Sunking mentioned in one of the stickies about the relationship between inverter size and battery voltage - that 2000W should be the limit of 24V. I have two MPPT 80 CCs capable of 600 V at 80 Amps. My system was sized with a 4000 W inverter (Schneider XW4024). I told the vendor I wanted to stick to 24V and this is what they pointed me to. The smallest cables I have from my power panel to my battery is a #2 (Amazon: Camco 47485 Red 3/8" Stud 36" Long 2-Gauge Marine Battery Cable and Lug Assembly Tinned) and those that came with the battery (1575 AH) which are #0 AWG and were already tipped by the manufacturer.
At present, I have a 4230W PV system, which means I could theoretically reach 176 Amps of charging. Most of the time, being a battery backup system, my inverter is doing the charging and not at very high amps, though it could do so if the SoC is low after running off batteries for some time. I also have a BTS which would allow the CCs and Inverter to adjust the charge to compensate for battery temp.
I would hope that someone selling systems such as mine was aware of maximum amps per wire gauge and that I was not sold a fire hazard. I'd also wonder why Schneider would make an inverter that supports 4000 W yet can operate at 24 V and also be UL listed.
All that aside - Is my setup problematic like this? Secondly, since this IS what I have, and I'm not eager to plunk down $6k on a 48V battery - would it be recommended to limit the amps of the CC charger based on wire gauge rather than the C/10-C/12 range?
At present, I have a 4230W PV system, which means I could theoretically reach 176 Amps of charging. Most of the time, being a battery backup system, my inverter is doing the charging and not at very high amps, though it could do so if the SoC is low after running off batteries for some time. I also have a BTS which would allow the CCs and Inverter to adjust the charge to compensate for battery temp.
I would hope that someone selling systems such as mine was aware of maximum amps per wire gauge and that I was not sold a fire hazard. I'd also wonder why Schneider would make an inverter that supports 4000 W yet can operate at 24 V and also be UL listed.
All that aside - Is my setup problematic like this? Secondly, since this IS what I have, and I'm not eager to plunk down $6k on a 48V battery - would it be recommended to limit the amps of the CC charger based on wire gauge rather than the C/10-C/12 range?