  • uscgsapper1
    Member
    • Jun 2016
    • 37

    #16
    Nope, panels into controller and 6g going from controller to bank and 4g from bank to inverter.

    Comment

    • littleharbor
      Solar Fanatic
      • Jan 2016
      • 1998

      #17
      Very strange. I would tend to suspect the batteries are shot bot you said they were new. Are they getting fully charged? What is your absorb voltage set at?
      2.2kw Suntech mono, Classic 200, NEW Trace SW4024

      Comment

      • uscgsapper1
        Member
        • Jun 2016
        • 37

        #18
        Just bought the batteries and I made sure they were new and not refurbished, I let them charge for 2 days and they reached float status before I even started to use them. Not sure what you mean by absorb voltage, if it's what I think it's around 14.2 while there is sun on panels and no load being pulled. Once they float it settles around 13.3 or so.

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15166

          #19
          Originally posted by uscgsapper1
          Just bought the batteries and I made sure they were new and not refurbished, I let them charge for 2 days and they reached float status before I even started to use them. Not sure what you mean by absorb voltage, if it's what I think it's around 14.2 while there is sun on panels and no load being pulled. Once they float it settles around 13.3 or so.
          It sounds like the batteries are ok but something is causing the TV to not run properly or it requires a lot more wattage then anticipated.

          Comment

          • uscgsapper1
            Member
            • Jun 2016
            • 37

            #20
            I'm only running the box fan right now on medium and it's drawing only 75w and after 35min of running the bank is down to 12.38, just doesn't add up.

            Comment

            • SunEagle
              Super Moderator
              • Oct 2012
              • 15166

              #21
              Originally posted by uscgsapper1
              I'm only running the box fan right now on medium and it's drawing only 75w and after 35min of running the bank is down to 12.38, just doesn't add up.
              Can you measure the current being drawn from the battery?

              It does sound like something is causing the battery to quickly discharge with only a small load connected to it.

              Comment

              • uscgsapper1
                Member
                • Jun 2016
                • 37

                #22
                Not sure how to do that? I put my load tester on the batteries when I bought them and the tested in the green, how can I test the current being drawn from the batteries? Between the batteries and the inverter?

                Comment

                • littleharbor
                  Solar Fanatic
                  • Jan 2016
                  • 1998

                  #23
                  Bulk charging mode is everything your panels can give. Absorb mode is the set voltage point where your controller will hold that voltage and allow your batteries absorb amperage until it tapers off and goes into float. If the absorb voltage level is too low your batteries will never get fully charged.

                  I think Sun Eagle is onto something though.
                  2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                  Comment

                  • uscgsapper1
                    Member
                    • Jun 2016
                    • 37

                    #24
                    It sits around 14.2 while charging until it goes into float mode around 13.2 and holds there when fully charged. But as soon as I put any load even minimal the voltage starts dropping fast, it seems like it's doing the same thing as I did before when I had a crappy dead 12v deep cycle battery (bad battery). The whole set up is acting like I'm putting a heavy load on it even if it's minimal.

                    Comment

                    • littleharbor
                      Solar Fanatic
                      • Jan 2016
                      • 1998

                      #25
                      Again, could be another problem but you need your absorb voltage about 14.7 I believe for your Trojan flooded batteries. 14.2 is even low for sealed lead acid batteries.
                      2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                      Comment

                      • uscgsapper1
                        Member
                        • Jun 2016
                        • 37

                        #26
                        My controller is a Wanderer 30a, I don't think it's adjustable, I think it's all set from factory.

                        Comment

                        • littleharbor
                          Solar Fanatic
                          • Jan 2016
                          • 1998

                          #27
                          Here's the manual for it. Possibly your battery settings are incorrect. It looks fairly easy to change. It looks like the flooded setting is 14.6 volts. that should help you get your batteries a better charge.

                          2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                          Comment

                          • Sunking
                            Solar Fanatic
                            • Feb 2010
                            • 23301

                            #28
                            OK here is your check list.

                            1. Set Controller Bulk/Absorb to 14.8 volts, and Float to 13.5 volts straight from Trojan Spec Sheet.
                            2. Disconnect everything from the battery and let it charge for a day or two. You are not going to see 14.8 volts on the battery until it is near fully charged up.Once full charged the controller will drop the voltage back to 13.5 volts.
                            3. Once charged up connect up Inverter and a load like your TV or Fan and turn it on. Measure the voltage in two places. Before and after you turn on the TV/Fan. Directly on the Battery Term Post, and at the Input Terminals on the Inverter. Example if the battery is fully charged up in noon sun you had better see 13.5 volts on both the battery and input to inverter with it turned off. Then when you turn on the Inverter and assuming it is noon with bright sunny sky, the battery should stay at 13.5 volts, and the Inverter Input voltage may drop slightly to say 13.45 volts. This is going to tell you exactly what is going on.

                            I suspect a couple of things. You have poor connections or way to long and small of wire. If the battery voltage holds 13.5 volts and you see the voltage on the Inverter drops more than 0.2 volts, you have a wiring problem.. Either to small of a wire, too long, or really poor connections.

                            Now if you do this say at night, normal battery voltage of a fully charged battery is 12.6 to 12. volts. 100 watt load on the battery will sag a bit but no more than .05 volts. If it drops to say 12.5 or less, your battery is not charged up.

                            Lastly 400 watts of panels is more than enough for a pair of Trojans. More than enough to run the TV and Fan both at the same time on a bright sunny day at noon. If not then you have a problem with the charging system you need to fix because your battery is not being charged up. You need a good 12 volt battery charger to get your new batteries charged up immediately.

                            Run the above test and you will find the problem. If it is the panels or CC we need to run 2 more test to see what is wrong.

                            EDIT NOTE:

                            If your charger has an Equalize setting use it. Crank the voltage as high as it will allow you to go. This will tell you in short order if the panels and CC works. If you see the voltage go up to above 14 volts or equal to the setting, you know the panels and charger are working, and you should see the batteries fizzing like a soda pop.
                            Last edited by Sunking; 05-21-2017, 06:00 PM.
                            MSEE, PE

                            Comment

                            • uscgsapper1
                              Member
                              • Jun 2016
                              • 37

                              #29
                              Alrighty, disconnected everything and attached a 1.5a charger, see what happens. My charge controller is not adjustable.
                              Last edited by uscgsapper1; 05-21-2017, 06:21 PM.

                              Comment

                              • Sunking
                                Solar Fanatic
                                • Feb 2010
                                • 23301

                                #30
                                Originally posted by uscgsapper1
                                Alrighty, disconnected everything and attached a 1.5a charger, see what happens.
                                Well at 1.5 amps and a 225 AH battery can take up to:

                                225 AH / 1.5 A = 150 hours or about a week Actually longer because of the batteries self discharge. You need a minimum of C/10 or 225 AH / 10 Hours = 22.5 amps.

                                Amp Hours = Amps x Hours
                                Hours = Amp Hours / Amps
                                Amps = Amp Hours / Hours.

                                A trojan T-105 can easily be discharged at C/6 with only 0.12 volt sag. C/6 is 38 amps and at 12 volts is 38 x 12 = 456 watts. Use your 500 watt Inverter, and turn it off when not in use. 1000 is a bit to much, and being your 1000 watt Inverter is MSW your TV may not like that and not work.
                                Last edited by Sunking; 05-21-2017, 06:29 PM.
                                MSEE, PE