Hello everybody,
I've just received my new Rolls 6 CS 25P deep-cycle 6V battery (820Ah) to replace my Rolls S550 (428Ah) ones - 8 of them for a 48v sytstem.
I'll basically just write them in series like the old ones. I've a Schneider XW6848 inverter, 2 MPPT 600V-80A controllers and the PDP (and other stuff, like the battery monitor, SCP, gen start, etc.). I basically plan to: disconnect the power panel from the inverter
disconnect the PV array from each MPPT controller (I have at DC disconnect for that for each of them)
disconnect the MPPT from the battery bank (I have breakers in the PDP of that)
disconnect the battery bank - postive first, negative after from the battery terminals
Then, swap the batteries and connect them in series like right now. Then do 4 to 1. I do no think I can disconnect the *inverter* from the battery bank through the PDP using a breaker.
Does that sound about right? Any extra precautions to take?
Thanks!
I've just received my new Rolls 6 CS 25P deep-cycle 6V battery (820Ah) to replace my Rolls S550 (428Ah) ones - 8 of them for a 48v sytstem.
I'll basically just write them in series like the old ones. I've a Schneider XW6848 inverter, 2 MPPT 600V-80A controllers and the PDP (and other stuff, like the battery monitor, SCP, gen start, etc.). I basically plan to: disconnect the power panel from the inverter
disconnect the PV array from each MPPT controller (I have at DC disconnect for that for each of them)
disconnect the MPPT from the battery bank (I have breakers in the PDP of that)
disconnect the battery bank - postive first, negative after from the battery terminals
Then, swap the batteries and connect them in series like right now. Then do 4 to 1. I do no think I can disconnect the *inverter* from the battery bank through the PDP using a breaker.
Does that sound about right? Any extra precautions to take?
Thanks!