System Design for Dock Lights

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Datech
    Junior Member
    • May 2016
    • 8

    System Design for Dock Lights

    I've been trying to design a solar system for my in-laws' dock, but I've been running into some issues and wanted to make sure I've got the calculations right.

    Background:
    - Off-grid system to provide power for lights on a boat dock
    - Dock already has electrical appliances (listed below) as it used to be hooked up to land power
    - Dock is a two bay, two story with a top sun deck, and the edges of the sun deck has a slightly sloped tin roof angled toward the sun that are about 3'x25' (hopefully will mount panels here)
    - Primarily need power for lights at night (4-5 hours)
    - Will also use power for vacuuming the boat and maybe powering a fan or a speaker
    - Since this is a boat dock we won't be using it much, if any, in the winter, so the calculations below should cover the maximum need

    Current Appliances:
    - Two motion sensor flood light fixtures with two bulbs each (4 bulbs total)
    - Four accent lights on top deck (4 bulbs total)
    - Two general purpose lights over each bay (2 bulbs total)
    - Four total standard receptacles

    In order to make this work, we can change the bulbs to anything. I'm thinking 11W CFLs for the accent lights, some low wattage LEDs for the flood lights, and probably some 15-20W CFLs for the general purpose lights. I don't have specifics on the vacuum, but from a quick Google search it seems the average is around 450W (probably no more than 15 minutes for a boat). A fan seems to be about 100W, and to be safe that could be up to 8 hours continuous run. Other stuff like iPhone or Bluetooth speaker charging will hopefully be negligible.

    With all of that info, I keep coming back to 4x 160W panels, a 1000W inverter, and 2x 220Ah 12V batteries minimum. I know I can cut some off by keeping the fan and the vacuum out of the calculation, but I figured I'd start high.

    Questions:
    1. Am I even close on the calculations?
    2. If I'm close, is there any where I can reasonably cut back?
    3. Any reason I should go with 24V instead of 12V?
    4. Should I piece the design together myself, or order a kit?
    5. Should I worry about loss at the panels since they'll be mounted on a tin roof on a dock?
    6. Aside from dropping components into the water and general electrical safety, anything I should worry about with a solar system on a dock?
    7. Any reputable suppliers that you guys prefer over others?

    Thanks!
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15125

    #2
    You may have an issue with what you have picked out but lets go through the math.

    Have your added up all of your loads and how long each will run to get a total daily watt hour usage?

    If not then looking at your 2 x 12v 220Ah batteries, if you connect them in parallel you have a 12v 440Ah system which can get you about (12v x 440Ah x 25% = 1320watt hours) a day.

    And a pv system with 4 x 160watt = 640watt. With a 60amp MPPT charge controller you can get up to 53amps (if you get a few hours of uninterrupted sun) which is fine for that 440Ah system.

    The 1000 watt inverter should work but can easily drain those batteries if you do not pay attention.

    So your batteries, panel wattage, inverter should work if you use a true 60A MPPT type CC.

    But the question is, will 1320 watt hours be enough for you when you end up using that vacuum system along with all your lights and that fan on a day that does not get you much sun?

    Comment

    • Datech
      Junior Member
      • May 2016
      • 8

      #3
      Originally posted by SunEagle
      Have your added up all of your loads and how long each will run to get a total daily watt hour usage?
      I picked out some bulbs on Amazon to make it simple, so we'll use this going forward:
      - 4x 14W (100W eq) LED floodlights, total of 1 hour a day since they'll mainly be security lights: 56W
      - 4x 14W (60W eq) accent lights, probably brighter than I need, for 5 hours at night: 280W
      - 2x 9W (65W eq) overhead lights, for 4 hours at night: 72W
      - 1x 450W vacuum for 15 minutes: 112.5W
      - 1x 100W fan for 8 hours (overkill): 800W

      That adds up to 1320.5W, which would be the very high end of use. Since I would be very surprised if we ran the fan for 8 straight hours, I feel like that's a pretty safe estimate for 50% DOD for sizing. I'm considering just closing off the receptacles and saying lights-only in order to keep costs down.

