Understood. I hear mostly similar comments from my many Canadian friends, although they're still at a loss to figure out what has/will happen to the U.S.
Unfortunately is has gone down those tubes and is actually worse than US even if it's hard to imagine so. Locals say it was much better before, some 30 years ago. Nowadays teachers have union, go on strikes and in general not very concerned with outcome of their work. As one of their late 'reforms' I heard was decision to introduce 'sex' education in early grades up to the point parents went to public protests. Just because their current minister of education is lesbian. I'm not making this up: https://www.lifesitenews.com/news/le...he-world-video Sorry if this confirms your pessimism about direction humanity going in lately. I gave up reading those news while ago and just realized the same person was elected Premier of Ontario in 2013. I just don't know what needs to happen for that place to come to senses
.
Back to business.Leave a comment:
-
Unfortunately is has gone down those tubes and is actually worse than US even if it's hard to imagine so. Locals say it was much better before, some 30 years ago. Nowadays teachers have union, go on strikes and in general not very concerned with outcome of their work. As one of their late 'reforms' I heard was decision to introduce 'sex' education in early grades up to the point parents went to public protests. Just because their current minister of education is lesbian. I'm not making this up: https://www.lifesitenews.com/news/le...he-world-video Sorry if this confirms your pessimism about direction humanity going in lately. I gave up reading those news while ago and just realized the same person was elected Premier of Ontario in 2013. I just don't know what needs to happen for that place to come to senses
You can make a fairly accurate psychrometer using a bulb or even spring type, or electronic thermometer, some gauze and a fan. I've got a professional sling psychrometer given to me by one of my mentors. The made one using a 10K thermistor, and it's as accurate as the sling psychrometer after I fine tuned the thermistor with boiling H2O, an ice bath and my body temp.
Just trying to get it right and fill in a few blanks with info.
As usual, take what you want. Scrap the rest.
Seems like (Ontario) Canadian high school physics hasn't gone down the tubes yet. Hope it never does. Got lots of friends in, and respect for, the Great White North EHH ?!? Spent lots of time in TO.
.
Last edited by max2k; 09-13-2017, 01:49 AM.Leave a comment:
-
Ya even running the dehumidifier feels like the room is heating up.Leave a comment:
-
You can make a fairly accurate psychrometer using a bulb or even spring type, or electronic thermometer, some gauze and a fan. I've got a professional sling psychrometer given to me by one of my mentors. The made one using a 10K thermistor, and it's as accurate as the sling psychrometer after I fine tuned the thermistor with boiling H2O, an ice bath and my body temp.
Very interesting, thank you. I shall admit when it comes to HVAC or heating/cooling in general my 'expertise' is at high school physics course level as I never dealt with this on professional level. I was using relative humidity simply because I had such device at home recently while the last hygrometer capable of measuring dew point I saw > 30 years ago in high school
.
Just trying to get it right and fill in a few blanks with info.
As usual, take what you want. Scrap the rest.
Seems like (Ontario) Canadian high school physics hasn't gone down the tubes yet. Hope it never does. Got lots of friends in, and respect for, the Great White North EHH ?!? Spent lots of time in TO.Leave a comment:
-
Very interesting, thank you. I shall admit when it comes to HVAC or heating/cooling in general my 'expertise' is at high school physics course level as I never dealt with this on professional level. I was using relative humidity simply because I had such device at home recently while the last hygrometer capable of measuring dew point I saw > 30 years ago in high school
Actually Max, it's more about about dew point temperatures, how oversized HVAC systems do not lower the dew point temps. as much or as effectively as less oversized systems will, and the difference between dewpoint and skin temp. At a given (probably elevated) body temp., the hypothalamus gland will tell the sweat glands to produce liquid to, in effect, turn the body's surface into an evaporative cooler to reduce or regulate the body's temp. For the most part, and to a 1st approx., but not exactly, for the same activity level, the body will produce as much sweat in an environment that has a 20 deg. C. dewpoint as it will in an environment that has a -5 c. dewpoint. The difference is that in a lower dewpoint environment most, or all of the sweat will evaporate, while in the higher dewpoint environment, it will not. That non-evaporation will not cool the body as effectively and cause sweating to continue as the hypothalamus attempts to maintain homeostasis. This is usually a not too comfortable situation for most folks.
On the HVAC side, oversized systems, in a counterintuitive way, do not wring as much moisture out of the air as smaller capacity systems, mostly but not entirely because their compressors do not run as long, and so don't have as much moist air going through them. That means the dew point of the air in the conditioned space says high(er) - the air tends to stay more humid - making the temp. difference between the dew point and the skin less, with the dew point temp. and what's called the dry bulb temp, closer together. Since the difference between the dew point and the skin temp. is what drives the rate of sweat evaporation, less sweat will be evaporated, with the ensuing discomfort as described above as a result.
The ways Psychometrics and physiology interact are quite interesting but one of the less precise fields of engineering endeavor,
FWIW, the actual condensate load (how much moisture is "knocked out" of the air in the cooling process) can be anywhere from zero to maybe ~ 20% - 30% of the load the air conditioner sees.
Take what you want of the above. Scrap the rest.
.
