Putting together a system for my off grid garage (no grid power and never will have it). Inverter will be the Conext SW4048. I will use the Midnight Solar E-panel. MS E-panel has room for three double throw breakers.
I plan to put three small subpanels in various parts of the garage. Each of these will have a 20a double pole upstream breaker at the MS E-panel. One of the subpanels will be in the location where my grounding rod is located. This will be about a 75' subpanel run. My plan is to use 10/3 wire for this subpanel and bond neutral to ground at this panel. The other panels including the MS E-panel will not have neutral bonded. I have also confirmed that the inverter does not have neutral bonded. I will also make sure my generator does not have neutral bonded.
Does this sound right? If I decided to bond neutral at the MS E-panel instead would the 10ga ground in the subpanel run be adequate?
Thanks for any advice.
I plan to put three small subpanels in various parts of the garage. Each of these will have a 20a double pole upstream breaker at the MS E-panel. One of the subpanels will be in the location where my grounding rod is located. This will be about a 75' subpanel run. My plan is to use 10/3 wire for this subpanel and bond neutral to ground at this panel. The other panels including the MS E-panel will not have neutral bonded. I have also confirmed that the inverter does not have neutral bonded. I will also make sure my generator does not have neutral bonded.