Well let's see 27,000 watts / 48 volts = 563 amps from the panels. Go fing that charge controller and determine the wire size. -
So what would I need for this system?. What is wrong with the traditional approach? There are three phase inverters with 48V input and 3phase output rated at 10KW. I appreciate your input and just want to learn more.Leave a comment:
-
It would be almost impossible to run this with as 48 volt battery, and you would need to own a copper mine to cable it out. You are talking industrial application and using industrial equipment and practices. You need to be looking at 400 to 500 volts DC battery.Leave a comment:
-
what voltage battery?Hi. Based on 5 hours peak sun I get a similar value for the array size, a bit higher for mine I get 30Kwp.
For the batteries I get a requirement of 15100Ah with a 48V battery system.
Based on Ah = (Daily energy req x Number of days storage) / ( System voltage x DOD x Inverter efficiency x cables efficiency).
So based on using 200Ah batterys I would need 75 batteries.Leave a comment:
-
Hi. Based on 5 hours peak sun I get a similar value for the array size, a bit higher for mine I get 30Kwp.
For the batteries I get a requirement of 15100Ah with a 48V battery system.
Based on Ah = (Daily energy req x Number of days storage) / ( System voltage x DOD x Inverter efficiency x cables efficiency).
So based on using 200Ah batterys I would need 75 batteries.Leave a comment:
-
95 Kwh/m2 is impossible. There is no such thing as a 95 Sun Hour day. Sure you do not mean 5 Kwh/m2?
Assuming your shortest Sun Hour day is 5 hours and daily consumption is 90 Kwh/day you will need a 27 Kw panel array operating into a 490 volt battery of 1000 AH. You are looking at in USD $ $500,000 to $1,000,000. Of that will be $100,000 in batteries that need replaced about every 5 years. In the first 5 years you electric cost will be roughly $4.54/Kwh. In the USA electricity cost on average $0.111/KwhLeave a comment:
-
Stand Alone System powering 3 phase load
Hi.
I am designing a stand alone system to power a 3 phase load. I need some assistance to make sure I am doing the sizing correctly. My daily energy consumption is 90kwh/day. The irradiance in the worst month is 95 Kwh/m2. My load is 10KW. Can anyone give me some pointers. My peak sun hours are 5hours.
Any assistance would be very much appreciated.