low output from charge controller
Collapse
X
-
Now 480 in and 460 out is a real number meaning your controller is 95% efficient and burning 20 watts of waste heat, but if you really had 480 in and only 145 out your controller would be on fire burning off 335 watts. You have to be doing something wrong or leaving something out.Leave a comment:
-
Seems you should reconfigure your panels to provide higher voltage at less amps. Most CC operate most efficient with a voltage at least twice the battery bank. Your CC will have an efficiency curve posted on a website somewhere.
What you describe with the battery charging is normal, the part where the amps trail off when the battery is close to charged up anyways, whether you have the proper voltages programmed into the CC you haven't said.Leave a comment:
-
hmmm. I can't tell if you are running 12V or 24V. You may have a "counterfeit" controller, that "says" MPPT, but it is not actually, most folks can't tell the difference, but you may have caught them at it.
When the controller is outputting low amps, try turning on a substantial load, and see if the controller produces more power as the battery voltage sags. It may be that the bulk stage of the charge is done, and you are in Absorb.Leave a comment:
-
hmmm. I can't tell if you are running 12V or 24V. You may have a "counterfeit" controller, that "says" MPPT, but it is not actually, most folks can't tell the difference, but you may have caught them at it.
When the controller is outputting low amps, try turning on a substantial load, and see if the controller produces more power as the battery voltage sags. It may be that the bulk stage of the charge is done, and you are in Absorb.Leave a comment:
-
hmmm. I can't tell if you are running 12V or 24V. You may have a "counterfeit" controller, that "says" MPPT, but it is not actually, most folks can't tell the difference, but you may have caught them at it.
When the controller is outputting low amps, try turning on a substantial load, and see if the controller produces more power as the battery voltage sags. It may be that the bulk stage of the charge is done, and you are in Absorb.Leave a comment:
-
low output from charge controller
using this cc.. http://www.australianwindandsolar.com/MP3735_Manual.pdf
the input to the batteries is often low, for example, panel output would be 32v x 15amps = 480w. the output to the batteries would be 29v x 5amps = 145w . the batteries are at 75%. they are 250ah at 24v,what could be the problem? when i connect the dc charger via the gen the batteries will take 40amps + at 14.4v. arranged in a 12v 500ah config of course.
Leave a comment: