is 2.4KWH which is about 25% DOD.

                            Comment

                            • SunEagle
                              Super Moderator
                              • Oct 2012
                              • 15210

                              #15
                              Originally posted by paulcheung
                              He did say he will only need for fans and lights. if is two fans at 50 watts each and some LED lights, say 150 watts total for 16 hours on battery that is 2.4KWH which is about 25% DOD.
                              He also said refer or fridge. He might be able to get away with the lower usage but IMO going from 35kWh to 7kWh is a major change in lifestyle.

                              Comment

                              Working...