      Originally posted by SunEagle
      So your batteries, panel wattage, inverter should work if you use a true 60A MPPT type CC.
      I didn't mention it, but I originally had a 45A MPPT charge controller. Did I miss something that would tell me I should get the 60A? Also, since this is a boat dock in Georgia that will almost exclusively be used during the swimming season (or at least 55 degrees and up), could I generate some cost savings by going PWM?


      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15125

        #4
        Originally posted by Datech

        I picked out some bulbs on Amazon to make it simple, so we'll use this going forward:
        - 4x 14W (100W eq) LED floodlights, total of 1 hour a day since they'll mainly be security lights: 56W
        - 4x 14W (60W eq) accent lights, probably brighter than I need, for 5 hours at night: 280W
        - 2x 9W (65W eq) overhead lights, for 4 hours at night: 72W
        - 1x 450W vacuum for 15 minutes: 112.5W
        - 1x 100W fan for 8 hours (overkill): 800W

        That adds up to 1320.5W, which would be the very high end of use. Since I would be very surprised if we ran the fan for 8 straight hours, I feel like that's a pretty safe estimate for 50% DOD for sizing. I'm considering just closing off the receptacles and saying lights-only in order to keep costs down.



        I didn't mention it, but I originally had a 45A MPPT charge controller. Did I miss something that would tell me I should get the 60A? Also, since this is a boat dock in Georgia that will almost exclusively be used during the swimming season (or at least 55 degrees and up), could I generate some cost savings by going PWM?

        With 640 watt of panels and using 12volt battery your MPPT "could" see as much as 53amps (640w / 12v = 53.3a) so to be safe going with a 60A CC would be better then overloading a 45A CC.

        But if you do not get maximum sunlight your panels may only generate less than 50 amps so you could be ok depending on how much that 45A CC can accept for input wattage.

        Once you exceed 200 watts a PWM CC basically "steals" wattage from you. Since a PWM is Amps in = Amps out then you will only get the total amps of the 4 panels if you wire them all in parallel. That will probably come to less than 10 amps each or less than 40amps total. Which should ok for your PWM CC but basically turns that 640 watt system into a 450watt system. If that is ok with you then that is your choice.

        Comment

        • Datech
          Junior Member
          • May 2016
          • 8

          #5
          Ah, that's the info I wasn't paying attention to, thanks!

          Maybe I should approach this from the other end, by starting small and then building in the head room.
          Device Units Watts Hours Total
          Flood Lights 4 14 1 56
          Accent lights 4 14 5 280
          Overhead Lights 2 9 4 72
          Vacuum 1 450 1/6 75
          Fan 1 30 4 120
          Total 517 603
          I switched to a small 30W fan, and changed the vacuum to 10 minutes, putting me at 603Whr.

          Here's the rest of the calculations

          Battery Capacity
          Watt Hours (W*hr): 603
          Battery Voltage (V): 12
          Battery Capacity (Ah): 50.25
          Battery Capacity @ 50% DOD: 100.5
          Specc'd Capacity (Ah): 100
          12V 100Ah Deep Cycle: $149.95


          Solar Panel
          Power Output of Panels: 1200
          Effective Hours/Day: 4
          Power Generated Per Hour (W): 300
          Number of Panels: 3
          Power per Panel (W): 100
          3x Renogy 100W Panels: $419.97


          Charge Controller
          Charge Controller Rating (V): 12
          Current Rating (A): 25
          MPPT Tracer CC 30A: $158.19

          Inverter

          Max Load (W): 517
          Zamp 600W Pure Sine Inverter: $202.96


          If this is the absolute minimum:
          1. Do my calculations look so I can scale up from here?
          2. Any comments on the materials chosen?
          3. I understand the majority of the wiring between the CC, batteries, and inverter, but how do the panels get wired to the CC?

          Comment

          • Datech
            Junior Member
            • May 2016
            • 8

            #6
            Ah, that's the info I wasn't paying attention to, thanks!

