Charge controller, battery & inverter connections

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • nayubis
    Junior Member
    • Sep 2010
    • 4

    #1

    Charge controller, battery & inverter connections

    Question on charge controller, battery & inverter connections.

    From the off-grid basic setup scheme :
    Array >> Charge Controller >> Battery / Inverter >> AC load

    1 - Where is the inverter drawing power from?
    2 - Are the battery & inverter connected in parallel to the charge controller or are they
    connected in series?

    If the battery & inverter are connected in parallel (that is, battery & inverter positive terminals connected together & their negative terminals similarly connected together) and then connected to the charge controller, is the inverter drawing power from the battery or from the charge controller ?

    Is it possible for the inverter to draw power directly from the array instead of getting power from the battery during DAYTIME to lessen the charge/discharge cycles of the battery? And then at the same time charge the battery to be used during NIGHTTIME.

    Is this possible at all? Can anyone help, please?

    Thanks.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    First, connect the inverter cables to the battery posts. This places the high current wire next to the battery terminal, less loss.

    Then, either on top of inverter cable, or on the other side of the battery post, your charge controller connections, and the Battery Temperature Sensor goes on top of that.

    If you have more than one battery, read up on connecting on the "diagonal"

    Inverter and Charger connect to the same terminals.

    Here's a great article about connecting batteries in parallel (on the diagonal)
    http://www.smartgauge.co.uk/batt_con.html (connect batteries on diagonal )

    and some other battery stuff:

    http://www.windsun.com/Batteries/Battery_FAQ.htm (short & sweet)
    http://www.batteryfaq.org/ (very large)

    Generally, much easier to manage 2, 6V in series, than 2, 12V in parallel. Same wattage.



    Don't forget a fuse on your battery, I love the simple and compact MRBF terminal fuse by blue sea (MRBF - Marine Rated Battery Fuse)

    Get the fuse & holder.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #3
      Originally posted by nayubis
      1 - Where is the inverter drawing power from?
      2 - Are the battery & inverter connected in parallel to the charge controller or are they
      connected in series?
      1., From the batteries mainly, sometimes from both batteries and solar panels, and at rare times just the panels. Depends. Battery acts as a buffer..
      2. Neither really. The batteries are connected to the output of the CC


      Originally posted by nayubis
      If the battery & inverter are connected in parallel (that is, battery & inverter positive terminals connected together & their negative terminals similarly connected together) and then connected to the charge controller, is the inverter drawing power from the battery or from the charge controller ?
      It depends on the state of charge of the batteries, how much load you are demanding, and how much power the panels are producing. It is all a balancing act that has to equal.

      For example lets say it is solar noon, batteries are fully charge, and power demand is less than the maximum input power to the CC from the panels. In that case provide the power.

      However if demand exceeds the input power from the panels it comes from both panels and batteries making up for the short fall If it is dark, all batteries.




      Originally posted by nayubis
      Is it possible for the inverter to draw power directly from the array instead of getting power from the battery during DAYTIME to lessen the charge/discharge cycles of the battery? And then at the same time charge the battery to be used during NIGHTTIME.
      Think I just covered that. However if you asking can you connect panels directly to a battery inverter the answer is NO.

      Battery inverters have vary narrow input voltage requirements that have to be met, and solar panels are not voltage sources they are current sources with willy large voltage variations the inverter cannot tolerate. Therefor you must have a battery acting as a buffer, or some kind of voltage regulation.
      MSEE, PE

      Comment

      • nayubis
        Junior Member
        • Sep 2010
        • 4

        #4
        Thank you for the quick response.

        Comment

        • xyxoxy
          Junior Member
          • May 2011
          • 14

          #5
          Similar question

          My question is very similar to the one posted here but I just want to be sure I understand.

          Mine is a very small system designed to add minimal LED lighting to an out-building. One 50W x 12v panel with a single 12v x 50 Amp Hour AGM battery and an 1100 Watt inverter.

          My charge controller has a set of terminals each for the panel(s), the battery, and the "load". The connections to the solar panel and the battery are obvious and if I understand correctly I can use regular 12-14 gauge household wire for those connections as they are only carrying a small charge from the panel and no run is more than 20 feet.

          However I'm not sure if I should connect the inverter to the "load" terminals on the charge controller or directly to the battery. It seems the charge controller should be able to kill the load on the battery if the charge drops below a set level... assuming the inverter is connected to it. Or should that be the inverter's job? Are the "load" terminals only for DC powered devices?

