    Question about sizing a SMA Off Grid System using Sunny Boy & Sunny Island

    Hi everyone,
    I have a question about sizing an Off Grid system using SMA components Sunny Boy and Sunny Island.
    The design of SMA is basically different than other brands. (AC Coupling) The PV Modules are connected to the Sunny Boy. The Sunny Boy is connected to the Sunny Island. Normally the PV Modules would be connected to the charge controller.
    This is the situation:
    Location Jayapura West Papua Indonesia
    Ground Mounting so optimal azimuth and tilt
    Sun Peak Hours per day 4,88 (worst case)
    Days of autonomy 1
    Operational Voltage battery bank 48 volts
    Single phase
    According to you specialists what do I need?
    So far I came up myself with:
    18 kWh per day
    Calculating losses 30%
    18/0,7 = 26 kWh
    23 300 Wp PV modules produce 26 kWh per day ((according to Sunny Design SMA design software webversion free of use, I can recommend it)
    23 x 300 = 6.9 kWp PV System
    2 x Sunny Boy 3600 TL 21
    1 x Sunny Island 8.0H
    48 x 2 volt 620 Ah batteries
    Please advice
    Thanks a lot and for everybody a fine newyears eve and a fantastic sunny 2017



  • solarix
    Super Moderator
    • Apr 2015
    • 1415

    #2
    Do you need 240Vac? SunnyIslands only do 120V and if you need 240V (or need to intertie with a 240V grid), you need to either use dual SunnyIslands or use their "SMArtformer". Gets pretty expensive....
    BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

    Comment

    • Bendesa1962
      Solar Fanatic
      • Nov 2016
      • 112

      #3
      Originally posted by solarix
      Do you need 240Vac? SunnyIslands only do 120V and if you need 240V (or need to intertie with a 240V grid), you need to either use dual SunnyIslands or use their "SMArtformer". Gets pretty expensive....
      Hi thanks for your reply. In Indonesia we need 220 volts AC and 50 Hz cycle power.

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Other problem. 18KWh daily usage & est 26KWh harvest, leaves little space for recharging after 1 cloudy day.
        with a 59,520 KWh battery getting a generator would be essential to keep the battery healthy, since you don't have much extra solar capacity
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • solarix
          Super Moderator
          • Apr 2015
          • 1415

          #5
          "In Indonesia we need 220 volts AC and 50 Hz cycle power." Just make sure you get the (non-US version) SMA inverters that can be configured for your power type.
          BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

          Comment

          • Bendesa1962
            Solar Fanatic
            • Nov 2016
            • 112

            #6
            yes I found out about that. The US versions have a output of 120 Volt. The none US versions can be used here in Indonesia Thanks for your tip!