I really could use some constructive criticism with my newly installed system. I should have asked these questions before initial set-up I realize, but better late than never I guess. Unfortunately, I am one of those people who suffer from analysis paralysis - so for a lot of projects I need to dive right in and fix it up later - I know that is not ideal, but I have found this is only way I get started sometimes...
48 Volt system. Charge controller is Midnite Solar Kid with battery temp sensor . Inverter is Exeltech XP600. Solar Panels are Solar World SW255 (nameplate Voc 38.7 and 9.05A) - 3 of them in series.
Batteries are 6-year old Interstate DCM0075U (12v 75AH AGM) in 2 strings - so total of 150AH @ 48V. Batteries are from some backup system - before installation their resting voltage was 12.7-12.8, so I think they still have some life in them. I could use some guidance on what absorb and float setting to put into Kid. The spec sheet for the batteries says "Float 13.5-13.8. Cycle 14.4-15.0". Currently I have them set for Absorb 57.6V (120 minutes) and Float 54.0V. I don't believe these batteries should be equalized, so I set that at 57.6V as well.
My loads on this system are minimal - running/charging a couple of laptops, charging phones, charging some cordless tools, running a few fans, and chest freezer to fridge conversion. I am expecting daily loads to run about 600-750 watt-hours - I don't have permanent wiring yet - running off extension cord and plan to hook Kill-a-watt up for a few days to measure total loads.
Wiring is as follows:
Currently, panels are not grounded - they are on temp mount practically on the ground. Inverter, Kid, and Neg batteries are currently grounded. I have current ground set up with 8 AWG copper to 8' ground rod in moist area right outside shed.
Questions:
48 Volt system. Charge controller is Midnite Solar Kid with battery temp sensor . Inverter is Exeltech XP600. Solar Panels are Solar World SW255 (nameplate Voc 38.7 and 9.05A) - 3 of them in series.
Batteries are 6-year old Interstate DCM0075U (12v 75AH AGM) in 2 strings - so total of 150AH @ 48V. Batteries are from some backup system - before installation their resting voltage was 12.7-12.8, so I think they still have some life in them. I could use some guidance on what absorb and float setting to put into Kid. The spec sheet for the batteries says "Float 13.5-13.8. Cycle 14.4-15.0". Currently I have them set for Absorb 57.6V (120 minutes) and Float 54.0V. I don't believe these batteries should be equalized, so I set that at 57.6V as well.
My loads on this system are minimal - running/charging a couple of laptops, charging phones, charging some cordless tools, running a few fans, and chest freezer to fridge conversion. I am expecting daily loads to run about 600-750 watt-hours - I don't have permanent wiring yet - running off extension cord and plan to hook Kill-a-watt up for a few days to measure total loads.
Wiring is as follows:
- Panels to Kid CC - 50' of 10awg PV wire going through 15A MNEPV Breaker on + wire (breaker in BigBabyBox)
- CC to pos and neg bus bar in Big Baby Box - 10awg wire with positive going through 30A MNEPV Breaker.
- Batteries connected in series with 4AWG wire and each string connected to pos/neg bus bars with 6' of 8awg wire. 30A MRBF fuses between positive string and 8awg wire.
- Inverter connected to pos/neg bus bars with pos wire going through 30A MNEPV breaker - 8 AWG wire for this.
Currently, panels are not grounded - they are on temp mount practically on the ground. Inverter, Kid, and Neg batteries are currently grounded. I have current ground set up with 8 AWG copper to 8' ground rod in moist area right outside shed.
Questions:
- Big Red Flags?
- How are my CC settings so I get max life out of batteries?
- Sizing of panels to batteries to loads balanced?
- Are my wiring sizes correct?