i have 4 panels [I'd like to add one more using a combiner box] tied in parallel using 3 sets of mc4y connectors. My (isc per panel is 8.57) so i am assuming the correct mathematics when it comes down to choosing the proper circuit breaker in my case would be 4 * 8.57 = 34.28 * 125% = 42.85 rounded 45.00 amps .
and for my newly added panel with the same isc, I'd simply multiple 8.57 * 125% = 10.71 rounded to a 12 amp circuit breaker .
Are my four panels currently tied in parallel considered a string and if so, do I leave it like that and just purchase a 45 amp circuit breaker? and why is that I can only find 2 pole 45 amp breakers, looks like it's twice the size of a regular circuit breaker.
and for my newly added panel with the same isc, I'd simply multiple 8.57 * 125% = 10.71 rounded to a 12 amp circuit breaker .
Are my four panels currently tied in parallel considered a string and if so, do I leave it like that and just purchase a 45 amp circuit breaker? and why is that I can only find 2 pole 45 amp breakers, looks like it's twice the size of a regular circuit breaker.