I've just upgraded my inverter to an Aims 6000w Pure Sine split phase unit. Looking at the specs I noticed the idle consumption is listed at 76.8 watts. I'm looking for some input on the proper way to include the idle consumption in a daily load analysis. I have the 24v unit, running off a 430ah bank. This is in a weekend camp with calculated daily watt usage at 3100 watts, not including inverter idle consumption. Thanks.
Announcement
Collapse
No announcement yet.
Inverter idle consumption in off grid load calculations
Collapse
X
-
-
76.8w x 24hr = 1843.2wh That's enough power to run a pre-energy star Fridge.
It's also 2/3 of your current load, which is now up to 4943.2wh.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister -
So just tack the idle number to the total? I wasn't sure if that idle number was as constant load, or if it changed/diminished when more load was demanded from the inverter. This unit has a power saver mode (29 watt idle draw), but it needs 50 watts of load to wake it up. In the evenings with only a couple LED lights on I assume the inverter would go into sleep mode, and I'd be in the dark.
Originally posted by Mike90250 View Post76.8w x 24hr = 1843.2wh That's enough power to run a pre-energy star Fridge.
It's also 2/3 of your current load, which is now up to 4943.2wh.Comment
-
That idle is always there, added to what ever you are consuming, PLUS when you consume 100w and you have 90% eff inverter, there is another 10W left warming the inverter, actually using 110w.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||