Leave a comment:
-
Actually Max, it's more about about dew point temperatures, how oversized HVAC systems do not lower the dew point temps. as much or as effectively as less oversized systems will, and the difference between dewpoint and skin temp. At a given (probably elevated) body temp., the hypothalamus gland will tell the sweat glands to produce liquid to, in effect, turn the body's surface into an evaporative cooler to reduce or regulate the body's temp. For the most part, and to a 1st approx., but not exactly, for the same activity level, the body will produce as much sweat in an environment that has a 20 deg. C. dewpoint as it will in an environment that has a -5 c. dewpoint. The difference is that in a lower dewpoint environment most, or all of the sweat will evaporate, while in the higher dewpoint environment, it will not. That non-evaporation will not cool the body as effectively and cause sweating to continue as the hypothalamus attempts to maintain homeostasis. This is usually a not too comfortable situation for most folks.
it's not about just absolute max, it's about relative humidity as well: 25C at 95% feels 'hot' simply because there's not enough temp difference for the body to cool down so you start to sweat but due to high humidity that doesn't work either so you end up having sauna for free. Canadians have special expression for this: 'sticky weather'. If you have oversized AC it will cool air too quickly leaving most of the air moisture where it was and actually bringing relative humidity practically to 100% making air very 'dump' inside the house, that's what JPM was pointing to.
On the HVAC side, oversized systems, in a counterintuitive way, do not wring as much moisture out of the air as smaller capacity systems, mostly but not entirely because their compressors do not run as long, and so don't have as much moist air going through them. That means the dew point of the air in the conditioned space says high(er) - the air tends to stay more humid - making the temp. difference between the dew point and the skin less, with the dew point temp. and what's called the dry bulb temp, closer together. Since the difference between the dew point and the skin temp. is what drives the rate of sweat evaporation, less sweat will be evaporated, with the ensuing discomfort as described above as a result.
The ways Psychometrics and physiology interact are quite interesting but one of the less precise fields of engineering endeavor,
FWIW, the actual condensate load (how much moisture is "knocked out" of the air in the cooling process) can be anywhere from zero to maybe ~ 20% - 30% of the load the air conditioner sees.
Take what you want of the above. Scrap the rest.Leave a comment:
-
it's not about just absolute max, it's about relative humidity as well: 25C at 95% feels 'hot' simply because there's not enough temp difference for the body to cool down so you start to sweat but due to high humidity that doesn't work either so you end up having sauna for free. Canadians have special expression for this: 'sticky weather'. If you have oversized AC it will cool air too quickly leaving most of the air moisture where it was and actually bringing relative humidity practically to 100% making air very 'dump' inside the house, that's what JPM was pointing to.Leave a comment:
-
I live in a cooler climate.Think we passed 30 C 5 times this summer. Honestly anything is doable but at what cost. I dont have a big system and it definity isnt professional. Just conversationLeave a comment:
-
Leave a comment:
-
some of us still care, thanks for pointing to HVAC size/humidity relation, I bet this gets regularly missed.
If anyone cares: Any HVAC unit will only run long enough to satisfy the load it sees. If a window shaker sees a small load, as when cooling a well insulated space, for example, it will not run much.
If an A/C unit, window, central or otherwise is oversized, it may well produce less than desirable comfort levels in a conditioned space by not running long enough to knock enough moisture out of the dwelling air, resulting in cooler air in the dwelling that's more damp than a smaller unit running longer would produce. That happens a lot when older houses are retrofitted with a lot of insulation and building sealing without consideration of the HVAC equipment, particularly in the SE part of the U.S. and especially when a dwelling is tightened up and air leakage is reduced.Leave a comment:
-
If anyone cares: Any HVAC unit will only run long enough to satisfy the load it sees. If a window shaker sees a small load, as when cooling a well insulated space, for example, it will not run much.
not enough details; I can also state I ran my 36,000 BTU ACs this summer for 7 hrs on average daily off my solar but without details it would sound like bragging and not meaningful discussion. No matter how different your setup is the law of energy preservation still applies so 'doable' is not an argument.
If you had your AC on for only 40 min and it was enough for entire day it would mean you either live in relatively cool climate or have very efficient home or combination of both. Without context that statement doesn't mean much.
If an A/C unit, window, central or otherwise is oversized, it may well produce less than desirable comfort levels in a conditioned space by not running long enough to knock enough moisture out of the dwelling air, resulting in cooler air in the dwelling that's more damp than a smaller unit running longer would produce. That happens a lot when older houses are retrofitted with a lot of insulation and building sealing without consideration of the HVAC equipment, particularly in the SE part of the U.S. and especially when a dwelling is tightened up and air leakage is reduced.Leave a comment:
-
not enough details; I can also state I ran my 36,000 BTU ACs this summer for 7 hrs on average daily off my solar but without details it would sound like bragging and not meaningful discussion. No matter how different your setup is the law of energy preservation still applies so 'doable' is not an argument.I ran my ac this summer.Only on sunny days was it needed and usually after lunch,when the batteries have had a good charge.Whats funny is that my 5000 btu 4.6a ac unit made by Gree ran almost completely off the panels and didnt even touch the batteries.It only cools for 20 min @ 4.6 a then 1.2a just fan for 20min . Its doable. I set up my solar differently then most.
If you had your AC on for only 40 min and it was enough for entire day it would mean you either live in relatively cool climate or have very efficient home or combination of both. Without context that statement doesn't mean much.Leave a comment:
-
Either way Id be cleaning off the panels.Grid tie or notLeave a comment: