    Exceeding recommended PV array wattage

    Hi all,

    I've a question about a Outback FlexMax 60 Amps. 150 VDC

    I've a 12 VDC Battery bank and 4 x 300Watt panel.

    The recommended PV array wattage for the FlexMax 60 in combination with a 12 VDC battery bank is 750 watt. What would happen if I connect the 4 x 300 Watt panel to the FlexMax 60? I will connect it in 2 strings of each 2 panels. I will stay within the maximum of the 150 VDC.

    So I'm exceeding the recommended PV array wattage with 550 watt.

    what will happen, how will the system behave?

    Many thx

    Regards








  • SunEagle
    Super Moderator
    • Oct 2012
    • 15123

    #2
    Originally posted by Bendesa1962
    Hi all,

    I've a question about a Outback FlexMax 60 Amps. 150 VDC

    I've a 12 VDC Battery bank and 4 x 300Watt panel.

    The recommended PV array wattage for the FlexMax 60 in combination with a 12 VDC battery bank is 750 watt. What would happen if I connect the 4 x 300 Watt panel to the FlexMax 60? I will connect it in 2 strings of each 2 panels. I will stay within the maximum of the 150 VDC.

    So I'm exceeding the recommended PV array wattage with 550 watt.

    what will happen, how will the system behave?

    Many thx

    Regards







    There are two possible options.

    One is that the inverter handles the extra wattage but "clips" it so you only get a maximum of 60amps output instead of 100amps (1200w / 12v = 100amp)

    The second option is that the inverter fails due to exceeding the input wattage.

    My suggestion is if you want to use all 4 300w panels then make sure 2 are facing in a different compass direction (East or West) then the other 2. That way you really only get about 600watt input to the inverter instead of the full 1200 watts but you get a longer time period for charging the batteries.

    Comment

    • Bendesa1962
      Solar Fanatic
      • Nov 2016
      • 103

      #3
      Hi SunEagle

      thanks for your reply. I guess by inverter you mean chargecontroller right?

      regards

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15123

        #4
        Originally posted by Bendesa1962
        Hi SunEagle

        thanks for your reply. I guess by inverter you mean chargecontroller right?

        regards
        Yep. My bad on confusing the issue. The CC is the heart of a solar/battery system. You do not want to abuse it.

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          I concur with half the array aimed easterly, and half westerly. That spreads your peak harvest to be less peak, but a longer duration.

          do plan to include a generator for backup charging, and to assist with monthly EQ charging.

          Even with optimum sun & angle, the panels will seldom produce more that 960 watts / 14V = 68A, so the controller will clip a bit, but as long as it's well vented, it should survive.
          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • PNW_Steve
            Solar Fanatic
            • Aug 2014
            • 433

            #6
            A little different application but similar situation. I am putting significant solar on the roof of my RV. They will be flat mounted and will see use anywhere from Seattle in January to Yuma in July. My ability to collect will vary significantly depending on where I park so I have overpaneled significantly.

            Someone pointed out a feature that the newer Midnite Classic charge controller when used in conjunction with the Whizbang Jr. You can set the maximum charge current supplied to the battery bank. That way I can have lights in Seattle without fear of boiling my batteries when I head to Yuma.

            Prior to finding that nifty feature I was considering using the breakers in my combiner to selectively turn strings on and off depending on conditions. I think that would have been adequate as long as I never forget to turn one or more strings off before heading South. One senior moment could be disastrous for the batteries.

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #7
              The output limit setting on a Midnight classic, does not need the whizbang to function
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • PNW_Steve
                Solar Fanatic
                • Aug 2014
                • 433

                #8
                Originally posted by Mike90250
                The output limit setting on a Midnight classic, does not need the whizbang to function
                My understanding from talking with Midnite was that if you include the Whizbang jr that you can limit the current to the battery while still have access to the excess to support loads.

                Without the Whizbang, you can set a hard current limit and anything the panels produce in excess of the set limit is wasted. Or, so says Midnite tech support. I do not have it in production yet.

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #9
                  Midnight support is right if you want other loads at the same time. Generally, I find that the batteries will only consume what they need, as they charge up, their amp draw reduces.
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||