Hi everyone, My name is Michael and I live in NSW Australia, at a place called Cootamundra. We get good sun hours, but I don't know actual statistical data (not that anything is consistent about the weather these days!).
I have been using a 100% off grid setup for almost 2 years, comprising 4x 120W 12v panels, 6x 2v 525Ah flooded batteries (ex-pallet truck) (used and tired but still giving 40%) which is lasting about 2-3 days. Charger is a Sidewinder 40A PWM. The batteries only ever charge at up to 270W according to the LCD display, and the batteries are showing signs of suffering - each month the available capacity seems to be lower than the month before, although not a rule. I feel the need for equalisation, but this setup just does not provide the power to get the batteries gassing well.
I am about to add an additional load of about 400W x 6hrs per day (office) which is computer, LED screens and lights. I guesstimate power usage to be in the order of 4000w per day.
I am going to assume winter sun hours to be around 4.5. Summer won't really be relevant as I will need to run aircon which will have to be mains powered. I don't have mains yet, but will get it before the warm weather in 6 months time or so. It's a tough call, going off-grid solar when the grid is (will be) there, the cost of solar is soooo expensive compared to mains power, but it is fun!
I have my eye on some new batteries that are rated at 1000Ah as they are a good price, but 1000Ah is a bit overkill for my needs - but the price is right - about $3000. I am not really liking the idea of an 80 amp charger though ($800) but unless I go 24v, I don't see any other choice. 2x 40A charger cost about the same as 1x 80A charger.
Also considering MPPT as my existing 40A charger is PWM.
So I have several options, not the least of which is to spend my $$$ on beers & smokes instead of batteries and just go Grid
. But let's just humour me and consider other options as well...
1. keep existing panels and batteries and upgrade controller and maybe add some panels.
2. add panels, replace batteries with new ones and a new charge controller.
3. what else?
Getting new batteries means superseding the old ones and to do what? seems a waste to chuck them out when they can still offer 3 or 4 kW for a while yet. Same with the controller. I am suspecting that doubling the panels will not do much if the batteries won't take the charge.
So, any ideas then on where to go from here? I don't mind throwing the bucks at the system, as it is a hobby and an adventure and I do love bad investments
Cheers
Mike
I have been using a 100% off grid setup for almost 2 years, comprising 4x 120W 12v panels, 6x 2v 525Ah flooded batteries (ex-pallet truck) (used and tired but still giving 40%) which is lasting about 2-3 days. Charger is a Sidewinder 40A PWM. The batteries only ever charge at up to 270W according to the LCD display, and the batteries are showing signs of suffering - each month the available capacity seems to be lower than the month before, although not a rule. I feel the need for equalisation, but this setup just does not provide the power to get the batteries gassing well.
I am about to add an additional load of about 400W x 6hrs per day (office) which is computer, LED screens and lights. I guesstimate power usage to be in the order of 4000w per day.
I am going to assume winter sun hours to be around 4.5. Summer won't really be relevant as I will need to run aircon which will have to be mains powered. I don't have mains yet, but will get it before the warm weather in 6 months time or so. It's a tough call, going off-grid solar when the grid is (will be) there, the cost of solar is soooo expensive compared to mains power, but it is fun!
I have my eye on some new batteries that are rated at 1000Ah as they are a good price, but 1000Ah is a bit overkill for my needs - but the price is right - about $3000. I am not really liking the idea of an 80 amp charger though ($800) but unless I go 24v, I don't see any other choice. 2x 40A charger cost about the same as 1x 80A charger.
Also considering MPPT as my existing 40A charger is PWM.
So I have several options, not the least of which is to spend my $$$ on beers & smokes instead of batteries and just go Grid

1. keep existing panels and batteries and upgrade controller and maybe add some panels.
2. add panels, replace batteries with new ones and a new charge controller.
3. what else?
Getting new batteries means superseding the old ones and to do what? seems a waste to chuck them out when they can still offer 3 or 4 kW for a while yet. Same with the controller. I am suspecting that doubling the panels will not do much if the batteries won't take the charge.
So, any ideas then on where to go from here? I don't mind throwing the bucks at the system, as it is a hobby and an adventure and I do love bad investments

Cheers
Mike