    Ive got a 180W solar panel in my van connected to a MPPT Tracer with MT5 and 115AH battery.

    I noticed that when the sun comes out the reading goes up to 100% full in a couple of minutes and then when some cloud comes over it goes back down to 50-60% very rapidly. Any ideas whats happening here??

    Thanks
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    What makes you think anything is wrong? Solar panels do not work with out direct sun light.
    MSEE, PE

    Comment

    • vagabondvanman
      Junior Member
      • Mar 2015
      • 12

      #3
      Because why would it reach 100% battery charge within a couple of minutes and then suddenly drop to about 50 % straight away?

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        Would indicate your battery is not charged up yet or poor connections.
        MSEE, PE

        Comment

        • vagabondvanman
          Junior Member
          • Mar 2015
          • 12

          #5
          But surely that doesn't account for why it reaches 100% charge very quickly when a tiny bit of sun comes out.

          Comment

          • sensij
            Solar Fanatic
            • Sep 2014
            • 5074

            #6
            Are you sure you set it up right? Correct battery capacity, temperature compensation, and type? Have you tried disconnecting all loads from the battery (besides the charge controller) so there is nothing that could drain it?

            A bad connection, as Sunking suggested, could cause the charge controller to get a bad voltage reading and misreport the SOC, especially when there is current flowing (when the sun is out).
            CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

            Comment

            • thastinger
              Solar Fanatic
              • Oct 2012
              • 804

              #7
              Originally posted by vagabondvanman
              Hi,

              Any ideas whats happening here??

              Thanks
              Yes, the voltage is going up and down.
              1150W, Midnite Classic 200, Cotek PSW, 8 T-605s

              Comment

              • vagabondvanman
                Junior Member
                • Mar 2015
                • 12

                #8
                Capacity/ and type are correct. I left temp comp. as default.

                I will disconnect everything tomorrow and see. How can I check/fix a bad connection if this is the problem? Thanks

                Originally posted by sensij
                Are you sure you set it up right? Correct battery capacity, temperature compensation, and type? Have you tried disconnecting all loads from the battery (besides the charge controller) so there is nothing that could drain it?

                A bad connection, as Sunking suggested, could cause the charge controller to get a bad voltage reading and misreport the SOC, especially when there is current flowing (when the sun is out).

                Comment

                • Wy_White_Wolf
                  Solar Fanatic
                  • Oct 2011
                  • 1179

                  #9
                  Originally posted by vagabondvanman
                  Hi,

                  Ive got a 180W solar panel in my van connected to a MPPT Tracer with MT5 and 115AH battery.

                  I noticed that when the sun comes out the reading goes up to 100% full in a couple of minutes and then when some cloud comes over it goes back down to 50-60% very rapidly. Any ideas whats happening here??

                  Thanks
                  Doesn't that controller have just a single led that flashes when it's charged and solid green when charging? If so how do know the battery is dropping to 50-60% when a cloud goes over?

                  Sounds to me like everything is actually working just as it should. Your battery is already charged. When the sun comes out the panel can put out full power and the flashing light is caused by the shunt controller kicking off when maximum voltage hits and turning back on after a few tenths of surface charge drops off or load drops the voltage. When a cloud goes over the panel cannot support full voltage that would make the shunt controller kick off so it stays on just providing a trickle charge or the load drops the voltage.

                  One of the problems with meters like the MT-5 is they have to read battery voltage under charging and load conditions. But that is a bad indicator of true SOC conditions.

                  WWW

                  Comment

                  • sensij
                    Solar Fanatic
                    • Sep 2014
                    • 5074

                    #10
                    Originally posted by Wy_White_Wolf
                    Doesn't that controller have just a single led that flashes when it's charged and solid green when charging? If so how do know the battery is dropping to 50-60% when a cloud goes over?

                    Sounds to me like everything is actually working just as it should. Your battery is already charged. When the sun comes out the panel can put out full power and the flashing light is caused by the shunt controller kicking off when maximum voltage hits and turning back on after a few tenths of surface charge drops off. When a cloud goes over the panel cannot support full voltage that would make the shunt controller kick off so it stays on just providing a trickle charge.

                    WWW
                    The MT5 meter reports SOC as a %, based on voltage feedback. I am assuming that is what the OP is reporting.
                    CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                    Comment

                    • Wy_White_Wolf
                      Solar Fanatic
                      • Oct 2011
                      • 1179

                      #11
                      Originally posted by sensij
                      The MT5 meter reports SOC as a %, based on voltage feedback. I am assuming that is what the OP is reporting.
                      Yes, so when a cloud goes over it changes from reading voltage under charge conditions to reading voltage under load conditions. We all already know that voltage is a poor measurement for SOC and is only remotely accurate if the batteries have been at rest for a couple hours.

                      WWW

                      Comment

                      • vagabondvanman
                        Junior Member
                        • Mar 2015
                        • 12

                        #12
                        Yeah thats correct.

                        Originally posted by sensij
                        The MT5 meter reports SOC as a %, based on voltage feedback. I am assuming that is what the OP is reporting.

                        Comment

                        • Mike90250
                          Moderator
                          • May 2009
                          • 16020

                          #13
                          Originally posted by vagabondvanman
                          Because why would it reach 100% battery charge within a couple of minutes and then suddenly drop to about 50 % straight away?
                          I would suspect that the batteries are old, or possibly sulphated. Time for new ones ? Get some more opinions before you spend any $$

                          What are your loads? what are the batteries ?
                          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                          solar: http://tinyurl.com/LMR-Solar
                          gen: http://tinyurl.com/LMR-Lister

                          Comment

                          • vagabondvanman
                            Junior Member
                            • Mar 2015
                            • 12

                            #14
                            Battery is only about 4 months old....

                            Comment

                            • sensij
                              Solar Fanatic
                              • Sep 2014
                              • 5074

                              #15
                              Originally posted by Wy_White_Wolf
                              Yes, so when a cloud goes over it changes from reading voltage under charge conditions to reading voltage under load conditions. We all already know that voltage is a poor measurement for SOC and is only remotely accurate if the batteries have been at rest for a couple hours.

                              WWW
                              Agreed. Taking the loads off the system and watching it over some time should give a better idea of what is going on, even if the measuring technique is still not great.