    #16
    Originally posted by inetdog
    Make that dry warm environments and I will agree.
    So just how cold and damp does it get in office spaces, shopping centers, warehouses, sporting arenas, and inside your house?
    MSEE, PE

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #17
      Originally posted by SunEagle
      +1 on the warm environment.

      What is amazing is the number of cities that have started to re-lamp their streetlights from HID to LED.
      Energy conservation is not the primary reason, just a side benefit. The driving force is maintenance cost.

      Secondly in cold climates a problem arises. Forget which city in Wisconsin converted all traffic lighting to LED, and school buses to run Vegetable oil aka bio-diesel. Worked great until winter hit. The bio-diesel congealed in the tanks and fuel lines rendering them useless, and Traffic lights were caked in layers of ice and snow so no one could see them. They had to tow all buses to a heated warehouse to thaw out to clear fuel in tanks and lines. Schools were closed for a week.

      Then the city had to switch back to incandescent lamps to melt the snow and ice and keep it off as the incandescent lights generate heat.

      Oops!
      MSEE, PE

      Comment

      • CA_Tom
        Member
        • Oct 2014
        • 87

        #18
        Originally posted by Sunking
        Energy conservation is not the primary reason, just a side benefit. The driving force is maintenance cost.

        Secondly in cold climates a problem arises. Forget which city in Wisconsin converted all traffic lighting to LED, and school buses to run Vegetable oil aka bio-diesel. Worked great until winter hit. The bio-diesel congealed in the tanks and fuel lines rendering them useless, and Traffic lights were caked in layers of ice and snow so no one could see them. They had to tow all buses to a heated warehouse to thaw out to clear fuel in tanks and lines. Schools were closed for a week.

        Then the city had to switch back to incandescent lamps to melt the snow and ice and keep it off as the incandescent lights generate heat.

        Oops!
        Haven't heard of biodiesel congealing and causing problems for busses - but I do remember a time in winter where one of the schoolbuses didn't have it's heater blanket working overnight, and they couldn't get it started. And that was long before biodiesel.

        As for the stoplights - they definitely have had issues that the new lights were too efficient - so weren't warm enough for melting off hard blowing snow. But the articles I recall seeing about Madison they didn't switch back to incandescents - instead they changed the sun-shade thingy so the snow wouldn't accumulate. This isn't the one I saw back then - but similar content: http://abcnews.go.com/GMA/ConsumerNe...ory?id=9506449

        Comment

        • inetdog
          Super Moderator
          • May 2012
          • 9909

          #19
          Originally posted by Sunking
          So just how cold and damp does it get in office spaces, shopping centers, warehouses, sporting arenas, and inside your house?
          That was in reference to the immediately preceding statement about LEDs being better for "lighting in parking lots, roadways and large cold warehouses. "
          I do not know of any large cold warehouses that are warm, regardless of the area. I would hope not damp though.
          And FWIW, some rooms in my house get well below 50 in the winter. And when I do into them I want the lights to work well. (Although it might also be nice if the lights gave off some heat too!)
          SunnyBoy 3000 US, 18 BP Solar 175B panels.

          Comment

          • SunEagle
            Super Moderator
            • Oct 2012
            • 15207

            #20
            Originally posted by inetdog
            That was in reference to the immediately preceding statement about LEDs being better for "lighting in parking lots, roadways and large cold warehouses. "
            I do not know of any large cold warehouses that are warm, regardless of the area. I would hope not damp though.
            And FWIW, some rooms in my house get well below 50 in the winter. And when I do into them I want the lights to work well. (Although it might also be nice if the lights gave off some heat too!)
            At my old job we swapped out the old Metal Halide HID fixtures with the T5 in our refrigerated warehouses. About 8 months after we had a number of complaints from the forklift drivers that the lights either did not come on fast enough or we very dim until they were on a while.

            Turns out that the cold (38F) storage was not a good environment for these lights. They were also installed in our dry ambient warehouses and work like a charm.

            Comment

            • OrdinaryBeauty
              Junior Member
              • Sep 2014
              • 10

              #21
              Umm, so I have some catching up to do here.


