Hello all,
Time for the hidden tips and tricks to make your Enphase array go offgrid like magic.
M250's "Turn-On-244vac output" phase lock requires: Pure sine wave @ 59.99-61Hz (+/- 2hz from 60), a THD less than 2%, 244-245vac, M250's provide a "split-Phase" 245vac with provided neutral and when stacked are the most affordable reliable modular micro-inverters in the world. For a 8KW backup UPS system in a box with 30 minutes of run-time with those above specs think $15-20K. You can build one longer lasting for far cheaper.
M250's actually power up at 22Vdc, and then off again at 18Vdc automatically. So if you were to use a 24VDC battery bank you could use that to run your M250's at night if you wire them accordingly and when the voltage gets too low they would just turn off, protecting your investment. Many PWM charge controllers operate at 24VDC and have an internal timer or PE sensor which will switch the micro-inverter load to battery on a schedule.
For the base "utility" signal, any "split phase" 244vac inverter which can match the above specs will do. You will find that specs that tight are not industry standard, but they are the more expensive type inverters to maintain the less than 2% THD. Expect to spend $2000+ for a split-phase 244vac inverter like a Magnasine, SunnyBoy, Nfinity to name a few. Chinese manufacturers will turn up the voltage for you if you ask nicely but they sell very few true sine wave inverters with true "split-phase" 244vac.
After phase lock if the solar power produced is not used, the excess panels need to be turned off or diverted to battery chargers if not hooked to the grid. Every minute or so a large voltage pulse builds up and can be seen in lighting which gets that much brighter when the pulses surge. It also takes 5 minutes for the M250 micro-inverters to turn back on after they fault or experience a power loss on the utility side.
As for a battery back-up, quit goofing around and put in some batteries! Go off-grid! I suggest a 24VDC bank as it is easier to match to the M250 inverters. The specs on batteries varies greatly, the most expensive batteries may not be the best option. Get some heavy, deep cycle, well reviewed batteries and stack em up.
I will suggest a dual-use option that you may not have considered. If you use 2, Y adapters from the Solar panel output, and split the power between an inexpensive PWM controller and a M250, the PWM controller will stop charging when the battery is full automatically and the full load of the panel will go to the M250. Automation made easy.
I see no issue connecting these isolated devices in this manner and welcome any arguments against except for the MPPT one.
If you can afford MPPT, then get MPPT, if not use PWM @ 3x the rating you will be using it at for longevity of the charge controller.
My current formula is: 1 24VDC battery source, 1 M250 micro-inverter, one 30A PWM or MPPT controller for each 300+ watt solar panel for AC/DC parallel wiring configurations and maximum uptime, think more than 5 decades. The battery choice is where they get you- BANG! pay up every 3-5 years or buy super expensive batteries that last 8-10. I choose the middle route of batteries, ones that cost me 1/3 of the cost of the big boys, and only last 33% of the max life of them too with little maintenance to do except check water levels. So what if I have to change out batteries that I can recycle $$ to maintain my system every 3-5 years? Probably will need some re-tensioning and terminal cleaning anyhow.
The average internet connected family will need 300-350Ah of battery storage to go through the night with the fans, the AC, and the computers.. etc... on.
The coolest part about the M250's is that they Phase lock individually, and those phase locks are very close to true, but they are not. When performing test readings/observations on my A.C. unit, I found it was much quieter when running on phase-locked solar, the motor didn't go mmm mmm mmmm mmm like it was grunting, it went almost silent. The fan's movement of air made more noise than the compressor, and it never blows colder air then when on the solar under a bright sun. It is possible to run an Air Conditioning unit on just solar power, but you will need some things like a battery bank and/or a M250 Phase lock array.
Being an avid field theory Major, I surmised the following: The phase lock being close but not exact is generating slightly off-axis magnetic fields in the motor wiring, which act like additional little arms pushing the motor more efficiently! Or something close to that definition. I found that my computer works better too, it was "smoother" which translates to better power usage since I didn't upgrade anything except the power source.
