My problem is that I need the pack to be capable of doing nothing for long periods of time without requiring exercise or maintenance. I also want a high cycle count and lithium provides both.. Additionally, the way I'm going about it, its also only about 15% to 20% of the cost of the FLA batteries that would be needed to match the same performance.
In fact, about the only drawback to the Lithium batteries that I can see is that they are known to catch on fire.. and that can be solved easily enough by using an insulated steel container outdoors. Heck, the FLA batteries and all the fumes require nearly the same thing.
Actually, the REC BMS can be programmed to pretty much do whatever I want it to so far as voltages are concerned. Its a lot like the FlexMax controller in that it has settings for almost every parameter and a PC interface to see how each cell is doing.
The way I envision this working is that the PV array will charge the batteries through the Flexmax.. if the BMS detects a problem, it can open the circuit between the charge controller and the PV array while it works to bleed off the rogue cell imbalance.. Of course, this is only in a worst case scenario, as you say, once balanced, they should stay balanced.
Heck, with a little McGuyvering, I should even be able to set up a double throw relay system so the PV power is sent to do something else and doesn't get wasted.. maybe heat some water or something or even charge a back up lithium pack.
When everything is operating as it should, then yes.. but we don't design things like this for times when they operate as they should.. If that was the case, we'd never need fuses or breakers.. We design for worst case scenario, and in this instance, that would involve a rogue lithium cell that has, for some reason, lost its capacity and is charging to its max voltage faster than the other cells. In such a case, we need to be able to either slow down the charger or cut it off all together.
I would think that a BMS would absolutely be capable of balancing the cells if the charge rate was low enough for it to keep up.. so to that end, I could either set the max amps in the FlexMax to a very low rate, or simply use fewer PV panels until all cells are balanced.
I don't think its an issue however as the cells I'm getting are used and already well balanced. They should still have greater than 90% of their life left in them.
I was under the impression that every electric car on the road used a BMS on their batteries.
Hey man, I have no biz working on a lot of things.... story of my life. Its always seems to be the first one that requires the most work...
In fact, about the only drawback to the Lithium batteries that I can see is that they are known to catch on fire.. and that can be solved easily enough by using an insulated steel container outdoors. Heck, the FLA batteries and all the fumes require nearly the same thing.
Like I said you have a lot to learn. Unless you have a bad cell, all cells charge equally and discharge equally. If they are Balanced from the start, they stay in Balance. You just said the BMS uses Vampire Boards, aka Bleeders. What you do not understand is how a Vampirte Board works. It only turns on when the first cell reaches 4.2 volts, and when it turns on only bypasses 0.9 amps. Problem is you may still be charging at say 50 amps. So when the first Vampire board turns on and bleeds 1 amp bypass leaves 49 amps flowing through your fully charged battery. Oops! Your BMS just destroyed the cell.
The way I envision this working is that the PV array will charge the batteries through the Flexmax.. if the BMS detects a problem, it can open the circuit between the charge controller and the PV array while it works to bleed off the rogue cell imbalance.. Of course, this is only in a worst case scenario, as you say, once balanced, they should stay balanced.
Heck, with a little McGuyvering, I should even be able to set up a double throw relay system so the PV power is sent to do something else and doesn't get wasted.. maybe heat some water or something or even charge a back up lithium pack.
Now stop and think. if you Balanced the cells properly initially. and you only charge to 56 volts (4.0 vpc) Your BMS never does anything because no cell ever reaches 4.2 volts now does it?
The real question is how do you intend to do the Initial Bulk Balance? You cannot do that with a BMS as it is not capable of balancing a battery. Do you have the equipment and knowledge to do the initial balance?
I don't think its an issue however as the cells I'm getting are used and already well balanced. They should still have greater than 90% of their life left in them.
Think of this no commercial EV manufacture allows a customer to ever fully charge the battery. I build racing golf carts and help a lot of people build DIY EV conversions. Very few would ever consider using a BMS because the BMS is the number 1 cause of failures. But there is a catch. We know what we are doing.
So until you figure out how to do the initial Balance and have the equipment to do it, you have no biz working with Lithium Batteries.
So until you figure out how to do the initial Balance and have the equipment to do it, you have no biz working with Lithium Batteries.
Hey man, I have no biz working on a lot of things.... story of my life. Its always seems to be the first one that requires the most work...