              It's entirely possible I misunderstood about the use of straight up DC for LED lighting, but I am certain that I got the part about LED conversions correct. Seems like LED for big lighting has become quite popular in Alaska. Although as CA_Tom points out, interesting possible downside to a light source which stays cool and doesn't melt off snow.

              So maybe the origin of advice I got about using DC power for economy is something that doesn't scale — cost savings result if used in large quantity, but for a residence, not significantly.

              But I did get a few solid answers today during my rough electrical inspection, which I went ahead with, figuring that getting the inspector's eyes on the project now would be worth the $90 it will cost to have him come by again.

              Turns out that everything that was wired for DC is wrong, and I need to run all that wire again if I want to keep DC outlets and lighting.

              So now I have an opportunity to decide if I will stubbornly keep some DC, and pull new wire. Or will I just use the AC and remove all trace of DC wiring that is there.

              FWIW, I also learned that all my breakers need to be Arc Fault (AFCI), as of July 1st. So I will be making that change, too.

              My location, which I was vague about, is roughly 48.8° N, 118° W. Fun fact: our 2010 census population is 28.

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #22
                Originally posted by OrdinaryBeauty
                FWIW, I also learned that all my breakers need to be Arc Fault (AFCI), as of July 1st. So I will be making that change, too.
                Get ready for sticker shock.
                MSEE, PE

                Comment

                • OrdinaryBeauty
                  Junior Member
                  • Sep 2014
                  • 10

                  #23
                  Originally posted by Sunking
                  Get ready for sticker shock.
                  Ah, what's another $200+?

                  (Any comments about the many different brands?)

                  Comment

                  • CA_Tom
                    Member
                    • Oct 2014
                    • 87

                    #24
                    Originally posted by OrdinaryBeauty
                    FWIW, I also learned that all my breakers need to be Arc Fault (AFCI), as of July 1st. So I will be making that change, too.
                    Probably you don't need AFCI for bathroom, kitchen and exterior. But will need GFCI on those outlets.

                    I have heard of people using AFCI for inspection and then swapping them out... I do not recommend that though.

                    Comment

                    • OrdinaryBeauty
                      Junior Member
                      • Sep 2014
                      • 10

                      #25
                      Originally posted by CA_Tom
                      Probably you don't need AFCI for bathroom, kitchen and exterior. But will need GFCI on those outlets.

                      I have heard of people using AFCI for inspection and then swapping them out... I do not recommend that though.
                      Whoa, seems crazy to go through the trouble of switching out breakers just to save a few hundred dollars. I already live in fear of forest fire; I think I'll just keep my house fire odds in my favor.

                      In Washington State, for permits pulled before July 1, 2014 AFCI protection requirement was limited to the bedrooms. Now it seems to be most rooms of a home with 120, single phase, 15 or 20 amp circuits (except bathrooms??). For areas that previously required only GFCI, my inspector endorses a AFCI breaker plus GFCI protection at the outlet.

                      Comment

                      • russ
                        Solar Fanatic
                        • Jul 2009
                        • 10360

                        #26
                        From the Wikipedia - http://en.wikipedia.org/wiki/Arc-fau...it_interrupter

                        Electrical code requirements[edit]

