Hello, I have a question about what sizing/gauge of wire to use going from the battery bank to the inverter. Most would probably say as big as you can go, but I have a specific requirement to meet. I would like to be able to run my toaster oven off my inverter. Here's some data of my planned system:
PV size: 240W
MPPT Charger: 20A
Battery Bank: 12V 225AH (2x 6V)
Inverter: 5000W Pure Sine Inverter (10kW peak)
Toaster Oven: 1200W 120VAC going to be on maybe 40 min a day max.
With the conversion of DC battery power to AC inverter power, won't my amps jump from 10A to 110.4A?
If so, would I not need 1/0 gauge wire from the the battery to the inverter?
The battery bank, inverter and MPPT charger will also be very close together (less than a foot of wire between each).
Thanks for the help!
Cheers
PV size: 240W
MPPT Charger: 20A
Battery Bank: 12V 225AH (2x 6V)
Inverter: 5000W Pure Sine Inverter (10kW peak)
Toaster Oven: 1200W 120VAC going to be on maybe 40 min a day max.
With the conversion of DC battery power to AC inverter power, won't my amps jump from 10A to 110.4A?
If so, would I not need 1/0 gauge wire from the the battery to the inverter?
The battery bank, inverter and MPPT charger will also be very close together (less than a foot of wire between each).
Thanks for the help!
Cheers
so this is all just in theory to me. At first blush it looked like it might be possible to run a toaster oven, but after it's been spelled out it doesn't seem at all possible with the restrictions I have haha!

Comment