Hello. I am not sure if this is the perfect place to post this question, so if there is somewhere better please let me know.
We have an outback FlexMax 80 cc that is rated up to 145 volts (150 max).
I am trying to wire 8 solar world 245 watt panels 4 ea. in series/parallel (1960 total watts) to charge a 24v bat bank. The FlexMax 80 is rated up to 2000 watts for a 24v bat bank.
The problem that I am running into is the Voc for each panel is 37.7 which puts it at 150.8 just over the "damage" warning for the cc.
The panels are 8.16 Imp, 30 Vmp, 37.7Voc. I don't want to burn up our cc so my question is:
Is there any inline diode (like a zener diode) that I could put on it to limit it to 144 or 145 volts?
or is there any other safe way to hook up these panels to this cc?
I am not overly familiar with Voc. From what I understand it is when the panels are not under load. Is there any way I can keep the panels under a small load before the cc so they never produce the full 37.7 Voc? On cold mornings before the sun even hits them directly they shoot right up to 147 volts. After they warm up the come back down, but about half our year here it is cold enough where they produce these higher voltages in the morning and the colder it is the longer it takes for them to warm up which means less power, plus I would never chance it and leave them connected to the FlexMax just in case they could burn it up...
any my help is appreciated. Thank you.
There is no Zener Fix. A Midnight Solar "clipper" could work, but that is pretty expensive. Also Midnight Classic 200 or 250 would work.
Magnum PT-100 has 185V max solar input
http://www.magnum-dimensions.com/pt-...rge-controller
And - you did post in some unrelated topic, and us Mods can't move posts to their own threads. So this is locked, and I will start a new thread for you. and come back and delete this. Mike
We have an outback FlexMax 80 cc that is rated up to 145 volts (150 max).
I am trying to wire 8 solar world 245 watt panels 4 ea. in series/parallel (1960 total watts) to charge a 24v bat bank. The FlexMax 80 is rated up to 2000 watts for a 24v bat bank.
The problem that I am running into is the Voc for each panel is 37.7 which puts it at 150.8 just over the "damage" warning for the cc.
The panels are 8.16 Imp, 30 Vmp, 37.7Voc. I don't want to burn up our cc so my question is:
Is there any inline diode (like a zener diode) that I could put on it to limit it to 144 or 145 volts?
or is there any other safe way to hook up these panels to this cc?
I am not overly familiar with Voc. From what I understand it is when the panels are not under load. Is there any way I can keep the panels under a small load before the cc so they never produce the full 37.7 Voc? On cold mornings before the sun even hits them directly they shoot right up to 147 volts. After they warm up the come back down, but about half our year here it is cold enough where they produce these higher voltages in the morning and the colder it is the longer it takes for them to warm up which means less power, plus I would never chance it and leave them connected to the FlexMax just in case they could burn it up...
any my help is appreciated. Thank you.
There is no Zener Fix. A Midnight Solar "clipper" could work, but that is pretty expensive. Also Midnight Classic 200 or 250 would work.
Magnum PT-100 has 185V max solar input
http://www.magnum-dimensions.com/pt-...rge-controller
And - you did post in some unrelated topic, and us Mods can't move posts to their own threads. So this is locked, and I will start a new thread for you. and come back and delete this. Mike