          Also I believe the inverter needs to connect to the battery with heavier gauge wire than what comes from the panels since the current depends on what you are trying to power. I think something I read said to use 6 Gauge battery cables. But I'm not sure what gauge wire is safe to use with my small 10 Amp charge controller if it is between the battery and the inverter.

          I'm just figuring this all out and still waiting on some parts so any advice is appreciated.

          - Mickey

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Charge controller load terminals are only for small, low amp loads. Connecting an inverter will blow the controllers fuse, or the controller. It should state the limits in your paperwork.

            inverters generally have their own Low Voltage Disconnect.

            14 ga wire is generally safe for 15Amps Be sure you use a fuse near the battery, in case the + wire develops a short, the fuse blows, life is fine. No fuse, and something happens, you get a fire.

            Use what the inverter suggests for wire.

            Longer wires need to be larger gauge (smaller number, 12ga is larger than 14 ga, just like shotguns ! )
            Last edited by Mike90250; 05-19-2011, 02:55 PM.
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • xyxoxy
              Junior Member
              • May 2011
              • 14

              #7
              Thank you for clearing that up!
              I expect most of my load will be from AC devices through the inverter. So unless I'm going to string some 12v DC xmas lights or something along those lines I probably won't even use the "Load" terminals on the controller... is that right?

              I was also planning to ask about fuses next. You say "... Near the battery...". Can you be more specific? Are we talking a 10Amp fuse between the battery and inverter? Between the controller and the battery? Both? And do I only need to fuse the positive wire(s) or negative as well? If I don't fuse the negative do I need a ground wire?

              I'm pretty comfortable with AC household wiring projects but this off-grid DC stuff is new to me.

              Thanks again!
              - Mickey

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                I love the simple and compact MRBF terminal fuse by blue sea (MRBF - Marine Rated Battery Fuse)

                Get the fuse & holder. Bolts to the battery terminal, and is a very clean install.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #9
                  Originally posted by Mike90250
                  I love the simple and compact MRBF terminal fuse by blue sea (MRBF - Marine Rated Battery Fuse)

                  Get the fuse & holder. Bolts to the battery terminal, and is a very clean install.
                  Only problem I have found with that Mike is the terminal bolt size. Works great if you select the right battery terminal post when you buy the batteries, suks otherwise because you have to rig something to make it work. Not too mention a bit pricey of around $16 to $30 for the connector, plus another $12 to $25 for the fuse. But i have used then and they are slick.
                  MSEE, PE

                  Comment

                  • xyxoxy
                    Junior Member
                    • May 2011
                    • 14

                    #10
                    The battery fuse looks very cool! Never knew such a thing existed.
                    My battery has an L2 post so I'll have to see how that works out.

                    So it looks like that one fuse will cover everything... and I guess there is no real need for a ground wire on my little system?

                    Thanks again guys. It's great to ask a question and actually get an informed answer.

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #11
                      Well, any panels outdoors, you need a wire to ground the FRAME to "earth".

                      Follow the INVERTER instructions about grounding it, some are allowed, some will smoke.

                      The battery - terminal will be called the Common or Return, and should not have a fuse. The more extensive your system is, the more importance is attached to grounding the battery - ( but not to the same point as the solar panel frames)

                      Grounding a mixed DC and AC system is a "fuzzy" science.
                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #12
                        Originally posted by xyxoxy
                        So it looks like that one fuse will cover everything... and I guess there is no real need for a ground wire on my little system?
                        Completely false statement. Depending on the voltage of the system whether or not the system has to be grounded or not. If the system is below 50 volts there is no requirement to ground anything except framework. If the system is ungrounded only having one fuse will do nothing to protect anything.
                        MSEE, PE

                        Comment

                        • Sunking
                          Solar Fanatic
                          • Feb 2010
                          • 23301

                          #13
                          Originally posted by Mike90250
                          Grounding a mixed DC and AC system is a "fuzzy" science.
                          Not really it is quite precise, you just have to know the rules and how to apply them. You know the link to the document that covers it Mike. But I will not answer questions about specific topologies. Not because I am mean, but because DIY do not even know the thousand of other questions they need to ask and know about. Heck I know 10 year veteran electricians who still have to ask questions about it.
                          MSEE, PE

                          Comment

                          • Mike90250
                            Moderator
                            • May 2009
                            • 16020

                            #14
                            Originally posted by Sunking
                            You know the link to the document that covers it Mike.
                            READING THIS DOCUMENT
                            Last edited by Mike90250; 05-20-2011, 10:04 AM.
                            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                            solar: http://tinyurl.com/LMR-Solar
                            gen: http://tinyurl.com/LMR-Lister

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by Mike90250
                              Yes Sir that is the one.
                              MSEE, PE

                              Comment