Checking my solar idea
    • 15204
    #31
    Originally posted by teknatronik
    Hello, im back
    So I seem to lose about 100 watts from each 255 watt panel
    i have 10 set direct bury wire in a 60ft run. Im 24 volt and have 4 255 watt panels . I caollect about 600 watts on a good day.
    I checked each panel and they watt out roughly the same. 155 watts each is what they show at c.c .
    I run them in series as it seems to work the best. I also do not have a combined box.
    What can i do to get my extra juice?
    It sounds like the panels are not getting the full amount of needed sunlight to produce more wattage.
    It really depends on where you are located and what angle the panels are facing. But even if you are at the Equator with total sunshine those panels may not provide more then 90% of their nameplate wattage. That 255 watts is really Lab results and not true field results.
    Your system may also have wire that is too small to stay below the 2% voltage drop. Your system will lose if it is not properly wired or if you have a inefficient charge controller.
    • littleharbor
      • Jan 2016
      • 1998
      #32
      What charge controller are you using? Sounds like a PWM controller from your statement about working better in parallel.
        • 15065
        #33
        Hello, im back
        How are you figuring how much irradiance is available when you're measuring ~ 155 W/panel ?
        The array's output will always be less than 255 * 4 = 1,020 W. Probably no better than 85 - 90 % or less of that number even under ideal conditions, even with the direct normal incidence angle == zero, that is, when the sun's rays are perpendicular to the plane of the array.
        If the POA irradiance is less than the rated STC irradiance (which is most all of the time) when you are reading 600 W output, the output will be less than STC output.
        You may have problems, but expecting 255 * 4 W output will not happen except maybe on very rare occasions if for no other reasons than the POA irradiance will almost never be 1,000 W/m^2.
        • teknatronik
          • Sep 2017
          • 31
          #34
          I have the energy mppt40 commander..
          I was expecting about 800 watts tbh.
          • teknatronik
            • Sep 2017
            • 31
            #35
            Sun Eagle, I am in south carolina, anderson. The sun does move a lot in the sky depending on season. I move my panels to fit that best I can.
            Littleharbor, it is mppt. I actually think the panels collect more in series vs par. I might have worded wrong earlier.
            Jpm, I am not checking irradiance as far as i know. I am hooking the panels up and looking at the info on the cc. The panels are 255, I expected 200 watts from them I figure with distance and all a 55 watt loss is not bad. 100 watts per panel seems a bit much. That is just my own opinion though.
            If wire size is an issue, should I just go to 8 awg?
            • littleharbor
              • Jan 2016
              • 1998
              #36
              You should be wired 2s2p to get the voltage higher for that long wire run. Why do you think it works better wired up in parallel? Incoming amps will look higher in an all parallel configuration but That doesn't mean you're getting the best charging efficiency. The MPPT controller does the voltage conversion and will boost incoming amps when it matches your charging voltage.
              • teknatronik
                • Sep 2017
                • 31
                #37
                I do not think its work better in par.
                From my tests, it works way better in series.
                I would wire in 2s 2p, but no combiner box yet. However, when I tie right into my charge controller with the 2p2s It doesnt seem to charge the battery as fast.
                  • 15204
                  #38
                  Wiring 2s 2p may not produce a voltage high enough for a 24v battery system if the wire run is long and the voltage drop is high. Going all 4 in series gets you the highest voltage to the CC which will convert almost 100% of the panel wattage to charging amps.
                  Something else may be a factor. Batteries that are close to full SOC will not accept more amps then needed. So the CC actually throttles back the amount of amps going to the battery which makes it look like your panels are not producing as much as you expect.
                  One way to test that is to discharge your battery system SOC to 50% and then see what the output of those panels are around Noon time under a clear sky. I expect the output wattage will be higher then that 600w you are currently getting from your 1000w system.
                  • littleharbor
                    • Jan 2016
                    • 1998
                    #39
                    His controller has a 100 VOC limit .These panels will come in with over 140 volts, open circuit.
                      • 15204
                      #40
                      Shoot. I missed that. Thanks for the info. It looks like 4s will not work for that CC.
                        • 15065
                        #41
                        You will only measure irradiance with a pyranometer.
                        The point is that you will only get about 85-90 % of the panels' STC output under the best of conditions that rarely occur. Anything less than ideal conditions will reduce output even more, and even less yet if the panels are not aimed directly at the sun.
                        • teknatronik
                          • Sep 2017
                          • 31
                          #42
                          My c.c. is 150volt. I run 130 into it.
                          • littleharbor
                            • Jan 2016
                            • 1998
                            #43
                            The one I looked up had 100 Voc. limit, various models under that name I think. Anyway 4 in series isn't advisable with 255 watt panels, knowing typical Voc. and Vmp. of this size panel..When you say you run 130 volts into it, is this working voltage, or rated Voc.?
                            • teknatronik
                              • Sep 2017
                              • 31
                              #44
                              I might have given wring name for c.c. its def 150 volt. Its working volts .The rated per panel is 37...
                              • littleharbor
                                • Jan 2016
                                • 1998
                                #45
                                The voltage limit relates to the sum of the Voc. which will be higher than the Voc. number on the panel, in very cold conditions.