Combiner box...

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Nefariis
    Junior Member
    • Jul 2014
    • 14

    #1

    Combiner box...

    So I was looking through plans online for combiner boxes and the way these things are being wired from an electrical standpoint just doesnt make sense to me.


    So if I built four panels that output 10 amps at 24v's and I wanted to put a 15 amp breaker on each panel - this is how I am seeing it done:

    New Bitmap Image.png


    This doesnt make any sense to me because fuses and breakers (most) are bi directional. So when the current passes through the first set of 15a breakers it could easily just feed back up the line and blow the breaker or fuse next to it.

    Am I missing something? How are people wiring these boxes so they input into a single slot on a charge controller? It seems like there would have to be an isolator or a diode for each panel between the 15a fuse and the 50a fuse.

    Thanks for the help
  • ILFE
    Solar Fanatic
    • Sep 2011
    • 236

    #2
    Originally posted by Nefariis
    Am I missing something? How are people wiring these boxes so they input into a single slot on a charge controller?
    Here is a typical combiner box and how it would be wired. Does viewing this image help?

    midnite_combiner_box.jpg


    EDIT: Alternatively, if it were possible to wire your array into a single series string, rather than parallel (as you have depicted in your drawing), you would only have one input to the charge controller and no need for a combiner box.
    Last edited by ILFE; 07-30-2014, 12:15 AM. Reason: additional text added.
    Paul

    Comment

    • Nefariis
      Junior Member
      • Jul 2014
      • 14

      #3
      Tomato Tomato.

      There are still 3 breakers touching each other at one end like in the drawn (poorly) bitmap. Those breakers are not unidirectional - so what is stopping the current from two 15 amp breakers form tripping the third? Is the electrical current incapable of traveling backwards if there is a forward current? (which wouldn't make sense in that combiner box as it would seem like the two 15a breakers on the right would put a > 15 amp current on the breaker on the left)

      Any more thoughts?

      Comment

      • ILFE
        Solar Fanatic
        • Sep 2011
        • 236

        #4
        Originally posted by Nefariis
        Tomato Tomato.

        There are still 3 breakers touching each other at one end like in the drawn (poorly) bitmap. Those breakers are not unidirectional - so what is stopping the current from two 15 amp breakers form tripping the third? Is the electrical current incapable of traveling backwards if there is a forward current? (which wouldn't make sense in that combiner box as it would seem like the two 15a breakers on the right would put a > 15 amp current on the breaker on the left)

        Any more thoughts?
        First, I am beginning to wonder if we are on the same page here. I may be off just a bit, but will do my best to stay with you.

        Second, the DC current that passes through breakers in the combiner will only go one way, from the PV array to the controller. To my knowledge, no power will ever be sent back from the batteries, through the breakers and into to the modules. (If it were, it would drain the batteries at night time when no light were shining on the array. This is due to the protection diodes in the modules. I would hazard a guess that modern controllers have similar protection to prevent this from happening as well??)

        Third, unless the panels are going to be installed in a parallel string, there is - realistically, no reason to even install a breaker between the PV array and the controller.

        The only real purpose a breaker will serve, is as a switch to disconnect the PV array from the controller in order to work on modules in a series string. (If you have a two conductor wire that will carry more current than a single module can produce, the circuit protection will never be needed and the wire can never be damaged by the current coming from the PV array.)

        When wiring two (or more) strings together in a combiner, will be the only reason / time to have breaker protection.
        Paul

        Comment

        • Nefariis
          Junior Member
          • Jul 2014
          • 14

          #5
          Breakers should be bidirectional (certainly the ones pictured), there are no diodes in them to only cause the current to flow one way - in fact most of them are just a simple thermal trip.

          I understand that no current will flow from the batteries back to the Panels, but that is because there are diodes in the charge controller and on the back of the PV panels - not because of the breakers.

          And yes, my 4 panels will be installed in parallel and not in a series - 4 panels in parallel.


          Ok, as I am writing this it finally hit me why this works...

          Its simply just the definition between AC and DC current. DC only flows one way (from the power source) where as AC alternates forwards and backwards : /

          I do quite a bit of AC wiring and I knew there was no way this would work as is - but I forgot that DC (unidirectional) doesn't quite work the same.

          A good AC/DC practice model I suppose.

          Comment

          • ILFE
            Solar Fanatic
            • Sep 2011
            • 236

            #6
            Originally posted by Nefariis
            I understand that no current will flow from the batteries back to the Panels, but that is because there are diodes in the charge controller and on the back of the PV panels - not because of the breakers.
            Yes, that is what I said, too.
            Paul

            Comment

            • inetdog
              Super Moderator
              • May 2012
              • 9909

              #7
              Originally posted by Nefariis
              I understand that no current will flow from the batteries back to the Panels, but that is because there are diodes in the charge controller and on the back of the PV panels - not because of the breakers.
              1. No modern panels have blocking diodes to prevent reverse flow. They have bypass diodes to protect shaded panel sections.
              2. The breaker is there to deal with a double failure: simultaneously
              a. The CC fails allowing battery voltage to feed back to the panels and
              b. one or more strings fail and allow large reverse currents through the panels and/or wiring.
              3. The breaker is also there in multiple (3 and up) parallel strings to prevent two or more good strings from producing damaging current back into a failed string.
              SunnyBoy 3000 US, 18 BP Solar 175B panels.

