Hi all,
I know that for grid tied inverters oversizing is a common thing to do. I was wondering what the thoughts on oversizing charge controllers are.
I have Two Outback FM80 Charge Controllers with an Outback inverter 3048. The battery bankruns on 48Volts.
The mac Amps for the FM 80 is 80Amps and MAC VOC is 150 VCD
I have panels of 550 Watt with the following specs:
MaxP 550 Watt
Voc 49.8 V
Isc 13.98 A
Vmp 41.95
IMP 13.12
Maximum recommended PV Array for the FM80 is 4000 Watt
My question is as follows:
Can I connect 3 x 3 panels in series connect in parallel with the FM80
Voc of each string will be 3 x 49.8 = 149.4 V (< dan 150 V)
Isc of each String will be 13.98
For 3 Strings the total Isc will be 41,94 A
The total Array will be 149.4 V (< 150 VDC) and 41,94 A (< 80 A)
So I stay within the limmits of the charge controller. But the Array is oversized. 3 x 550 Watt x3 = 4950 Watt
What do you guys think about this oversizing?
Many thanks for participating
Kind regards
Ben
I know that for grid tied inverters oversizing is a common thing to do. I was wondering what the thoughts on oversizing charge controllers are.
I have Two Outback FM80 Charge Controllers with an Outback inverter 3048. The battery bankruns on 48Volts.
The mac Amps for the FM 80 is 80Amps and MAC VOC is 150 VCD
I have panels of 550 Watt with the following specs:
MaxP 550 Watt
Voc 49.8 V
Isc 13.98 A
Vmp 41.95
IMP 13.12
Maximum recommended PV Array for the FM80 is 4000 Watt
My question is as follows:
Can I connect 3 x 3 panels in series connect in parallel with the FM80
Voc of each string will be 3 x 49.8 = 149.4 V (< dan 150 V)
Isc of each String will be 13.98
For 3 Strings the total Isc will be 41,94 A
The total Array will be 149.4 V (< 150 VDC) and 41,94 A (< 80 A)
So I stay within the limmits of the charge controller. But the Array is oversized. 3 x 550 Watt x3 = 4950 Watt
What do you guys think about this oversizing?
Many thanks for participating
Kind regards
Ben