            Maybe I should approach this from the other end, by starting small and then building in the head room.
            Device Units Watts Hours Total
            Flood Lights 4 14 1 56
            Accent lights 4 14 5 280
            Overhead Lights 2 9 4 72
            Vacuum 1 450 1/6 75
            Fan 1 30 4 120
            Total 517 603
            I switched to a small 30W fan, and changed the vacuum to 10 minutes, putting me at 603Whr.

            Here's the rest of the calculations

            Battery Capacity
            Watt Hours (W*hr): 603
            Battery Voltage (V): 12
            Battery Capacity (Ah): 50.25
            Battery Capacity @ 50% DOD: 100.5
            Specc'd Capacity (Ah): 100
            12V 100Ah Deep Cycle: $149.95

            Solar Panel
            Power Output of Panels: 1200
            Effective Hours/Day: 4
            Power Generated Per Hour (W): 300
            Number of Panels: 3
            Power per Panel (W): 100
            3x Renogy 100W Panels: $419.97

            Charge Controller
            Charge Controller Rating (V): 12
            Current Rating (A): 25
            MPPT Tracer CC 30A: $158.19

            Inverter

            Max Load (W): 517
            Zamp 600W Pure Sine Inverter: $202.96

            If this is the absolute minimum:
            1. Do my calculations look so I can scale up from here?
            2. Any comments on the materials chosen?
            3. I understand the majority of the wiring between the CC, batteries, and inverter, but how do the panels get wired to the CC?

            Comment

            • SunEagle
              Super Moderator
              • Oct 2012
              • 15125

              #7
              Your calculations are close but discharging your battery to 50% daily will shorten it's life and leave you in the dark if you get more than 2 days without sun light, so let me help you.

              Your daily load is 603wh. You should only discharge your battery about 25% a day so you would multiply that 603wh x 4 = 2412wh battery system. That gives you a couple of days to use your battery without needing to recharge it fully.

              Divide that value by your battery voltage of 12v. 2412 wh / 12v = 201 Ah. So you will need 2 of those 12v 100Ah batteries wired in parallel.

              Next to size your panel you need to use 1/10th the battery system Ah rating which would be 20 amps. Multiply that by the battery voltage of 12v. 20A x 12V = 240watts. So 300watt of panels should be able to get your 200Ah battery charged up if you use an MPPT type CC rated at least 25 amps which I have been told that 30a Tracer is.

              And that 600w pure sine inverter is sized a little high for a 200Ah battery so you will need to manage what you plug in and try to make sure you do not exceed that 603 daily watt hour usage.

              Finally while you may have properly calculated your daily watt hour usage most people do not include losses between the solar panels & charge controller & battery & inverter. Every item is not 100% efficient so you lose a little output at each stage. More than likely you will end up using more than 603 watthours which means you will discharge your 200Ah battery more than 25%. So be aware of your system limitations and how easy it will be to kill your batteries if you do not keep an eye on them.

              Comment

              • Datech
                Junior Member
                • May 2016
                • 8

                #8
                Originally posted by SunEagle
                Your calculations are close but discharging your battery to 50% daily will shorten it's life and leave you in the dark if you get more than 2 days without sun light, so let me help you.
                Thank you! I can use my limited electrical engineering background and all of the calculations I want but it's hard to replace experience.

                I'm good with the batteries in parallel. I was hoping I could add some headroom, but I wasn't sure if adding the battery meant scaling up the rest of the system too so it's good to know that's the recommendation. For the sine inverter, if it's a little high then can I get away with a 500W? It seems like there are a lot more 500W inverters out there with reputable reviews than there are 600W.

                Would throwing a simple meter on the batteries be sufficient to monitor charge, or are you suggesting I should ensure I leave the system open to adding another battery in parallel later? Obviously adding another panel would also change my CC, but if that's needed it should be a simple rip/replace of what I've already specc'd, right?

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15125

                  #9
                  Originally posted by Datech

                  Thank you! I can use my limited electrical engineering background and all of the calculations I want but it's hard to replace experience.