              Comment

              • ILFE
                Solar Fanatic
                • Sep 2011
                • 236

                #8
                Originally posted by inetdog
                1. No modern panels have blocking diodes to prevent reverse flow. They have bypass diodes to protect shaded panel sections.
                2. The breaker is there to deal with a double failure: simultaneously
                a. The CC fails allowing battery voltage to feed back to the panels and
                b. one or more strings fail and allow large reverse currents through the panels and/or wiring.
                3. The breaker is also there in multiple (3 and up) parallel strings to prevent two or more good strings from producing damaging current back into a failed string.
                So, the controller is the only thing stopping the reverse flow of current back to the panels, draining the batteries at night? Wouldn't it be a good decision, then, to have heavy diodes between the panels and controller, to help prevent this from occurring - in case of hardware failure?
                Paul

                Comment

                • mapmaker
                  Solar Fanatic
                  • Aug 2012
                  • 353

                  #9
                  Originally posted by livingincebu
                  So, the controller is the only thing stopping the reverse flow of current back to the panels, draining the batteries at night? Wouldn't it be a good decision, then, to have heavy diodes between the panels and controller, to help prevent this from occurring - in case of hardware failure?
                  Those heavy diodes are not needed and would cause an unnecessary voltage drop.

                  As far as the fuse or breaker protecting against large current flow from the battery (in the event of a controller fault AND a shorted panel), there is already a fuse or breaker between the controller and the battery.

                  If you use polarized breakers, the only breaker with the correct polarity to interrupt the double-fault current flow from the battery is the breaker between the controller and the battery.

                  --mapmaker
                  ob 3524, FM60, ePanel, 4 L16, 4 x 235 watt panels

                  Comment

                  • DVJeep
                    Junior Member
                    • Jun 2014
                    • 7

                    #10
                    Originally posted by Nefariis
                    Its simply just the definition between AC and DC current. DC only flows one way (from the power source) where as AC alternates forwards and backwards : /
                    Keep in mind that DC will flow either way depending on the potentials. DC flows from the highest potential (voltage) to the lowest potential. One way to look at it is DC negative is the "less positive" or the lower potential terminal. In DC the "power source" is the terminal with the highest potential. For example, if a battery charger (power source) positive lead is +14 volts and the positive battery terminal is +12 volts the current will flow from the battery charger lead to the "less positive" positive battery terminal when connected. However, if the battery charger fails and shorts the voltage of the lead becomes less than +12 volts, then the same battery terminal that was "less positive" now becomes the power source and current will flow the other way toward the "less positive" charger. Just another way to look at it.

                    Comment

                    • photowhit
                      Junior Member
                      • Apr 2010
                      • 21

                      #11
                      Originally posted by Nefariis
                      Ok, as I am writing this it finally hit me why this works...

                      Its simply just the definition between AC and DC current. DC only flows one way (from the power source) where as AC alternates forwards and backwards : /

                      I do quite a bit of AC wiring and I knew there was no way this would work as is - but I forgot that DC (unidirectional) doesn't quite work the same.
                      Indeed the breakers are there incase a panel shorts, preventing the backflow across the short, Small din rail breakers like these are currently polarized in that they need to be setup so the + is toward the greatest potential. I believe the NEC is working to change this, but there currently are few if any un polarized breakers in small din rail mounts.

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #12
                        Originally posted by Nefariis
                        Breakers should be bidirectional (certainly the ones pictured), there are no diodes in them to only cause the current to flow one way - in fact most of them are just a simple thermal trip.

                        I understand that no current will flow from the batteries back to the Panels, but that is because there are diodes in the charge controller and on the back of the PV panels - not because of the breakers.

                        And yes, my 4 panels will be installed in parallel and not in a series - 4 panels in parallel.


                        Ok, as I am writing this it finally hit me why this works...

                        Its simply just the definition between AC and DC current. DC only flows one way (from the power source) where as AC alternates forwards and backwards : /

                        I do quite a bit of AC wiring and I knew there was no way this would work as is - but I forgot that DC (unidirectional) doesn't quite work the same.

                        A good AC/DC practice model I suppose.
                        OK you do not quite understand what the main purpose of any Over Current Protection Detection is for. It has only one purpose, to interrupt and disconnect excessive current flow. Nothing more, nothing less. Breakers are sized by the normal operating current inspected, and there is a minimum size wire requirement based on the breaker current rating.