Time for the hidden tips and tricks to make your Enphase array go offgrid like magic.

M250's "Turn-On-244vac output" phase lock requires: Pure sine wave @ 59.99-61Hz (+/- 2hz from 60), a THD less than 2%, 244-245vac, M250's provide a "split-Phase" 245vac with provided neutral and when stacked are the most affordable reliable modular micro-inverters in the world. For a 8KW backup UPS system in a box with 30 minutes of run-time with those above specs think $15-20K. You can build one longer lasting for far cheaper.
M250's actually power up at 22Vdc, and then off again at 18Vdc automatically. So if you were to use a 24VDC battery bank you could use that to run your M250's at night if you wire them accordingly and when the voltage gets too low they would just turn off, protecting your investment. Many PWM charge controllers operate at 24VDC and have an internal timer or PE sensor which will switch the micro-inverter load to battery on a schedule.
For the base "utility" signal, any "split phase" 244vac inverter which can match the above specs will do. You will find that specs that tight are not industry standard, but they are the more expensive type inverters to maintain the less than 2% THD. Expect to spend $2000+ for a split-phase 244vac inverter like a Magnasine, SunnyBoy, Nfinity to name a few. Chinese manufacturers will turn up the voltage for you if you ask nicely but they sell very few true sine wave inverters with true "split-phase" 244vac.
After phase lock if the solar power produced is not used, the excess panels need to be turned off or diverted to battery chargers if not hooked to the grid. Every minute or so a large voltage pulse builds up and can be seen in lighting which gets that much brighter when the pulses surge. It also takes 5 minutes for the M250 micro-inverters to turn back on after they fault or experience a power loss on the utility side.
As for a battery back-up, quit goofing around and put in some batteries! Go off-grid! I suggest a 24VDC bank as it is easier to match to the M250 inverters. The specs on batteries varies greatly, the most expensive batteries may not be the best option. Get some heavy, deep cycle, well reviewed batteries and stack em up.
I will suggest a dual-use option that you may not have considered. If you use 2, Y adapters from the Solar panel output, and split the power between an inexpensive PWM controller and a M250, the PWM controller will stop charging when the battery is full automatically and the full load of the panel will go to the M250. Automation made easy.
I see no issue connecting these isolated devices in this manner and welcome any arguments against except for the MPPT one.
If you can afford MPPT, then get MPPT, if not use PWM @ 3x the rating you will be using it at for longevity of the charge controller.
My current formula is: 1 24VDC battery source, 1 M250 micro-inverter, one 30A PWM or MPPT controller for each 300+ watt solar panel for AC/DC parallel wiring configurations and maximum uptime, think more than 5 decades. The battery choice is where they get you- BANG! pay up every 3-5 years or buy super expensive batteries that last 8-10. I choose the middle route of batteries, ones that cost me 1/3 of the cost of the big boys, and only last 33% of the max life of them too with little maintenance to do except check water levels. So what if I have to change out batteries that I can recycle $$ to maintain my system every 3-5 years? Probably will need some re-tensioning and terminal cleaning anyhow.
The average internet connected family will need 300-350Ah of battery storage to go through the night with the fans, the AC, and the computers.. etc... on.
The coolest part about the M250's is that they Phase lock individually, and those phase locks are very close to true, but they are not. When performing test readings/observations on my A.C. unit, I found it was much quieter when running on phase-locked solar, the motor didn't go mmm mmm mmmm mmm like it was grunting, it went almost silent. The fan's movement of air made more noise than the compressor, and it never blows colder air then when on the solar under a bright sun. It is possible to run an Air Conditioning unit on just solar power, but you will need some things like a battery bank and/or a M250 Phase lock array.
Being an avid field theory Major, I surmised the following: The phase lock being close but not exact is generating slightly off-axis magnetic fields in the motor wiring, which act like additional little arms pushing the motor more efficiently! Or something close to that definition. I found that my computer works better too, it was "smoother" which translates to better power usage since I didn't upgrade anything except the power source.