Problem:
Off Grid Systeem:
Morningstar SureSine inverter 48 VDC 2500 Watt
Morningstar Tristar TS 45 Charge Controller
Battery bank 4S2P 8 x 12V 200Ah VRLA Gel batteries
4 x Longhi 550-Watt Solar Modules
System load:
dataurl691576.png
The system is located at Pulau Rote in Indonesia.
After it was installed in March of this year the client did ad a huge fridge/freezer to the system.
Specs of the fridge freezer:
When they disconnect the fridge freezer verything is smooth
I tell the client that this extra fridge was not in de design demands and they do understand that but they also ask how it is possible that it did run fine for 5 months. I think it has to do with SoC of the battery bank and the surge power of the fridge freezer. What do you guys think about the situation. And how could it be repaired?
Many thanks for participating
Kind regards
Off Grid Systeem:
Morningstar SureSine inverter 48 VDC 2500 Watt
Morningstar Tristar TS 45 Charge Controller
Battery bank 4S2P 8 x 12V 200Ah VRLA Gel batteries
4 x Longhi 550-Watt Solar Modules
System load:
dataurl691576.png
The system is located at Pulau Rote in Indonesia.
After it was installed in March of this year the client did ad a huge fridge/freezer to the system.
Specs of the fridge freezer:
- Fridge/freezer: Samsung RS61R5001M9
- Rated power: 270 W (220 V / 50 Hz)
- Normal running power: approx. 120–150 W
- Compressor startup surge: approx. 1000 / 1500 W (very brief)
When they disconnect the fridge freezer verything is smooth
I tell the client that this extra fridge was not in de design demands and they do understand that but they also ask how it is possible that it did run fine for 5 months. I think it has to do with SoC of the battery bank and the surge power of the fridge freezer. What do you guys think about the situation. And how could it be repaired?
Many thanks for participating
Kind regards