The OP has said he is happy to use a generator, if this is the case he could probably save allot of money by sizing the LFP battery so that in an average night he uses around 50% of the stored charge. If as he says he will only be running a fridge, freezer, lights and other small loads during the night there is no way he will be using 13.5kWh (50% of 27kWh). I would think that most of the time with such a large solar array in the tropics he will be able to recharge the battery on the next day. On the days that there is not enough sun and the battery SOC gets to less than say 20% all he has to do is run the generator and boost the battery SOC to around 40%-50% so there is still plenty of space in the battery to be charged from the sun.
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor
Latronics 4kW Inverter, homemade MPPT controller
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor
Latronics 4kW Inverter, homemade MPPT controller