Well he is correct, but not telling you everything. Could be he does not know.
Panels are current sources, not voltage like a battery. What varies is the CURRENT and it is directly proportional to the amount of Sun Lite striking its surface. So when you see in the SPEC Imp is a lab condition, not real world. In real world current will be lower, thus less power than specified. However open circuit voltage (Voc) is not affected by solar insolation. It is affected by temperature. It is a negative coefficient meaning as temps drops voltage goes up. When you look at a panel spec Voc is stated at 25 degrees C. There is also another spec called Temperature Coefficients that is used by designers to calculate Voc voltage as the temp drops. They use worse case cold numbers for your area. I am pretty sure your temps go below 25 C.
Since you are in a warm climate here is a simple formula to use. Voc x 1.25 = Corrected temp Voc. So if your CC Voc rating is 150 volts, then you know you want to keep Voc to 150/1.25 = 117 volts. So look at your panels specs, find Voc and add them up in series to see if you stay below 117 volts. I suspect thos panels Voc are greater than 117/4 = 29.3 volts. I bet they are pushing 40 volt Voc.
Panels are current sources, not voltage like a battery. What varies is the CURRENT and it is directly proportional to the amount of Sun Lite striking its surface. So when you see in the SPEC Imp is a lab condition, not real world. In real world current will be lower, thus less power than specified. However open circuit voltage (Voc) is not affected by solar insolation. It is affected by temperature. It is a negative coefficient meaning as temps drops voltage goes up. When you look at a panel spec Voc is stated at 25 degrees C. There is also another spec called Temperature Coefficients that is used by designers to calculate Voc voltage as the temp drops. They use worse case cold numbers for your area. I am pretty sure your temps go below 25 C.
Since you are in a warm climate here is a simple formula to use. Voc x 1.25 = Corrected temp Voc. So if your CC Voc rating is 150 volts, then you know you want to keep Voc to 150/1.25 = 117 volts. So look at your panels specs, find Voc and add them up in series to see if you stay below 117 volts. I suspect thos panels Voc are greater than 117/4 = 29.3 volts. I bet they are pushing 40 volt Voc.
Comment