picked up a new 24v 2000w pure sine wave inverter cheap, will it work ok off a 24v 200ah battery bank for short bursts on a 1350w coffee machine and maybe a 600w washing machine ? thanks
24v 2000w pure sine wave inverter 4000w surge
Collapse
X
-
-
-
Best case is that it works and no item releases its' internal "smoke".
Worse case is that it will not only fail to work but mess up your appliances so they no longer work.
It is a gamble when using "cheap" electronic hardware that is not design for real life usage.Comment
-
Only way of knowing if that inverter will work is to use it on your equipment.
Best case is that it works and no item releases its' internal "smoke".
Worse case is that it will not only fail to work but mess up your appliances so they no longer work.
It is a gamble when using "cheap" electronic hardware that is not design for real life usage.Comment
-
Comment
-
Inverter is only one weak spot. The real weak spots are the battery an dwiring is not capable of delivering that kind of current for any length of time. At 2000 watts @ 24 volts is 100+ amps on a 200 AH battery. Unless that battery is Lithium or very high end AGM, the voltage will collapse forcing the inverter to shut down. Even if the battery can do it then the wiring is the next weak spot. Very doubtful Joe Homeowner has the tools and skill to necessary to terminate a 100+ amp connection. If incorrectly done at best the Inverter shuts down, at worse will catch fire.MSEE, PEComment
-
Inverter is only one weak spot. The real weak spots are the battery an dwiring is not capable of delivering that kind of current for any length of time. At 2000 watts @ 24 volts is 100+ amps on a 200 AH battery. Unless that battery is Lithium or very high end AGM, the voltage will collapse forcing the inverter to shut down. Even if the battery can do it then the wiring is the next weak spot. Very doubtful Joe Homeowner has the tools and skill to necessary to terminate a 100+ amp connection. If incorrectly done at best the Inverter shuts down, at worse will catch fire.Comment
-
C10 discharge rate (20A) x 24V = 480Wx.92 inverter eff = 441 Watts
a coffee pot ins't like a skill saw, you may run a skill saw for 10 seconds to cut a 2x4, a coffee pot is going to consume max power for 10 or more minutes1150W, Midnite Classic 200, Cotek PSW, 8 T-605sComment
-
the coffee machine is not a coffee pot, its a cappicino maker. it runs for about 2-3mins. the heating is on off 30secs on, then off for about 10secs, then on 30secs. takes about 3 mins to make a cappicino.. so is my battery bank too small? c10 discharge rate needs to be 60A?Comment
-
I have a 2300 watt 24v inverter with 4 battery 12v 100 ah
I use a 4 slice toaster 1500 watt for 5 min cycle
The voltage when the inverter is loaded is 12.3 or 12.4 when the battery are almost full
The terminal on the inverter and the battery stay cold
Your voltage will probably go under 12 v with 2 batteryComment
-
thanks for the replies, tested it out on the coffee machine and the fridge. it had no problem with the coffee machine or the fridge. batteries were topped up again by the panels in no time. inverter didnt even get luke warm the fans didnt need to kick in at all, the voltage on the battery bank dropped to 23.5v while the coffee machine was drawing 1350w , some replies to this thread were just rubbishComment
-
If your panels had not been supplementing the batteries would have been sitting at 25.2 volts assuming they are fully charged. Try that in the morning when the batteries have discharged with cloud cover and your test results will be different. Boom Boom Out Go The Lights.
Issue is batteries have Internal Resistance. Current through resistance drops voltage. A battery internal resistance is directly related to it size. To stay with in 2 to 3% voltage sag discharge current is limited to about C/8. Go higher and you drop more than 2 to 3% as you stated you observed. You can get away with drawing excessive current as you did because your batteries were fully charged, and your panels were supplementing battery current.
It is not rubbish, it is the law of physics.MSEE, PEComment
-
ah thanks, so i really need a 500ah battery bank to do loads of 1500w for a c/8 discharge rate. my 200ah battery bank can do just 600w load. got it. so i will need to use my 7 panals to get my 500ah battery bank. so untill then my coffees will have to wait till the midday sun on a full battery bank. dang, looks like i will have to start the gen in the mornings
ok been thinking, to expand this on the cheap, i use 4 x 12v 100ah batteries, do 2 sets of 2 x 12 batteries in parallel, then configure these 2 sets in series to get a 24v battery bank of 400ah. put up another 3 x 250w panels in parallel same as the existing set of 3 panels in parallel. then i only need one more chi-com 30amp CC . so that will be 2 x chi-com 30amp CCs and have them both in a 24v series charge config. i should get away with a 400ah battery bank just like Wakie doesComment
-
I have a 2300 watt 24v inverter with 4 battery 12v 100 ah
I use a 4 slice toaster 1500 watt for 5 min cycle
The voltage when the inverter is loaded is 12.3 or 12.4 when the battery are almost full
The terminal on the inverter and the battery stay cold
Your voltage will probably go under 12 v with 2 battery1150W, Midnite Classic 200, Cotek PSW, 8 T-605sComment
-
thanks for the replies, tested it out on the coffee machine and the fridge. it had no problem with the coffee machine or the fridge. batteries were topped up again by the panels in no time. inverter didnt even get luke warm the fans didnt need to kick in at all, the voltage on the battery bank dropped to 23.5v while the coffee machine was drawing 1350w , some replies to this thread were just rubbish
Now that you know it works I would keep an eye on my battery system to make sure it is really getting back to 100% SOC. Using a volt meter will not give you that information. You either use a hydrometer and measure the density of the fluid or use an expensive battery testing system that will put it under load and measure the change of discharge.
My guess is that going below 24 volts repetitively will cause one or more of the cells in that system to have an early failure.
Hope it works out for you.Comment