problem with charging or overload ??? tristar 45 controller ?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • prince_77
    Junior Member
    • Oct 2011
    • 4

    #1

    problem with charging or overload ??? tristar 45 controller ?

    Hello all
    i have a small scale offgrid system, its build with
    2X190W (40V 8A) system
    Morningstar tristar 45 +RTS sensor
    2X12X2 (24V) trojan tmx24 batteries.

    the system is up and running for the last 2 days. now i check the system and the controller in the morning, the tristar is blinking green and when i open the battery bay i can hear a noise of water inside the battery, when touching the batteries i dont feel that there hot but there a smell of a little bit of acid.

    testing with multimeter , the controller is pusing 28V into the batteries even when its in blinking mode.

    i be greatful for any advice!
    thanks
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Is the the Tristar MPPT, or the PWM ? What voltage is it configured for ?

    I don't know what the " 2X12X2 (24V) trojan tmx24 batteries " means or what the battery capacitys are, please spell it out:

    Battery = __ V _____ah
    batteries in parallel ___
    batteries in series __

    I'm assuming these are flooded batteries, have you checked to see if distilled water needs to be added to bring them to the proper level?

    PV : 2X190W (40V 8A) 8A does not seem like much, but maybe it's all miswired and you should shut this all down till we figure out what is happening, when you smell acid fumes, things are not right.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • prince_77
      Junior Member
      • Oct 2011
      • 4

      #3
      thank u mike for the answer

      Is the the Tristar MPPT, or the PWM ? What voltage is it configured for ? PWM

      configure to work on 24V, but im not sure i got right the dip on the controller

      here is the link for the battery
      12V - 85H



      batteries in parallel - 2
      batteries in series - 2

      total making 24V system with 2X2 series

      i checked with multimeter and the system shows right flow plus to plus minus to minus

      thanks again for your help

      Comment

      • 894tom
        Member
        • Sep 2009
        • 58

        #4
        You got me worried now Mike. My system behaves just as he describes. Mine has been up and running for a year. We do have different C/C's. Anytime a FLA battery is charging it bubbles and gasses. This is normal FLA battery charging behavior.

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #5
          Sounds normal to me. At 28 volts indicated the CC is in charge mode. When a FLA battery charges it will fizz like a good glass of champagne and is normal.

          As I have said thousands of times on here voltage does not tell you much about the state of charge on a battery. Now if you read 23 volts on a 24 volt system you got problems, but the only way to tell what is really going on is with a lab quality temperature corrected hydrometer.

          A volt meter can only tell you what is going on with the battery disconnected from everything and rested for 4 to 6 hours. That is not practical with a working solar system.
          MSEE, PE