                  I'm good with the batteries in parallel. I was hoping I could add some headroom, but I wasn't sure if adding the battery meant scaling up the rest of the system too so it's good to know that's the recommendation. For the sine inverter, if it's a little high then can I get away with a 500W? It seems like there are a lot more 500W inverters out there with reputable reviews than there are 600W.

                  Would throwing a simple meter on the batteries be sufficient to monitor charge, or are you suggesting I should ensure I leave the system open to adding another battery in parallel later? Obviously adding another panel would also change my CC, but if that's needed it should be a simple rip/replace of what I've already specc'd, right?
                  Well I own a pretty good 600w pure sine wave inverter made by Xantrex. It is a little big for my 200Ah battery system but I also have a kill a watt meter which can track how much I use.

                  Two other little items you need to know about.

                  The first is that if you wire more than 2 batteries in parallel you can easily end up with unequal charging and discharging. That can kill one or more batteries much faster then it's rated life. A good system consists of all the batteries wired in series. That means you use lower voltage (2v, 4v, 6v) batteries with higher Ah rating. In my case I used 4 x 50Ah 12volt batteries wired in parallel to make a 12v 200Ah system when I should have used 2 x 6v 232Ah batteries wired in series for a 12v 232Ah system. The first way (4 in parallel) has a chance of the batteries failing sooner than later as well as costing much more (~ $400) then the second way (~ $250).

                  Second issue is that you can't just add new batteries to an existing system. Old batteries will "pull down" the performance of new ones that are not the same age or size. Sort of like one bad apple spoils the bunch idea. So expanding a system usually means replacing all the batteries at the same time while you increase the panel wattage and if necessary the Charge controller.

                  Comment

                  • Mike90250
                    Moderator
                    • May 2009
                    • 16020

                    #10
                    Consider 2 inverters, a small, low tare, 300w for the lights and fan, and a larger 1,000w that you only switch on for the vacuum or other large load.
                    And there is a lot you can do with 12V LED malibu style garden lights, leave the inverter off.
                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    • Datech
                      Junior Member
                      • May 2016
                      • 8

                      #11
                      Originally posted by Mike90250
                      Consider 2 inverters, a small, low tare, 300w for the lights and fan, and a larger 1,000w that you only switch on for the vacuum or other large load.
                      And there is a lot you can do with 12V LED malibu style garden lights, leave the inverter off.
                      I like the idea, but I'm not sure if I could make that work with the electrical system that's already on the dock. The dock expects an input from the land at the end of the gangway, and our plan was to have this system contained in a deck box near one of the bays. We would then splice the inverter output into the breaker just before the first receptacle. I'm having trouble comprehending how I would split that between two inverters.

                      Also, I had another post yesterday that had a bunch of Amazon links that are probably awaiting moderation. I'll post if here without the links for one final look. Aside from further considerations about two inverters, I think this might be my final system:
                      Part Cost Quantity Total Cost
                      12V 100Ah Deep Cycle Battery $ 155.87 2 $ 311.74
                      MPPT TRACER 30A Charge Controller $ 158.19 1 $ 158.19
                      Renogy 100W Solar Panels (3pc set) $ 415.91 1 $ 415.91
                      Zamp 600W Pure Sine Inverter $ 202.96 1 $ 202.96
                      MC4 Assembly Tool $ 6.99 1 $ 6.99
                      14W Flood Lights (4 pack) $ 46.80 1 $ 46.80
                      DC Voltmeter $ 9.80 1 $ 9.80
                      Renogy Mounting Brackets (set of 4) $ 44.99 1 $ 44.99
                      Renogy 5 Pair MC4 Connectors $ 9.99 1 $ 9.99
                      10ft Renogy Solar Extension Cable $ 14.99 6 $ 89.94
                      7ft Dock Box from Overton $ 634.99 1 $ 634.99
                      Total: $ 1932.30
                      If I have a 30' run from the panels to the CC I would need a 10# wire, correct? I believe that's the gauge of those 10ft Renogy cables and I would string 3 together. Otherwise I'll source that wire (and all of the other wire for CC to battery, battery to battery, and battery to inverter) locally and attach the MC4s as appropriate.

