I just read in the general discussion forum that 60 cell panels are considered 20v "nominal" panels", that does not have ample voltage to properly charge a 24v battery bank. Is this true? Just to get a proper answer about my panels, They are 60 cell 250 watt
Pmp 250Wp
Voc. 37.0
Isc. 9.081A
Vmp 30.0V
Imp. 8.108A
Maximum system voltage. 1000 VDC
Maximum reverse current. 10A
And the model No being 20250 sounds like 20v 250 w
I hope I don't have to start over with questions. But here it goes.
This system is not wired up yet but consist of 4 of these 60cell 250w panels that y'all will decide what the best way to wire together into a Renogy commander 40 amp MPPT12/24 CC, 24v battery bank=10-12v 100Ahr batteries wired in series, Xantrex statpower 800w/24v inverter, all will be wired with 6 gauge copper.
Should I still just look at this as a 1000w pv array. And wire the panels in 2-sets consisting of 2 panels in series then wire both sets parreled into the CC?
Believe me, like I said the more I read the deeper it gets. But not going to assemble the system until I get the go ahead.
Thanks!
Pmp 250Wp
Voc. 37.0
Isc. 9.081A
Vmp 30.0V
Imp. 8.108A
Maximum system voltage. 1000 VDC
Maximum reverse current. 10A
And the model No being 20250 sounds like 20v 250 w
I hope I don't have to start over with questions. But here it goes.
This system is not wired up yet but consist of 4 of these 60cell 250w panels that y'all will decide what the best way to wire together into a Renogy commander 40 amp MPPT12/24 CC, 24v battery bank=10-12v 100Ahr batteries wired in series, Xantrex statpower 800w/24v inverter, all will be wired with 6 gauge copper.
Should I still just look at this as a 1000w pv array. And wire the panels in 2-sets consisting of 2 panels in series then wire both sets parreled into the CC?
Believe me, like I said the more I read the deeper it gets. But not going to assemble the system until I get the go ahead.
Thanks!