                        Starting with the 1999 version of the National Electrical Code (NFPA 70) in the United States, and the 2002 version of the Canadian Electrical Code in Canada (CSA Standard C22.1), the national codes require AFCIs in all circuits that feed outlets in bedrooms of dwelling units. As of the 2014 version of the NEC,[4] combination type AFCI circuit breakers are required on all branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas. They are also required in dormitory units. This requirement may be accomplished by using either a kind of circuit-breaker (defined by UL 1699) in the breaker panel that provides combined arc-fault and overcurrent protection or by using an OBC AFCI Receptacle for modifications/extensions, as replacement receptacles or in new construction. Not all United States jurisdictions have adopted the AFCI requirements of the NEC as written so it is important to check local Code requirements.
                        The AFCI is intended to prevent fire from arcs. AFCI circuit breakers are designed to meet one of two standards as specified by UL 1699: "branch" type or "combination" type (note: the Canadian Electrical Code uses different terminology but similar technical requirements). A branch type AFCI trips on 75 amperes of arcing current from the line wire to either the neutral or ground wire. A combination type adds series arcing detection to branch type performance. Combination type AFCIs trip on 5 amperes of series arcing.
                        The advanced electronics inside an AFCI breaker detect sudden bursts of electric current in milliseconds; long before a standard circuit breaker or fuse would trip. A "combination AFCI breaker" will provide protection against parallel arcing (line to neutral), series arcing (a loose, broken, or otherwise high resistance segment in a single line), ground arcing (from line, or neutral, to ground), overload protection and short circuit protection.
                        OBC AFCI Receptacles contain electronic components within the device that constantly monitor a circuit for the presence of “normal” and “dangerous” arcing conditions. Based upon an established threshold in the sine wave, the AFCI can be triggered to quickly react and de-power a circuit if “dangerous” arcing is detected.
                        In 2002, the NEC removed the word "receptacle", leaving "outlets", with the effect that lights and other wired-in devices such as ceiling fans within bedrooms of dwellings were added to the requirement. The 2005 code made it clearer that all outlets must be protected despite discussion in the code-making panel about excluding bedroom smoke detectors from the requirement. "Outlets" as defined in the NEC includes receptacles, light fixtures and smoke alarms, amongst other things — basically, any point where electricity is used to power something is an outlet.
                        As of January 2008, only "combination type" AFCIs will meet the NEC requirement. The 2008 NEC requires the installation of combination-type AFCIs in all 15 and 20 ampere residential circuits with the exception of laundries, kitchens, bathrooms, garages and unfinished basements.
                        [SIGPIC][/SIGPIC]

                        Comment

                        • Sunking
                          Solar Fanatic
                          • Feb 2010
                          • 23301

                          #27
                          Originally posted by OrdinaryBeauty
                          In Washington State, for permits pulled before July 1, 2014 AFCI protection requirement was limited to the bedrooms. Now it seems to be most rooms of a home with 120, single phase, 15 or 20 amp circuits (except bathrooms??). For areas that previously required only GFCI, my inspector endorses a AFCI breaker plus GFCI protection at the outlet.
                          That is called LOCAL ADMENDMENTS. A local amendment modifies NEC and they can be less or more restrictive. Many Jurisdictions opted out of AFCI early on because the cost to the consumer was to great. It was only after several years before they adopted the AFCI requirements. I was part of the code making panel when AFCI came out and a lot of us tried to keep them out of the code at the time because there was only one company who made AFCI breakers and they were the ones pushing the requirement. Had it not been for Fire Departments and Insurance Companies they would have never been added until other manufactures were available to get the price down. That allowed that manufacture Wind Fall profits for 3 to 4 years before competition forced their hand and drove down prices. FWIW there are still some Jurisdictions that do not require AFCI. Ham radio operators hate them and replace all of them as the trip everytime they key their transmitters.

                          One more thing for you to think about if fire hazard really concerns you. Give up the idea of low voltage DC as you are just asking for a fire. That is why you *** got whacked by the inspector. He knows it is dangerous and you did not follow the code to compensate for the added danger.
                          Last edited by Mike90250; 11-20-2014, 01:36 AM. Reason: vulgarity
                          MSEE, PE

                          Comment

                          • OrdinaryBeauty
                            Junior Member
                            • Sep 2014
                            • 10

                            #28
                            Today we pulled out all the DC wiring, and replaced it with good ole regular Romex. Tomorrow, I will go on a hunt for some arc fault breakers, since no one locally has them in stock — if they even know what they are. I am aiming to pass a do-over rough inspection next Tuesday.

                            Thank you all for chiming in with such an array of information. I'm actually kind of excited about learning so much; good background for when I actually start planning the solar power install.

                            Comment

                            • CA_Tom
                              Member
                              • Oct 2014
                              • 87

                              #29
                              Originally posted by OrdinaryBeauty
                              Today we pulled out all the DC wiring, and replaced it with good ole regular Romex.
                              So what did you have before for wires?

                              Comment

                              • Sunking
                                Solar Fanatic
                                • Feb 2010
                                • 23301

                                #30
                                Originally posted by OrdinaryBeauty
                                Today we pulled out all the DC wiring, and replaced it with good ole regular Romex.
                                Why? What gauge?
                                MSEE, PE