Solar pandel and voltage divider problem, please help

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Geebbon
    Junior Member
    • Jul 2016
    • 5

    #1

    Solar pandel and voltage divider problem, please help

    Hello,
    I have a 87.5W solar panel which should provide 5.68A at 15.4V (18.48V open circuit).
    I want to connect 2 devices on it. One operates at 15V and can take up to 10A the other one operates at 12V and takes 0.2A.
    I have tried to build voltage divider which gives me when measured 15V and 12V.
    But when i connect device on 12V branch it does not work. If i measure voltage with device connected it shows only 1.8V.
    This is diagram of the wiring:

    solar.png

    All Rs are 10k Ohm.


    When i connect both devices only device1 runs.
    When i connect only device1 it runs.
    When i connect only device2 it does not run.
    When i connect device2 to 15V it runs.
    When i connect both devices parallel on 15V just device1 runs.

    As i wrote earlier, i measured branches with voltmeter and 1st shows 15V second shows 12V. Yet nothing runs from second branch.

    Im eletric newbie, could you please give me some hints what am i doing wrong? I though of putting battery (with some charge controller) before the devices but it gets expensive and i dont require battery, i need this only to run when its sunny.

    Thank you for any insight.
    Geebbon
    Attached Files
    Last edited by Geebbon; 07-06-2016, 09:12 AM.
  • sensij
    Solar Fanatic
    • Sep 2014
    • 5074

    #2
    Think about your design... For the 12 V circuit, how much power dissipation did you calculate for those 10k resistors? Why would any current flow through a 10k resistor when it can go to device 1 instead?
    CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

    Comment

    • bcroe
      Solar Fanatic
      • Jan 2012
      • 5213

      #3
      Originally posted by Geebbon
      Hello,
      I have a 87.5W solar panel which should provide 5.68A at 15.4V (18.48V open circuit).
      I want to connect 2 devices on it. One operates at 15V and can take up to 10A the other one operates at 12V and takes 0.2A.
      I have tried to build voltage divider which gives me when measured 15V and 12V.
      But when i connect device on 12V branch it does not work. If i measure voltage with device connected it shows only 1.8V.
      This is diagram of the wiring:
      All Rs are 10k Ohm.
      When i connect both devices only device1 runs.
      As i wrote earlier, i measured branches with voltmeter and 1st shows 15V second shows 12V. Yet nothing runs from second branch.
      Geebbon
      Welcome to Circuits 101. The voltage from your divider will change as soon as you draw current, because the circuit is changed.

      Look at Device 2. At 12V and 0.2A, it could be considered a 60 ohm resistor. In parallel with the 4 10K resistors, the load
      appears as 59.91 ohms. That load is being fed by the single 10K resistor to 15V, forming a voltage divider with an intermediate
      voltage of 0.0893V. The reason you're are getting even 1.8V, is that Device 2 contains some non linear devices (diodes, etc)
      that don't conduct till about 1V is applied. Bruce Roe
      Last edited by bcroe; 07-06-2016, 11:28 AM.

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        It is called Kirchoff's Law you know nothing about.
        MSEE, PE

        Comment

        • Geebbon
          Junior Member
          • Jul 2016
          • 5

          #5
          Well when i think of it yeah.. why would it...
          And when i think of it i guess 10k resistor even dampens the current so that device2 dont even run alone...
          hmmm

          could you point me to some direction that would actually work?

          Comment

          • bcroe
            Solar Fanatic
            • Jan 2012
            • 5213

            #6
            Originally posted by Geebbon
            Well when i think of it yeah.. why would it...

            could you point me to some direction that would actually work?
            You need a series element to drop 15V to 12V. The simplest way might be 4 to 6 diodes in series, wired in
            the conduction direction. There are an infinite number of ways. Bruce Roe

            Comment

            • Geebbon
              Junior Member
              • Jul 2016
              • 5

              #7
              Originally posted by Sunking
              It is called Kirchoff's Law you know nothing about.
              Obviously :-/


              Guess i need to balance the resistance on both branches. Is that correct? But that would be hard when device1 takes whatever amp i feed it up to 10 and with "variable" source such as solar panel.

              If i could stabilize input voltage by voltage regulator to 15V and i know that panel gives 5.68A then i guess i could calculate draw from device1 by substracting draw from device2 and calculating precise resistance values...

              Would that be work?

              Comment

              • Geebbon
                Junior Member
                • Jul 2016
                • 5

                #8
                Originally posted by bcroe

                You need a series element to drop 15V to 12V. The simplest way might be 4 to 6 diodes in series, wired in
                the conduction direction. There are an infinite number of ways. Bruce Roe


                But this way if i connect device1 on 15V before the diodes woudln't it still go through the device1 instead of going through diodes?

                Comment

                • bcroe
                  Solar Fanatic
                  • Jan 2012
                  • 5213

                  #9
                  Originally posted by Geebbon



                  But this way if I connect device1 on 15V before the diodes woudln't it still go through the device1 instead of going through diodes?
                  If your source can maintain 15V, the circuit to Device 2 will work regardless of Device 1. With voltage applied, current goes anywhere
                  and everywhere there is a path; it doesn't chose. Bruce Roe

                  Comment

                  • Geebbon
                    Junior Member
                    • Jul 2016
                    • 5

                    #10
                    Originally posted by bcroe

                    If your source can maintain 15V, the circuit to Device 2 will work regardless of Device 1. With voltage applied, current goes anywhere
                    and everywhere there is a path; it doesn't chose. Bruce Roe

                    I cuurently have just 3 diodes. Which drop around 0.5V. I will try it tomorrow if i manage to go to the store after work. I will let you know if it worked. Thanks for suggestion.

                    Comment

                    • Sunking
                      Solar Fanatic
                      • Feb 2010
                      • 23301

                      #11
                      Originally posted by Geebbon
                      Obviously :-/


                      Guess i need to balance the resistance on both branches. Is that correct?
                      No, none of the above. Use voltage regulators. I am not going to help you any further as it is way beyond your knowledge and capabilities.
                      MSEE, PE

                      Comment

                      • DaveDE2
                        Solar Fanatic
                        • Feb 2016
                        • 185

                        #12
                        Originally posted by Geebbon
                        Hello,
                        I have a 87.5W solar panel which should provide 5.68A at 15.4V (18.48V open circuit).
                        I want to connect 2 devices on it. One operates at 15V and can take up to 10A the other one operates at 12V and takes 0.2A.
                        Geebbon
                        If you have one device that operates at 15v and 10A, that's 150W, more than your panel can provide. A non-starter no matter what you do.

                        Comment

                        • Mike90250
                          Moderator
                          • May 2009
                          • 16020

                          #13
                          Use a zener diode on a heat sink, rated for the desired voltage, and 2x the amperage of the PV panel. (Simple, 2 parts, diode & heat sink)

                          But first, you need a PV panel of the right size, should be at least 2x the load you want to power, to insure it will work beyond solar noon.
                          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                          solar: http://tinyurl.com/LMR-Solar
                          gen: http://tinyurl.com/LMR-Lister