                      Final thoughts?
                      Last edited by Datech; 05-19-2016, 10:59 AM.

                      Comment

                      • SunEagle
                        Super Moderator
                        • Oct 2012
                        • 15125

                        #12
                        Originally posted by Datech

                        I like the idea, but I'm not sure if I could make that work with the electrical system that's already on the dock. The dock expects an input from the land at the end of the gangway, and our plan was to have this system contained in a deck box near one of the bays. We would then splice the inverter output into the breaker just before the first receptacle. I'm having trouble comprehending how I would split that between two inverters.

                        Also, I had another post yesterday that had a bunch of Amazon links that are probably awaiting moderation. I'll post if here without the links for one final look. Aside from further considerations about two inverters, I think this might be my final system: [TABLE="border: 1, cellpadding: 1, width: 500"]
                        ...

                        If I have a 30' run from the panels to the CC I would need a 10# wire, correct? I believe that's the gauge of those 10ft Renogy cables and I would string 3 together. Otherwise I'll source that wire (and all of the other wire for CC to battery, battery to battery, and battery to inverter) locally and attach the MC4s as appropriate.

                        Final thoughts?
                        Ahhh. Hold the phone. You want to build and off grid system that is "spliced into" a grid fed power panel.

                        Please do not do this because in most cases it would be illegal and unsafe without using the proper connecting system and expertise to use it. Also anytime you connect an electrical generation system that could "back feed" the grid you have to have approval from your POCO and local permitting people.

                        Comment

                        • Datech
                          Junior Member
                          • May 2016
                          • 8

                          #13
                          Originally posted by SunEagle

                          Ahhh. Hold the phone. You want to build and off grid system that is "spliced into" a grid fed power panel.

                          Please do not do this because in most cases it would be illegal and unsafe without using the proper connecting system and expertise to use it. Also anytime you connect an electrical generation system that could "back feed" the grid you have to have approval from your POCO and local permitting people.
                          Oh nonononono, that's not the plan. The dock's existing system was *designed* to be hooked up to the grid. It is not, and will not be hooked up to the grid (otherwise I wouldn't be chatting with you guys). This dock was purchased used and moved to a new location. The Corps of Engineers will not grant us the permit to extend grid power to the dock's new location.

                          My "splice" will simply be removing the connections that extended out along the gangway, and wiring in the inverter output. It's expecting 120VAC, and that's what I intend to give it. Sorry for the confusion!

                          Comment

                          • SunEagle
                            Super Moderator
                            • Oct 2012
                            • 15125

                            #14
                            Originally posted by Datech

                            Oh nonononono, that's not the plan. The dock's existing system was *designed* to be hooked up to the grid. It is not, and will not be hooked up to the grid (otherwise I wouldn't be chatting with you guys). This dock was purchased used and moved to a new location. The Corps of Engineers will not grant us the permit to extend grid power to the dock's new location.

                            My "splice" will simply be removing the connections that extended out along the gangway, and wiring in the inverter output. It's expecting 120VAC, and that's what I intend to give it. Sorry for the confusion!
                            Sorry. My misunderstanding.

                            Now your question is how to wire from your "inverter" to a distribution panel. I will tell you that backfeeding a receptacle is not a good idea so if I was doing it I would install a circuit breaker rated for just under the maximum output of that inverter into the dock's panel box and run the wire between the inverter and circuit breaker in a raceway to protect it.

                            While this should work it does open you up to allowing anything that is powered from the docks panel to be turned on at the same time and overloading the inverter or quickly draining the battery.

                            I would feel a safer set up would be to use a rated extension cord plugged into the inverter and then plug the load you want to use into the other end of that extension cord. That could be any of the lighting or that vacuum cleaner. That way you can control your "loads".

                            Comment

                            • Datech
                              Junior Member
                              • May 2016
                              • 8

                              #15
                              Well the project is finished and working well! I ended up making a post on reddit with a link to the Imgur album here: ​https://www.reddit.com/r/SolarDIY/co...wer_on_a_dock/