                        But here is what you are missing. The breakers are not there to keep current from flowing, and they do not care what direction the current is flowing. Their only job is to protect the wire, and nothing more. Why are they there you ask? Really simple when you go putting 3 or more parallel string, this is why the code requires combiners with fuses for 3 or more parallel string, if one string were to short out, the current flowing through it are its own and all the current from all other parallel stings. For example if you have 4 parallel strings with each string of panels with a 15 amps current, on estring shorts out and now has 60 AMPS flowing on wiring designed to only have 15 amps.

                        What happens if you have a breaker in the string when that happens? It operates and your system returns to normal operation missing one string.
                        MSEE, PE

                        Comment

                        • mapmaker
                          Solar Fanatic
                          • Aug 2012
                          • 353

                          #13
                          Originally posted by Sunking
                          The breakers are not there to keep current from flowing, and they do not care what direction the current is flowing. Their only job is to protect the wire, and nothing more.
                          I think in most cases the breakers are to protect the panel. The wire on most currently produced panels is usually capable of handling much greater current than the series string rating of the panels.

                          Originally posted by Sunking
                          Why are they there you ask? Really simple when you go putting 3 or more parallel string, this is why the code requires combiners with fuses for 3 or more parallel string, if one string were to short out, the current flowing through it are its own and all the current from all other parallel stings.
                          That you need string OCP (breakers or fuses) on 3 or more strings is certainly true for many/most currently produced panels. But the code, as I understand it, only requires OCP on a particular string if the sum of the currents from the other strings could exceed its series string fuse rating.

                          You may need OCP on only two parallel panels if, for example, one panel with a string rating of 5 amps is parallel to another panel with an Isc of greater than 5 amps.

                          Likewise if you have panels with a string rating of 10 amps and an Isc of 2 amps, you could have 5 in parallel without OCP.

                          --mapmaker
                          ob 3524, FM60, ePanel, 4 L16, 4 x 235 watt panels

                          Comment

                          • photowhit
                            Junior Member
                            • Apr 2010
                            • 21

                            #14
                            Originally posted by Sunking
                            ... The breakers are not there to keep current from flowing, and they do not care what direction the current is flowing.
                            Actually Most/all? din rail DC Breakers are polarized (magnetic) and need to be setup with the + toward the greatest potential. I believe the NEC is moving to make these no longer acceptable, likely, like the dead front combiners boxes, when they become available... https://www.youtube.com/watch?featur...&v=Mtq3cs9Gucc
                            Originally posted by Sunking
                            Their only job is to protect the wire, and nothing more. Why are they there you ask? Really simple when you go putting 3 or more parallel string, this is why the code requires combiners with fuses for 3 or more parallel string, if one string were to short out, the current flowing through it are its own and all the current from all other parallel stings. For example if you have 4 parallel strings with each string of panels with a 15 amps current, on estring shorts out and now has 60 AMPS flowing on wiring designed to only have 15 amps...
                            I'll agree with this if you include the solar panel as part of the 'wiring' I think it's confusing to people to say the breaker is there to protect the wiring, I've had arrays set up with 10 gauge wire where the combined strings didn't total 30amps the capacity of 10 gauge, but require a 15 amp breaker to not over load the 'wire' in the panel it's self.

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by mapmaker
                              I think in most cases the breakers are to protect the panel. The wire on most currently produced panels is usually capable of handling much greater current than the series string rating of the panels.
                              Here is the code specific language from 690.9

                              PV source-circuit overcurrent devices are required
                              to be rated so that the source-circuit conductors are protected
                              in accordance with Article 240 and so that the overcurrent
                              device ratings do not exceed the maximum
                              overcurrent device rating marked on the modules. Possible
                              backfeed currents from the other PV source circuits, other
                              supply sources through the inverter, and storage-battery circuits,
                              if any, have to be considered.


                              Blocking diodes (possibly required by the module manufacturer
                              for specific applications) can lose their blocking
                              ability because of overtemperature conditions or internal
                              breakdown. Therefore, overcurrent protection has to be considered
                              with a condition of shorted blocking diodes if they
                              are used in the circuit.

                              Originally posted by mapmaker
                              That you need string OCP (breakers or fuses) on 3 or more strings is certainly true for many/most currently produced panels. But the code, as I understand it, only requires OCP on a particular string if the sum of the currents from the other strings could exceed its series string fuse rating.
                              Here is 690.8 D

                              (D) Sizing of Module Interconnection Conductors.


                              Where a single overcurrent device is used to protect a set of
                              two or more parallel-connected module circuits, the ampacity
                              of each of the module interconnection conductors shall
                              not be less than the sum of the rating of the single fuse plus
                              125 percent of the short-circuit current from the other
                              parallel- connected modules.
                              [/QUOTE]

                              What it boils down to is this statement in 690.9

                              do not exceed the maximum overcurrent device rating marked on the modules.

                              So if you have 10 amp listed modules, each sting cannot be larger than 10 amps; no if ands or buts
                              MSEE, PE

                              Comment